    York micro channel vs tube-in-fin heat exchangers

    I'm getting someone to replace our extremely old (28 years) furnace and AC, and was quoted a York A/C condenser unit with a micro channel heat exchanger. The tube-in-fin option is about $ more, should I consider paying more? Dealer says micro channel is fine and I'm being silly, but I can't help to question why their top end models only come with tube-in-fin.

    I know they settled their lawsuit, but I'm more interested in a general: "which is better" response, and nobody would know better than the people who regularly work on them.

    Located in Ontario, Toronto area if it has any impact.

    Hoping this topic has not been discussed to death, I did a google search and didn't find a definitive answer.

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    I wouldn't want microchannel. Seen too many leaks. Funny that York brought back plate fin tube coils on a few of their models. Dealers must have been complaining.

  3. #3
    Join Date
    Mar 2018
    Location
    Cottonwood, Ca #StateofJefferson
    Posts
    2,187
    Post Likes
    If you didn't have any reason to worry, then why is York upselling their tube and fin coils? I wouldn't use a microchannel anything.

  4. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,735
    Post Likes
    Somethings wrong.
    We use a lot of micro channels in refrigeration and I’ve only had 1 failure!

  5. #5
    Join Date
    Jan 2008
    Location
    Texas
    Posts
    7,957
    Post Likes
    Another vote for no on the micro channel. I have had several Guardians which came from the York distributor leak where the aluminum meets with the copper.

  6. #6
    Join Date
    Sep 2019
    Location
    Ontario, GTA
    Posts
    2
    Post Likes
    Thread Starter
    Thank you all for the input, I decided to pay extra and get the tube-in-fin model.

  7. #7
    Join Date
    Mar 2018
    Location
    Cottonwood, Ca #StateofJefferson
    Posts
    2,187
    Post Likes
    I should clarify, I dislike MC because they clog up pretty quickly with all the tree dandruff we have in my area. A lot of my commercial accounts with mc need a washing every 60 days or they dont keep up or start shutting dow on high pressure safeties, so maintenance is more critical imo on mc coils. I do appreciate the smaller refrigerant charge that comes with mc coils though

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •