Results 1 to 13 of 18
    Oct 2002
    Plano, TX
    Get the code book.
    I had a report that a contractor received a red tag for improper whip to CU. THHN conductor inside NM liquid tite not OK. Must have UF cable inside NM liquid tite conduit. Apparently, in the new mechanical code,
    Anybody know of this code?
    May 2014
    Bay Area California
    Wire rated for underground? Maybe because it has a ground wire embedded.
    Maybe that red tag was because the contractor did not pull a ground.
    If you were a real tech, you'd solder a relay on that board and call it good to go.
    I do a triple evac with nitro to remove non condensables.
    I use 56% silver on everything except steel.
    Did you really need the " If you were a real tech " ??
    New Jersey
    Was the wire dual rated THHN and THWN? I am not aware of that code, but it sounds like an inspector that does not know his job.
    Why is the mechanical inspector checking that? That is under the NEC code.
    Sent from my ASUS_P00J using Tapatalk
    Jun 2002
    Dacula, GA
    What code? National Electric Code Year?, International Mech. Code Year? etc. Give us some info. Maybe a Texas amendment to a code. Never heard of that requirement. Nothing in the IMC-2012 Edition on power to a condenser at all. Sounds like BS to me. What code books and edition is Texas using? Give a little info. Thank you very much
    Sen. Barry Goldwater
    Southeastern Pa
    The electrical part of mechanical codes is derived from the national electrical code.
    It sounds to me as though the inspector did not observe the fact that most THHN wire today is coded for multiple uses, as in THHN, THHN-2, THWN, etc.... which means that it is suitable for outdoor use, and seal tight is a correct choice for that. In addition, the seal tight is permissible for use as a ground in the code up to a certain current based upon the diameter of the seal tight becaise of the spiral metal used inside. Not all liquid tite raceway is listed for that use, so you have to know the product listing.
    Now.... it is possible that there was something about that installation which does not meet the local code, and the local code can be as restrictive as they want to make it, as long as it has been adopted into law as an ordinance of that municipality.
    So you would have to look into this further to know whether or not the failure was justified or if it was not.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Southeastern Pa
    I have to question the idea that the failure was for THHN, and that the inspector wanted UF cable instead.
    Some folks believe that NM - B uses THHN listed for outdoor use, and that is not the case. If the outer jacket says NM-B, it cannot be used anywhere outdoors...in wet or damp locations... NM-B is strictly an indoor use only cable, and the inspector may have said if you want to use an assembled cable for this application it must be UF..... and that would be correct.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Oct 2002
    Plano, TX
    Quote Originally Posted by timebuilder View Post
    So what would you use NM liquid tight (seal tite) for? Just a casing for UF or inside? Why not just forget the seal tite all together.
    I am aware that some percent of a filled conduit reduces its ampacity, but don't know if omly pertains to current carrying wires.
    Mar 2015
    Tx
    Also UF because of the jacket is limited to an amperage rateting of 60 Centigrade , 140 F.
    This must be Plano thing as I do the classroom CE and no mention of a change such as this.
    Aug 2009
    Beatrice, NE
    As I understand it you can not put romax or UF cable inside conduit because of the possibility it will get to hot from the extra jacket. If this is the case it would make no sense to put UF inside NM sealtite. No I have seen where guys will try to run sealtite metal or NM from the hole in the house into the disconnect or from disconnect into the hole in the cabinet of the equipment with no fitting on 1 end. Without that fitting it makes the inside of the conduit a wet location which would require UF or other suitable cable.
    Southeastern Pa
    The only limitation on placing a cable assembly in a raceway is adherence to conduit fill requirements. The cable dimension at it's widest is used as a conductor diameter for use with the tables in the back of the NEC book.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Mar 2015
    Hamersville, Ohio
    Quote Originally Posted by timjimbob View Post
    Huh?
    Which Mechanical Code?
    The NEC, doesn't call for UF to be run in liquid -Tite for a CU.
    Hos 4:6 My people are destroyed for lack of knowledge. Because you have rejected knowledge, I will also reject you, that you may be no priest to me. Because you have forgotten your God’s law, I will also forget your children.
    "You've got to Stand for Something or You'll fall for anything" (A. Tippin)
    Mat_15:24 But he answered, “I wasn’t sent to anyone but the lost sheep of the house of Israel.”
    Southeastern Pa
    Quote Originally Posted by DavidDeBord View Post
    Huh?
    First, we are not getting the full story. The OP got it second hand.
    Next, imagine the contractor saying, "I want to just put a cable in the sealtite. What will you accept?"
    The code guy says, "you can put UF in there if you want to install a cable."
    Bottom line....if the THHN was manufactured in the last 10 years, it is most likely coded for all THHN variants
    it IS possible that he bought a bunch of discount whips that are not mult- use coded, too.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Jan 2010
    Everyone here knows that you can buy pre made whips that are UL rated. Yes they have THHN wire inside and not cable.