Results 1 to 4 of 4
  1. #1
    Join Date
    Sep 2013
    Posts
    11
    Post Likes

    Communnicating to a XL10 VAV via WEBs800

    Hello all,

    I'm attempting to communicate and live discover an Honeywell XL10 VAV through a WEBs 8000 running N4.6 . When I enable the local lon device and configure the comm setting for the LON module, and hit discover. I get the following error...

    Failed [11:20:58 20-Sep-19] Unexpected exception in BLonDiscoverJob.
    javax.baja.lonworks.LonException: sendNormal failed
    at com.tridium.lonworks.loncomm.NLonComm.doLonCommSen dNormal(NLonComm.java:448)
    at com.tridium.lonworks.loncomm.NLonComm.sendNormal(N LonComm.java:369)
    at com.tridium.lonworks.loncomm.NLonComm.sendUnackRep eat(NLonComm.java:354)
    at com.tridium.lonworks.util.NmUtil.setRespondToQuery (NmUtil.java:759)
    at com.tridium.lonworks.util.NmUtil.initDiscover(NmUt il.java:700)
    at com.tridium.lonworks.netmgmt.BLonDiscoverJob.doDis cover(BLonDiscoverJob.java:88)
    at com.tridium.lonworks.netmgmt.BLonDiscoverJob.run(B LonDiscoverJob.java:67)
    at javax.baja.util.Worker.process(Worker.java:168)
    at javax.baja.util.Worker$Processor.run(Worker.java:1 41)
    at java.lang.Thread.run(Thread.java:748)
    Caused by: javax.baja.lonworks.LonException: Failed transmit to lonDriver.
    at com.tridium.lonworks.loncomm.NLonLinkLayer$LonTran smitDriver.run(NLonLinkLayer.java:405)
    ... 1 more
    Caused by: java.lang.NullPointerException
    at com.tridium.platLon.BLonPlatformServiceQnx.write(B LonPlatformServiceQnx.java:106)
    at com.tridium.lonworks.loncomm.NLonLinkLayer$LonTran smitDriver.run(NLonLinkLayer.java:389)
    ... 1 more
    javax.baja.lonworks.LonException: Failed transmit to lonDriver.
    at com.tridium.lonworks.loncomm.NLonLinkLayer$LonTran smitDriver.run(NLonLinkLayer.java:405)
    at java.lang.Thread.run(Thread.java:748)
    Caused by: java.lang.NullPointerException
    at com.tridium.platLon.BLonPlatformServiceQnx.write(B LonPlatformServiceQnx.java:106)
    at com.tridium.lonworks.loncomm.NLonLinkLayer$LonTran smitDriver.run(NLonLinkLayer.java:389)
    ... 1 more
    java.lang.NullPointerException
    at com.tridium.platLon.BLonPlatformServiceQnx.write(B LonPlatformServiceQnx.java:106)
    at com.tridium.lonworks.loncomm.NLonLinkLayer$LonTran smitDriver.run(NLonLinkLayer.java:389)
    at java.lang.Thread.run(Thread.java:748)


    I'm not getting any comm lights on the module. Any ideas on what I might be doing wrong?

  2. #2
    Join Date
    Jan 2014
    Posts
    10
    Post Likes
    When you enable the local device, is the status ok?
    What is the status of your lon network?

    Sent from my SM-G930V using Tapatalk

  3. #3
    Join Date
    Jul 2009
    Location
    Wa
    Posts
    336
    Post Likes
    A lot of the X10 controllers depending on age probably were commissioned with LonSpec. Different domain length ID is something to consider.

  4. #4
    Join Date
    Sep 2013
    Posts
    11
    Post Likes
    Thread Starter
    Thank you all for the reponses. Turns out all I need to do was reboot the Station and these errors cleared up and I was able to communicate to the controller. Hate when its that easy.