good pressures and super heat but will not cool
i have this fixed orfice heat pump. all my pressures are great. my super heat is on target, but the damn thing isnt cooling that well. its got me stumped, mit really makes no since
-
-
With EVERYTHING being "great" I gonna say this so called problem is just a figment of your imagination.
-
Post Likes - 2 Likes, 0 Dislikes
-
So as there are no numbers to go off of or anything other than it's all good we will just have to take your word for it and say good job getting the numbers correct...
-
Lets see the numbers...
We will evaluate whether they are good or not.
That is what we are here for.
-
-
Pressures great
Super Heat perfect
Nothings wrong
Here's my bill!
-
Originally Posted by
slickster
i have this fixed orfice heat pump. all my pressures are great. my super heat is on target, but the damn thing isnt cooling that well. its got me stumped, mit really makes no since
Gonna need a lot more information than just this to determine what or if there is an issue
-
"Something is rotten in the state of Denmark."
[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES CMS, HVAC Electrical Specialist
Member, IAEI
AOP Forum Rules:
-
That's where tools like the fieldpiece charge and air flow probes come in handy. Look up blower performance and BTU output of the unit,measure air flow and change in enthalpy and you know exactly what it's putting out vs what it is rated for.
-
Start with model and serial numbers, orifice type, then blower speed and static pressure, and refrigerant pressures with superheat and sub cool.
-
@slickster
I guess you get the point!
Good
Target
Perfect
Within range
Just doesn't cut it. Get back to us with facts and figures.
-
Did ya check to see if a heat strip was stuck on?
-
WELL WELL Terry, you are 100% right. lol. it was just so damn hot that day. it was like 101 outside and that attic was weldong worthy. , but anyway
the next morning i went back and it was chilling like a villan,