Results 1 to 13 of 34
    Jul 2009
    Columbia, MD
    Freeze pump on 100% OAU
    Installed a freeze pump for a 100% OAU. Dual temp coil. It has frozen 2 years in a row. More pics to come.
    Motor starter has HOA. Hand runs pump 24/7. Auto runs thru a Tstat set at 40* to run the pump even unoccupied.
    Jul 2009
    Columbia, MD
    New piping from the tee on the supply to the bottom of the actuator flange on return
    Oct 2016
    What happens if the pump knocks off? There should be a freeze stat to shut off the fan and open the valve for full flow if the temp get below 38 deg anywhere in the air stream. Just finished a similar job and I had the control guys bring the pumps on at 45 deg just to make sure no freeze stat trips.
    Face and bypass coils are the best for 100% oa units. Just open the valve 100% and modulate how much air goes through the coil. Especially with a steam coil.
    Pipe work looks good.
    Jul 2009
    Columbia, MD
    The unit has a freeze stat that;
    Closes o/a damper. Opens control valve 100%. Shuts the fan off.
    I tested operation and verified it worked. First time seeing the unit, the county takes care of it.
    I installed new coil and a freeze pump per their request.
    Jul 2009
    Columbia, MD
    Nov 2014
    Northern Idaho
    That is some clean work Gravity!
    Nice job on adding OC protection to the control circuit since it leaves the panel
  7. Likes gravity liked this post.
  8. #7
    use oily rag on pipe to prevent solder drips?
    Keep it simple to keep it cool!
  9. #8
    Jul 2009
    Columbia, MD
    Quote Originally Posted by stanbyyourword View Post
    Just dont drip
  10. #9
    Good job then 😎
  11. #10
    Jul 2009
    Columbia, MD
    Good job then
    Actually, if i have a drip about to occur, i wipe/flick it with my finger on my pants. Lol
  12. #11
    Southold, NY
    Pro Press all the way now!
    Nice Job as well!
  13. #12
    Jul 2009
    Columbia, MD
    Nice Job as well!
    Dislike
  14. #13
    Nov 2014
    Northern Idaho
    Quote Originally Posted by gravity View Post
    Dislike
    curious what type of solder you use?
    How did you select the pump?