    Water dripping from face of vertical coil (15 ton)

    Just installed new 15 ton split system (TWE180) and water is dripping off coil especially when unit shuts down. Anyone have this problem before? Any help greatly appreciated! Thanks

  2. #2
    Join Date
    Jul 2013
    Location
    Richmond, VA
    Posts
    6,027
    Post Likes
    Static pressure too high? Is the water beading on the coil, if so, there may be something oily on the fins that is reducing the surface tension of the condensation. Try spraying it with coil cleaner and try again.

  3. #3
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,444
    Post Likes
    Cleaning the coil with Mfgs rec product to get rid of mfg oil should clear this up.
    UA Local 32 retired as of Jan 2020

  4. Likes CEAS-AC-TECH liked this post.
  5. #4
    Join Date
    Aug 2006
    Posts
    3,691
    Post Likes
    We were starting up AirFlow units for MCI / WorldComm. The “V” Coils would drip onto the Fans. We found out you could take the small bottle of JetDry, mix it with three gallons of very warm tap water, in a Pump-up Sprayer. Soak the coil down, after 20 to 30 minutes, we would rinse the coil with three gallons of water. This put a very slight etch on the coil, so the water had something to cling to.

  6. Likes CEAS-AC-TECH liked this post.
+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •