Thread: First time for everything

  1. #1
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    5,579
    Post Likes

    First time for everything

    Had a call that the condenser was kicking the breaker as soon as it came on. Customer called an electrician and was told it was most likely a shorted compressor. I was thinking maybe bad breaker. So I ask her what size and make and pick one up on the way to the call.

    Get there and check condenser first. Pull cover and see capacitor bulging. Check Mf =0. Put in new cap and all is well.

    Just never saw a bad run cap trip a breaker before.

    Guess there is a first time for everything.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

  2. #2
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,873
    Post Likes
    Maby its internal overload didnt trip quick enough. It seems that breakers blow a lot faster than fuses.
    Quote Originally Posted by joemach View Post
    Had a call that the condenser was kicking the breaker as soon as it came on. Customer called an electrician and was told it was most likely a shorted compressor. I was thinking maybe bad breaker. So I ask her what size and make and pick one up on the way to the call.

    Get there and check condenser first. Pull cover and see capacitor bulging. Check Mf =0. Put in new cap and all is well.

    Just never saw a bad run cap trip a breaker before.

    Guess there is a first time for everything.
    Sent from my rotary telephone using Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  3. #3
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    5,579
    Post Likes
    Thread Starter
    Quote Originally Posted by R600a View Post
    Maby its internal overload didnt trip quick enough. It seems that breakers blow a lot faster than fuses.

    Sent from my rotary telephone using Tapatalk
    No fuses. Non fused disconnects are popular around here, except if they are real old.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

  4. #4
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,873
    Post Likes
    I mentioned fuses because it seems they dont blow as often from things like that. I see breakers trip much more often. I was thinking that a fuse would likely not have blown in a similar situation.
    We have more fuses here.

    Sent from my rotary telephone using Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  5. #5
    Join Date
    Jun 2012
    Location
    Ahoskie NC
    Posts
    166
    Post Likes
    I have seen that one a couple of times this year. Strange though.

  6. #6
    Join Date
    Feb 2015
    Location
    Coastal South Carolina
    Posts
    384
    Post Likes
    How did the Capacitor ohm to ground?

  7. #7
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    5,579
    Post Likes
    Thread Starter
    Quote Originally Posted by safebustr View Post
    How did the Capacitor ohm to ground?
    That is a great question. I never even thought about testing that.

    Thanks for making me think.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

  8. #8
    Join Date
    Mar 2018
    Location
    Kansas Flatlands
    Posts
    833
    Post Likes
    Quote Originally Posted by R600a View Post
    Maby its internal overload didnt trip quick enough. It seems that breakers blow a lot faster than fuses.

    Sent from my rotary telephone using Tapatalk
    Intresting point but it seems that way to me also. 30 yrs ago we changed a lot more fuses, especially after a lightning storm. May be these HACKR rated breakers today, don't know. Strange because now we have widespread use of scroll compressors which seem to have a higher LRA rating than that of the old recips.

  9. #9
    Join Date
    Aug 2018
    Location
    Piedmont Triad, NC
    Posts
    891
    Post Likes
    Just had one 45 mins ago was the same problem. ~12 year old carrier with swollen capacitor and tripped breaker. It’s rare but I think I’ve had two others like it this year. I think the internal overload is taking too long to trip so the breaker steps in, or it’s a slightly weak breaker.

  10. #10
    Join Date
    Aug 2018
    Location
    Piedmont Triad, NC
    Posts
    891
    Post Likes
    Oh, and it had a fused disconnect with good fuses.

  11. #11
    R600a's Avatar
    R600a is offline Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    31,873
    Post Likes
    We had a trane snowball with a bad start relay that was drawing like 90 amps a second at a time till it would shut off on internal overload and it never blew the 30 amp fuses

    Sent from my rotary telephone using Tapatalk
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  12. #12
    Join Date
    Sep 2019
    Posts
    6
    Post Likes
    Run across this maybe 5 times a year. Also run across the breaker tripping for no "apparent" reason sometimes. Both seem related.

  13. #13
    Join Date
    Jul 2013
    Location
    Richmond, VA
    Posts
    6,027
    Post Likes
    I wonder if the plates inside the capacitor hit the wall, which would ground through the frame. If you still got it, check resistance between each terminal and the outside of the cap.

  14. #14
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    5,579
    Post Likes
    Thread Starter
    Quote Originally Posted by CircusEnvy View Post
    I wonder if the plates inside the capacitor hit the wall, which would ground through the frame. If you still got it, check resistance between each terminal and the outside of the cap.
    Sorry tossed it. Wish I saved it.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

  15. #15
    Join Date
    Dec 2015
    Location
    Ohio
    Posts
    28
    Post Likes
    That was my first thought, shorted cap. I’ve seen it a few times. Other things I would look at too are wire size to unit, tightness of electrical connections, condition of contactor points. Is the breaker properly sized according to MOP on nameplate with properly sized conductors. I always look for stupid stuff

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •