    Niagara graphics: displaying point values without the status?

    Displaying some points and I'm stuck with either a naked number when I use the out:value slot, or a number with units and then the {OK} status appended. All I want is xxx CFM or XX degrees F. Is there an easy method for displaying values with units without the status?

  2. #2
    Join Date
    Sep 2002
    Location
    Hampton Roads, Virginia
    Posts
    1,995
    Post Likes
    Add "Units" facet to the point, then use %out.value% on the px page

    Controls is a lifestyle not a job

  3. #3
    Join Date
    Mar 2018
    Posts
    74
    Post Likes
    Thread Starter
    Quote Originally Posted by klrogers View Post
    Add "Units" facet to the point, then use %out.value% on the px page
    They already have the units facet. Using: Point_TEMP/out/value returns a bare number, no units.

  4. #4
    Join Date
    Sep 2002
    Location
    Hampton Roads, Virginia
    Posts
    1,995
    Post Likes
    Have you animated the text?
    Attached Images Attached Images   

    Controls is a lifestyle not a job

  5. #5
    Join Date
    Mar 2018
    Posts
    74
    Post Likes
    Thread Starter
    Quote Originally Posted by klrogers View Post
    Have you animated the text?
    Haven't tried that yet, but looks like it'll work. Thank you very much for the help.