Thread: Walk-in Freezer Superheat

  1. #1
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes

    Walk-in Freezer Superheat

    Ok its not running right

    Ok so I went with a 7000 btu evap by Trenton TPLP207LE-S2B-R6 according to the sheet i saw online

    ( dealer called it a 7500 for some reason )

    Compressor is

    5170 BTUH @ -20 SST @ 90 AMB
    7160 BTUH @ -10 SST @ 90 AMB

    a day later it wont pull below 15 , just hovers there

    I go check it out

    Ambient outside 80

    High 265

    Low 42

    Line Temp 15 ( at pump )

    So I have 5 deg SH

    Had some bubbles so I topped it off , no change

    Evap clean , no snow

    Crank the TXV ( in ) a bunch of turns , didnt see much change

    Turn all way in , back out 1 turn ( i dont like to leave them snugged in )

    Low 38 psi , Line Temp 11

    STILL 5 DEG SH



    Didnt check SC , but the filter felt like your typical warm drier

    Lineset length 12 ft
    Attached Images Attached Images  
    Last edited by Snapperhead; 08-23-2019 at 05:19 PM.

  2. #2
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Thread Starter
    aint the neatest , but its functional

    AND its a 6 x 8 x 7 box

    I was guessing on the original post
    Attached Images Attached Images  

  3. #3
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    My initial thought says the TXV isn't doing what it's supposed to do...ie, control superheat.

    Did somebody assemble this valve for you and forget to put a cartridge in it? I've heard of that before.

  4. #4
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Thread Starter
    It come pre-assembled , i tore out the old evap , and just hung the new

    I strapped the bulb directly outside the cabinet

  5. #5
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Quote Originally Posted by Snapperhead View Post
    It come pre-assembled , i tore out the old evap , and just hung the new

    I strapped the bulb directly outside the cabinet
    Never trust, therefore verify. Replace the valve.

  6. #6
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    I once forgot to tighten down the cartridge in a Sporlan Q valve and got the same kind of floodback.

  7. #7
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    BTW...I've asked for this to be moved to a new thread.

  8. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Made this its own thread.

  9. Likes icemeister liked this post.
  10. #9
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    The TXV came with assembled to the evaporator coil -

    Is there sub cooled liquid refrigerant at the TXV inlet?

    Is the TXV bulb's full length snug and secure to the suction line?

    If the TXV correct for the system's refrigerant?

    If three yes answers the TXV is defective or the inlet screen is plugged.

    PHM
    --------


    Quote Originally Posted by Snapperhead View Post
    Ok its not running right

    Ok so I went with a 7000 btu evap by Trenton TPLP207LE-S2B-R6 according to the sheet i saw online

    ( dealer called it a 7500 for some reason )

    Compressor is

    5170 BTUH @ -20 SST @ 90 AMB
    7160 BTUH @ -10 SST @ 90 AMB

    a day later it wont pull below 15 , just hovers there

    I go check it out

    Ambient outside 80

    High 265

    Low 42

    Line Temp 15 ( at pump )

    So I have 5 deg SH

    Had some bubbles so I topped it off , no change

    Evap clean , no snow

    Crank the TXV ( in ) a bunch of turns , didnt see much change

    Turn all way in , back out 1 turn ( i dont like to leave them snugged in )

    Low 38 psi , Line Temp 11

    STILL 5 DEG SH



    Didnt check SC , but the filter felt like your typical warm drier

    Lineset length 12 ft
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  11. #10
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,736
    Post Likes
    Good Job!

  12. #11
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Is there a question in here somewhere ?
    As for the head line ..... I like 4-6 @ the evaporator.
    Last edited by VTP99; 08-23-2019 at 07:34 PM.

  13. #12
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Wait a minute, if he's flooding back the coil can't be starving.

  14. #13
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    Oh you're right - doing too many things at once here. Delete my inlet screen reference. <g>

    Can you think of any thing else I have overlooked?

    Quote Originally Posted by VTP99 View Post
    Wait a minute, if he's flooding back the coil can't be starving.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  15. #14
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    What's the defrost setup ?
    Personally I'd eliminate them till frost shows up.
    Also what were the TEV spec's ?

  16. #15
    Join Date
    Jun 2005
    Location
    Atlanta - Retired
    Posts
    1,250
    Post Likes
    What is the compressor number?

  17. #16
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Thread Starter
    Walkin freezer super heat is pretty effective when set right

  18. #17
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Thread Starter
    CF06K6E-PFV-25S

  19. #18
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Thread Starter
    Quote Originally Posted by VTP99 View Post
    What's the defrost setup ?
    Personally I'd eliminate them till frost shows up.
    Also what were the TEV spec's ?
    4 times a day 30 min

    TEV specs ? I asked for a 404a coil

    I glanced at the power head , its a zp with 404 label

    Didnt take amp readings

    He just called said its holding 11 deg

    I told him shutter down until i can get back tomoro

    I will yank that TXV apart

  20. #19
    Join Date
    Jan 2010
    Posts
    45,371
    Post Likes
    Did you by chance get a amp reading ?
    Attached Images Attached Images  

  21. #20
    Join Date
    Aug 2009
    Location
    Maine
    Posts
    8,146
    Post Likes
    Quote Originally Posted by VTP99 View Post
    Is there a question in here somewhere ?
    As for the head line ..... I like 4-6 @ the evaporator.
    I use 5. look for 30 or less at compressor

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •