Results 1 to 10 of 10
  1. #1
    Join Date
    Jun 2019
    Location
    Viet Nam
    Posts
    6
    Post Likes

    Help!!! Water cooled chiller

    Please tell me this chiller is working normally or not?
    Why is the Approach temp is 1.2
    Click image for larger version. 

Name:	20190820_151350[1].jpg 
Views:	106 
Size:	45.8 KB 
ID:	810865

  2. #2
    Join Date
    Aug 2019
    Location
    LA
    Posts
    21
    Post Likes
    44 & 41.9 = 2.1
    So yes it’s 1.2c diff do not calculate

  3. #3
    Join Date
    Jun 2008
    Location
    Windsor, Ont.
    Posts
    778
    Post Likes
    I think what you need to know is what “Approach” means. It is the difference between leaving water temperature and saturated refrigerant temperature. 6.7C - 5.5C =1.2C. This is a common measurement used to determine efficient heat transfer, the lower the approach the better.

  4. #4
    Join Date
    Jun 2019
    Location
    Viet Nam
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by nyrb View Post
    I think what you need to know is what “Approach” means. It is the difference between leaving water temperature and saturated refrigerant temperature. 6.7C - 5.5C =1.2C. This is a common measurement used to determine efficient heat transfer, the lower the approach the better.
    hi,
    I know approach means. But this is a new chiller, we just running about 100 hours.
    Approach temp of Condensor is 0 C and Approach temp of Evap is 1.2 C now.
    Do you think the refrigerant charge is not enough?

  5. #5
    Join Date
    Jun 2019
    Location
    Viet Nam
    Posts
    6
    Post Likes
    Thread Starter
    hi bro, Approach temp on the Evap side is 1.2 C I think is true.
    What is 44 & 41.9?

  6. #6
    Join Date
    Jun 2019
    Location
    Viet Nam
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by HYP1278 View Post
    44 & 41.9 = 2.1
    So yes it’s 1.2c diff do not calculate
    hi bro, Approach temp on the Evap side is 1.2 C I think is true.
    What is 44 & 41.9?

  7. #7
    Join Date
    Jun 2008
    Location
    Windsor, Ont.
    Posts
    778
    Post Likes
    Being a new chiller you should have all design information readily available from the manufacturer. Most chillers today are designed for very low approach temperatures of 0.5 to 1.0 C but there are many factors that can affect approach. Incorrect flow, load conditions, glycol, commissioning, refrigerant charge etc. Assuming you had a factory rep provide a proper startup it should all be detailed in their startup report.

    The design info should tell you what design flow, differential pressure and approach is supposed to be at full load conditions and sometimes they give you part load numbers as well. Find that information and that should point you in the right direction.

    The 44 and 41.9 numbers on the other post are Fahrenheit equivalents of your readings, most people on this forum do not work in metric.

  8. #8
    Join Date
    Jun 2019
    Location
    Viet Nam
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by nyrb View Post
    Being a new chiller you should have all design information readily available from the manufacturer. Most chillers today are designed for very low approach temperatures of 0.5 to 1.0 C but there are many factors that can affect approach. Incorrect flow, load conditions, glycol, commissioning, refrigerant charge etc. Assuming you had a factory rep provide a proper startup it should all be detailed in their startup report.

    The design info should tell you what design flow, differential pressure and approach is supposed to be at full load conditions and sometimes they give you part load numbers as well. Find that information and that should point you in the right direction.

    The 44 and 41.9 numbers on the other post are Fahrenheit equivalents of your readings, most people on this forum do not work in metric.
    Thank you so much for your information.

  9. #9
    Join Date
    Jun 2010
    Location
    U.A. (upper Alabama)
    Posts
    1,253
    Post Likes
    Leaving chilled water sensor and saturated temp or evap pressure transducer reading a little off can throw the approach off. Did you verify they are reading right?


    Sent from my iPhone using Tapatalk

  10. #10
    Join Date
    Jun 2019
    Location
    Viet Nam
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by cperk View Post
    Leaving chilled water sensor and saturated temp or evap pressure transducer reading a little off can throw the approach off. Did you verify they are reading right?


    Sent from my iPhone using Tapatalk
    I will check it with my technical service team.