    Walk in cooler call unbelievable 🤦*♂️

    Cooler wasnt working. New customer. Suction pressure/temp was off. 404a box. Something wasnt right. Sight glass clear and saturation temp was the same as my box temp. WTF? Was with my nephew so was the perfect call to check what the superheat and valve was doing and show him how to adjust it. Till I noticed there was NO TXV. WTF? I looked again, and told him something is very wrong or Im going to learn something. Double take at solenoid valve. Electronic? NO. Started asking customer questions he said wasnt going below 45 and was working right. I asked when box was installed. 10 years ago. Then he said well no the coil was just installed 2 years ago, was working fine. Ya right. I was going thru paperwork looking for info. He then said who installed it and said the company that did was on Lafayette Avenue. I told nephew button it up and get me model numbers, and then told customer ummmm sorry its never worked right and I know who the company is on Lafayette, and I use company loosely. I told him its never worked right and the dumb SOB forgot to install the TXV. I sent it over to my supplier and in email I said Brian I think Im missing something can you help. He calls me laughing, I think hes still laughing. Never in 25 years or his 30 years have I seen something like this. Im assuming this appliance guy and his gang of hacks thought the distributor nozzle was a metering device. LOL I just cant believe this. Box got down to 45 ish and has been running non stop for 2 years. Who in the F does shit like this? The valve was with equipment supplier checked and I saw packing slip. Wall of shame
    Attached Images Attached Images  

  2. Likes trippintl0, bacciagalupe liked this post.
  3. #2
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    We don't need no expansion valve!!!
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  4. #3
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes

  5. #4
    Join Date
    Oct 2014
    Location
    Columbus, Ohio
    Posts
    1,507
    Post Likes
    I can only imagine the thought process rattling around his thick noggin: "It's a big cooler, so these giant cap tubes are supposed to be big as well, right?" LOL

  6. #5
    Join Date
    Apr 2010
    Location
    California
    Posts
    717
    Post Likes
    Quote Originally Posted by Iceman_pdx View Post
    Cooler wasnt working. New customer. Suction pressure/temp was off. 404a box. Something wasnt right. Sight glass clear and saturation temp was the same as my box temp. WTF? Was with my nephew so was the perfect call to check what the superheat and valve was doing and show him how to adjust it. Till I noticed there was NO TXV. WTF? I looked again, and told him something is very wrong or Im going to learn something. Double take at solenoid valve. Electronic? NO. Started asking customer questions he said wasnt going below 45 and was working right. I asked when box was installed. 10 years ago. Then he said well no the coil was just installed 2 years ago, was working fine. Ya right. I was going thru paperwork looking for info. He then said who installed it and said the company that did was on Lafayette Avenue. I told nephew button it up and get me model numbers, and then told customer ummmm sorry its never worked right and I know who the company is on Lafayette, and I use company loosely. I told him its never worked right and the dumb SOB forgot to install the TXV. I sent it over to my supplier and in email I said Brian I think Im missing something can you help. He calls me laughing, I think hes still laughing. Never in 25 years or his 30 years have I seen something like this. Im assuming this appliance guy and his gang of hacks thought the distributor nozzle was a metering device. LOL I just cant believe this. Box got down to 45 ish and has been running non stop for 2 years. Who in the F does shit like this? The valve was with equipment supplier checked and I saw packing slip. Wall of shame
    Thank You Much, for Sharing, and Making My end of Day! Take Care!

  7. #6
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    His bid was one TEV cheaper

  8. #7
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    5,579
    Post Likes
    How the heck was that thing keeping temp?
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

  9. Likes UmmScott liked this post.
  10. #8
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Txv's are for sissies

  11. #9
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    3,814
    Post Likes
    Did it even have a nozzle?

    Could be the only way it somewhat worked

    Sent from my SM-G975U using Tapatalk

  12. #10
    Join Date
    May 2003
    Location
    Utah
    Posts
    921
    Post Likes
    Must have been the same "company" that installed this amazing WI Box door (which was purchased at Home Depot).

    Low bid.

    Name:  WI Box Door.jpg
Views: 754
Size:  33.2 KB

  13. Likes icemeister, icy78, bacciagalupe, Turtleman liked this post.
  14. #11
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Quote Originally Posted by UmmScott View Post
    Did it even have a nozzle?

    Could be the only way it somewhat worked

    Sent from my SM-G975U using Tapatalk
    I recall this being reported here on Htalk once or twice before. If they "worked" at all, they would definitely need to have a distributor nozzle installed.

  15. #12
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    5,579
    Post Likes
    Quote Originally Posted by icemeister View Post
    I recall this being reported here on Htalk once or twice before. If they "worked" at all, they would definitely need to have a distributor nozzle installed.
    Some sort of nozzle may be making it work. The OP should check for that before putting in the TXV. Don't need 2 metering devices on one system.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

  16. #13
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Quote Originally Posted by joemach View Post
    Some sort of nozzle may be making it work. The OP should check for that before putting in the TXV. Don't need 2 metering devices on one system.
    Actually, with a pressure-drop type of distributor like the ones made by Sporlan, you DO need both the TXV and the nozzle. The nozzle isn't there as a metering device per se. It's needed for equal distribution and it must be accounted for when selecting a TXV because it significantly affects the available pressure drop.

  17. #14
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    5,579
    Post Likes
    Quote Originally Posted by icemeister View Post
    Actually, with a pressure-drop type of distributor like the ones made by Sporlan, you DO need both the TXV and the nozzle. The nozzle isn't there as a metering device per se. It's needed for equal distribution and it must be accounted for when selecting a TXV because it significantly affects the available pressure drop.
    Good to know. Thanks!
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

  18. #15
    Join Date
    Jan 2019
    Location
    EU
    Posts
    76
    Post Likes
    Quote Originally Posted by icemeister View Post
    Actually, with a pressure-drop type of distributor like the ones made by Sporlan, you DO need both the TXV and the nozzle. The nozzle isn't there as a metering device per se. It's needed for equal distribution and it must be accounted for when selecting a TXV because it significantly affects the available pressure drop.
    Do you have some document or a link where where this is explained a bit more? Thanks.

  19. #16
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Quote Originally Posted by BobFrost View Post
    Do you have some document or a link where where this is explained a bit more? Thanks.
    Sporlan Bulletin 20-10 / Refrigerant Distributors: (See p.2-4)

    https://www.parker.com/literature/Sp...=10085&elqat=2

    Heatcraft - Refrigerant Distribution:

    https://icemeister.net/backroom/dist...t-distribution

  20. #17
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Quote Originally Posted by BobFrost View Post
    Do you have some document or a link where where this is explained a bit more? Thanks.
    some new evaps come with a little bag with 2 nozzles you choose from

    it looks like a metal donut

    You shove the nozzle into the pipe , then a clip , then braze on txv

  21. #18
    Join Date
    Oct 2009
    Location
    Raleigh, NC
    Posts
    1,022
    Post Likes
    That system had a metering device. You can tell by looking at the u-bends and the green corrosion. The last few passes of each circuit have never really been much below the cold room temp and they don't sweat and oxidize.

    Sent from my Pixel 2 using Tapatalk

  22. #19
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Quote Originally Posted by MicahWes View Post
    That system had a metering device. You can tell by looking at the u-bends and the green corrosion. The last few passes of each circuit have never really been much below the cold room temp and they don't sweat and oxidize.

    Sent from my Pixel 2 using Tapatalk
    The caps off the distributor are feeding the top.
    Or what would be the front had the picture been turned.
    Attached Images Attached Images  

  23. #20
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,452
    Post Likes
    I found an AC with no metering devices.

    And believe it or not, it was at NASA. You know how those rocket scientists are, LOL.

    Long time ago, so can't remember all of the details. Think is was a 20 ton AC with one semi Copeland compressor and two evap circuits. Can't even remember what the original call was. May have been tripped on oil pressure, or may have been a dead compressor.

    Installed maybe ten years prior to me seeing it.

    When I reported back to the HMFIC, he said no way. I said, way.

    Virtually every tech and higher up had to go look at it to verify. Yup, no TEV.
    I do a triple evac with nitro to remove non condensables.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •