+ Reply to Thread
Results 1 to 12 of 12
Thread: JCI VMA-1620 - I'm not able to write setpoints to it.
    Jul 2018
    New England
    I am trying to integrate a number or these VAVs under a new Jace, they are currently on a Metasys system which is going away.
    There are AHUs and VAVs. I can write to all setpoints on the AHUs, but on the VAVs I get faults when I try to write to setpoints like:
    - Occ Cool Stpt
    - Occ Heat Stpt
    - Min Occ Cool CFM
    - Max Occ Cool CFM
    I only found one setpoint I could write to, something like ZoneSP. (but not Occ Cool Stpt, etc)
    I have tried writing at different priorities, no luck.
    Any ideas of what's going on here?
    Thanks!
    Mar 2009
    Several Miles from Sane
    Try changing the "Present Value" field to "3113" and see if that works.
    If sense were so common everyone would have it !
    You cannot protect the Stupid from themselves !
    "Experience is the ability to recognize a mistake Before you make it again!" (Stolen Quote)
    Jul 2018
    New England
    hi KG,
    Unfortunately, I'm no longer at the site but will make another visit before too long.
    From the jace I've been trying to write a new value at various priorities with no luck.
    Are you thinking the point may not have a pri array, and therefore those writes may not work?
    I'm not sure how to write to the present value without a priority. Can you do that from workbench?
    And while we're at it, is their significance to 3113?
    thanks a lot!
    Jan 2003
    Quote Originally Posted by CtrlPuffer View Post
    Ever use the fallback slot on a writable point? That's exactly what tridium does with BACnet.
    Its a little game JCI plays to waste your time. You need to change the property your working with to 3113 from present value and forget about priorities as they have nothing to do with your problem.
    Quote Originally Posted by Cagey57 View Post
    Jul 2018
    New England
    ah ha. Glad I asked again as I didn't get it the first time.
    Thank you both. So JCI invented property 3113 and uses it instead of the BACnet present value (I believe property 85)
    I will certainly try that!
    Jul 2018
    New England
    The other impediment to moving the devices to the jace is that about 10 of the devices have device instance = 1.
    Do you think the utility in workbench for changing device number will work on the JCI devices? Somehow I doubt it will, and I'm afraid to try it while the system is still operating under the old system. I'm pretty sure I could not set device instance back to device 1 with 9 other devices at that same instance number.
    Jan 2003
    JCI's signature game....make all the instance's the same number.
    Device instance is not writable, so you cannot just change in Tridium that I'm aware of. Could be another hidden property for this but I assume you will need PCT/CCT.
    Jul 2018
    New England
    they are good... I was thinking the instances probably could not be changed from "the outside."
    I will see if we have those tools on the workstation. If not we may have to trash those devices, unfortunately.
    Appreciate the good advice!
    Mar 2018
    South East US
    What’s different about 3113?
    If the point is an activity input or output the only way I’ve m known to change them was to change them to write on the relinquish default property instead of present value. Downside is overrides and then going back to auto does not put the values back.
    Jul 2018
    New England
    thanks bolt, I'll test just using the relinquish default (fallback) of the actual point property 3113, and have a psuedopoint exposed to the user which can be locked etc. The psuedopoint will write to the actual point.
    Jan 2010
    Just to clarify, you need to change the point's proxy ext Property Id from the default of "Present Value" to "3113"
    Mar 2018
    South East US
    Quote Originally Posted by legionrider View Post
    What’s 3113?
    I’ve tried typing it in and got faults. However if i select relinquish default, that works.
    Anyways I just make network inputs instead as they take overrides better.