    Package AC unit not that cold

    I am working on a Carrier Unit
    Model 50PG-C14-D-50--P
    R-410A
    I have running pressures of 125/400 stage 1 comp
    Running amps - 18
    Both Condensor fans are running, coils washed/cleaned
    filters aren't dirty, evap are fairly clean, belt is still good.
    supply temp out of the unit is 69F (lowest it will go)

    Not sure what is the problem, help please!
    Thank you

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    24,360
    Post Likes
    Super Heat
    Sub Cooling
    TESP
    ? ? ?

  3. #3
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    40,304
    Post Likes
    Great supply temp if your return is 89

    So 1 of 2 comps running, what IS your return?

    What's outdoor temp? 400 is high unless really hot out. Coil need splitting?

  4. #4
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    31,450
    Post Likes
    If you're a maintenance guy and not an HVAC technician, you're going to need to call somebody in on this, because we can't walk you through all the diagnostics in the open forums.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  5. #5
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    9,486
    Post Likes
    Quote Originally Posted by Knoxtoy View Post
    I am working on
    Carrier Unit Model 50PG-C14-D-50--P ... R-410A
    I have running pressures of 125/400 stage 1 com
    Supply temp out of the unit is 69'F (lowest it will go)

    Not sure what is the problem, help please!

    Thank you
    __ IT IS COMPLEX.

    https://dms.hvacpartners.com/docs/10...9/50PG-5PD.pdf
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  6. #6
    Join Date
    Oct 2007
    Location
    Austin Texas
    Posts
    1,989
    Post Likes
    What kind of expansion devise?
    Nemo me impune lacessit.

    How much blood do I have to bathe in to get clean?

    Don't look down on anyone unless you're helping them up.

  7. #7
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    31,450
    Post Likes
    They use thermostatic expansion valves.

    The unit is designed to appear to be a poor man's Lennox L Series, like the Predator is in the York line.

    Carrier has made this unit sufficiently different from their other style machines... for no apparent good reason...and it's like walking up to a unit you've never seen before and having to figure out how this particular style was designed. It is especially frustrating if you're a technician who has never used their scrolling Marquee system which is used on many of the Centurion units.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  8. #8
    Join Date
    Oct 2007
    Location
    Austin Texas
    Posts
    1,989
    Post Likes
    Oh, well I didn't know if Carrier had carried on with their orfice tube set up. I'm a on site fella and just know what is here.
    Nemo me impune lacessit.

    How much blood do I have to bathe in to get clean?

    Don't look down on anyone unless you're helping them up.

  9. #9
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    31,450
    Post Likes
    Quote Originally Posted by John Culpepper View Post
    Oh, well I didn't know if Carrier had carried on with their orfice tube set up. I'm a on site fella and just know what is here.
    Well, if you have the marquee displays, I would read up on the abbreviations used.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  10. #10
    Join Date
    Oct 2007
    Location
    Austin Texas
    Posts
    1,989
    Post Likes
    Quote Originally Posted by timebuilder View Post
    Well, if you have the marquee displays, I would read up on the abbreviations used.
    I do have one Carrier chiller with the digital display. I'll have to take a closer look at it. Thanks.
    Nemo me impune lacessit.

    How much blood do I have to bathe in to get clean?

    Don't look down on anyone unless you're helping them up.

  11. #11
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,258
    Post Likes
    Intertwined indoor coil or split in half? what does the temp split show with both circuits on? A little more numbers and temps would get more help.