    30hxc T026-027

    I have been getting these T026 and T027 alarms. I am pretty sure it is a little low on freon just want to verify with yall. The only think i not sure of is do i need to add some oil to it. Circuit a i can not see the oil in the sight glass though . Thanks for any help . I attache the pic of the reading form my I-vu system Click image for larger version. 

Name:	Screen Shot 2019-08-29 at 11.23.07 AM.png 
Views:	89 
Size:	635.5 KB 
ID:	811028

  2. #2
    Join Date
    Aug 2000
    Location
    Under my tree
    Posts
    5,133
    Post Likes
    You've got a 5F evap approach, Looks to be short on gas. JMHO
    To much work with too little time!!!!

  3. #3
    Join Date
    May 2012
    Location
    California
    Posts
    683
    Post Likes
    The book tells you how to get the oil back unless you found it all over the floor.

    It's in your evap

    Sent from my SM-G960U using Tapatalk

  4. #4
    Join Date
    Feb 2010
    Location
    montreal
    Posts
    296
    Post Likes
    Quote Originally Posted by Jeremy325 View Post
    I have been getting these T026 and T027 alarms. I am pretty sure it is a little low on freon just want to verify with yall. The only think i not sure of is do i need to add some oil to it. Circuit a i can not see the oil in the sight glass though . Thanks for any help . I attache the pic of the reading form my I-vu system Click image for larger version. 

Name:	Screen Shot 2019-08-29 at 11.23.07 AM.png 
Views:	89 
Size:	635.5 KB 
ID:	811028
    How do you know you need refrigerant?

    I only see part of the data needed to arrive to that answer.

    Put some meat on the bone if you want help.

    No offense meant but I'm wondering how often you have worked on a chiller.
    Have you read the manual?

  5. #5
    Join Date
    Apr 2007
    Location
    uk
    Posts
    285
    Post Likes
    The EXV position is under 60% operation can be anywhere between 40% and 60% normally being towards the 40% end. Over 60% would be classed as low on refrigerant. All these checks including subcool are done at 100% load and as close to your chiller setpoint variations of water flow including condenser flow can vary the subcool. With the readings your given the low oil pressure problem is not charge related.

    Gibbo

  6. #6
    Join Date
    Dec 2011
    Location
    TN
    Posts
    50
    Post Likes
    Thread Starter
    Click image for larger version. 

Name:	Screen Shot 2019-09-18 at 1.45.14 PM.jpg 
Views:	33 
Size:	76.6 KB 
ID:	811493Click image for larger version. 

Name:	Screen Shot 2019-09-18 at 1.46.36 PM.png 
Views:	32 
Size:	738.0 KB 
ID:	811494Click image for larger version. 

Name:	Screen Shot 2019-09-18 at 1.46.43 PM.png 
Views:	31 
Size:	350.6 KB 
ID:	811495

  7. #7
    Join Date
    Dec 2011
    Location
    TN
    Posts
    50
    Post Likes
    Thread Starter
    maybe this is enough info to help.

  8. #8
    Join Date
    May 2018
    Location
    VA/DC
    Posts
    235
    Post Likes
    Quote Originally Posted by Jeremy325 View Post
    maybe this is enough info to help.
    have you looked into the things people mentioned?

    this is 134a right? by your temp drop you have way to much flow or low refrigerant. By the condenser temp rise its low. You're at 100% load with a 4 deg temp rise on the condenser. I doubt the pumps are flowing 3 times what you need so low on charge. I need to see a pt chart to see what the super heat is.

    Low refrigerant will reduce oil return with can make it trip the low level alert. How much experience do you have working on chiller?

  9. #9
    Join Date
    Feb 2010
    Location
    montreal
    Posts
    296
    Post Likes
    Quote Originally Posted by Jeremy325 View Post
    maybe this is enough info to help.
    How many compressor per circuit?

    If you want to get the data needed take the same reading at 100% on all circuit.
    With water temp.
    Have you read the manual about oil return procedure?