    I was given specs of the coil. Freeze pump i was told to design at 1/3 of gpm of coil
    51gpm coil
    17gpm at 15ft/hd
    Went on wilo website, plugged in numbers and found the smallest pump i could use.
    Southold, NY
    A job the fitters are doing for us.
    The labor savings more then make up for the cost of the fittings!
    Apr 2003
    St. Louis
    Installation looks good but a power failure coils done. Plate hx pump and expansion tank and glycol the only 100% way for protection.
    Jul 2009
    Columbia, MD
    Quote Originally Posted by servicefitter View Post
    Thats a pretty good idea.
    If they just switched to glycol. Everything would be good
    Oct 2016
    What protects the waterside of your system when the power failure occurs? Our coil is good, but the boiler and our new hxger are leaking water....
    Apr 2003
    St. Louis
    Quote Originally Posted by gravity View Post
    Problem with whole system treated with glycol is more pump is needed, less heat transfer ,cost of glycol and the maintaince.
    May 2009
    SC
    The unit has a freeze stat that;
    Closes o/a damper. Opens control valve 100%. Shuts the fan off.
    I tested operation and verified it worked. First time seeing the unit, the county takes care of it.
    I installed new coil and a freeze pump per their request.
    And it still froze? This is the cooling coil right? Do they not bring on the CHW pumps in freezing conditions?
    One theory; if the damper isn't darn near perfect the other units running in the building may still pull OA through the unit causing things to freeze.
    Scott Jalbert, WebCTRL ninja, Naiagara AX and EcoStruxure Building Expert newb, SiteScan Retired
    The master has failed more times than the beginner has even tried
    Jul 2009
    Columbia, MD
    After pictures if insulation
  9. Likes chander liked this post
  10. #22
    Oct 2014
    Columbus, Ohio
    Fantastic job. Did you do that or did you call in an insulator?
  11. #23
    Jul 2009
    Columbia, MD
    Quote Originally Posted by rjk_cmh View Post
    Had the pros do it
    Union insulators
  12. #24
    to bad all those thin purple wires could not be put in conduit would really make this thing look grate
  13. #25
    Jul 2009
    Columbia, MD
    Quote Originally Posted by pctech View Post
    They could have came thru the floor and kept them low, go around the unit to the right and behind and back up.
    I agree, it does look like crap. Lazy IT guys
  14. #26
    Southold, NY
    Damn Nice Work.
    Makes you appreciate other people’s trade skills!