    Refrigeration cycle efficiency breakdown?

    I am trying to fully understand how different variables affect refrigeration cycle efficiency.

  2. #2
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    1,008
    Post Likes
    Thread Starter
    So i understand basically how using bigger evaporator and condensor coils can help efficiency because they can bring down the compression ratio. But what other variables are there either theoretical or real world?

  3. #3
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    1,008
    Post Likes
    Thread Starter
    Well i have had some time to think about this some more.
    I was thinking about varying the evaporator size and coil temperature.
    So suppose i have a 3 ton 14 seer ac that has a matching evaporator coil with txv running 400 cfm per ton with a suction saturation temperature of 40* and 10* superheat.
    Now suppose i changed that evaporator out for a 5 ton (to take this thought experiment to the extreme) but i use the same 3 ton txv and adjust the air flow and charge to get a 40* suction saturation temperature with 10* superheat.

    What would change?
    Would my eer change and if so how?
    Would my latent sensible ratio change and if so how?
    How would it affect my head pressure and subcooling?

    So now what if i changed the evaporator out for a 2 ton again with 40* suction saturation temp and 10* superheat what affect would that have on the aforementioned parameters?

    Sent from my rotary telephone using Tapatalk

  4. #4
    Join Date
    Nov 2001
    Posts
    171
    Post Likes
    I will take a stab that this.

    First, I am going to assume that when you say that you will keep the 3-ton TXV that means that I will have the same refrigerant mass flow. If I adjust airflow to get the same evap temperature and superheat, the refrigerant will absorb the same amount of heat with the 5-ton evaporator as it did with the 3-ton. Since the split between evap temp and condensing temp are the same and the mass flow of the refrigerant is the same, the refrigeration side of the system will not have any change in efficiency.

    But, since I did have to reduce airflow to maintain the evap temperature and same superheat my fan energy will be reduced, so there will be system energy savings. Note that since I am taking the same amount of heat from the reduced airflow my discharge temperature will go down, so lower cfm/ton.

  5. #5
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    1,008
    Post Likes
    Thread Starter
    That is what i would expect also.
    How do you think it would affect latent capacity?
    I think it would increase latent capacity vs a smaller evaporator.
    Quote Originally Posted by coolcoil View Post
    I will take a stab that this.

    First, I am going to assume that when you say that you will keep the 3-ton TXV that means that I will have the same refrigerant mass flow. If I adjust airflow to get the same evap temperature and superheat, the refrigerant will absorb the same amount of heat with the 5-ton evaporator as it did with the 3-ton. Since the split between evap temp and condensing temp are the same and the mass flow of the refrigerant is the same, the refrigeration side of the system will not have any change in efficiency.

    But, since I did have to reduce airflow to maintain the evap temperature and same superheat my fan energy will be reduced, so there will be system energy savings. Note that since I am taking the same amount of heat from the reduced airflow my discharge temperature will go down, so lower cfm/ton.
    Sent from my rotary telephone using Tapatalk

  6. #6
    Join Date
    Nov 2001
    Posts
    171
    Post Likes
    Agreed. Lower discharge temp causes lower SHR. That’s assuming, of course, that your initial conditions had an SHR <1.0. If that was not the case, then you would have to know the entering air conditions and flows to determine if latent capacity changed.

  7. #7
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    1,008
    Post Likes
    Thread Starter
    Now what if we take that same base 3 ton system and recover some of that cooling that is lost down the drain by using the cold condensate to cool the liquid line below ambient?
    How what affect would that have?


    Sent from my rotary telephone using Tapatalk

  8. #8
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    1,008
    Post Likes
    Thread Starter
    Would the cooler refrigerant have more cooling power thus causing the txv to close more increasing head pressure and load on the compressor?
    Would increasing airflow fix that problem resulting in no increase in load while increasing the btu output?


    Sent from my rotary telephone using Tapatalk

  9. #9
    Join Date
    Nov 2001
    Posts
    171
    Post Likes
    That would have some positive effect on both capacity and efficiency. Assuming you were getting some flashing at the TXV you would now get less flashing so more liquid to evaporate in the condenser. The improvement would depend entirely on how well subcooled the liquid already is at the condenser.

    I am going to guess that it is not all that much as manufacturers are continually investigating methods to improve subcooling, and I am sure that somebody in the industry has tried this and found it not worthwhile sometime in the last 70 years*. When I worked for a manufacturer we often looked at ways to use condensate, and the only viable use that I've ever heard of is collecting the water for other uses - feeding back to the cooling tower or watering the lawn - and that is only done for very large systems where there is enough water generated to cover the cost of piping somewhere.

    *For what it's worth, I am always coming up with ingenious new HVAC ideas only to discover, (1) it is actually a dumb idea, or (2) the idea was patented 40 years ago.

  10. #10
    Join Date
    Nov 2001
    Posts
    171
    Post Likes
    Quote Originally Posted by R600a View Post
    Would the cooler refrigerant have more cooling power thus causing the txv to close more increasing head pressure and load on the compressor?
    Would increasing airflow fix that problem resulting in no increase in load while increasing the btu output?
    I would have to think about it, but off the top of my head I don't think the TXV would see a difference. The same net total amount of heat is being transferred into the refrigerant. The only difference is that with better subcooling it happens in the airstream rather than before getting into the coil.

  11. #11
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    1,008
    Post Likes
    Thread Starter
    Also maby you could set the charge for lower subcooling at the condensor and run lower head pressure.

    Sent from my rotary telephone using Tapatalk

  12. #12
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    1,008
    Post Likes
    Thread Starter
    I was supposing that both systems had sufficient subcooling. Lets just go with 10* before the condensate heat exchanger.
    Quote Originally Posted by coolcoil View Post
    I would have to think about it, but off the top of my head I don't think the TXV would see a difference. The same net total amount of heat is being transferred into the refrigerant. The only difference is that with better subcooling it happens in the airstream rather than before getting into the coil.
    Sent from my rotary telephone using Tapatalk

  13. #13
    Join Date
    Jul 2019
    Location
    Oklahoma home its in the name
    Posts
    1,008
    Post Likes
    Thread Starter
    Well this is not a new idea. My boss did it before i was born but he did not try to quantify the results.
    Also i found a patent for this very thing on ptacs and window units along with using it to cool the discharge line before the condensor.
    Quote Originally Posted by coolcoil View Post
    That would have some positive effect on both capacity and efficiency. Assuming you were getting some flashing at the TXV you would now get less flashing so more liquid to evaporate in the condenser. The improvement would depend entirely on how well subcooled the liquid already is at the condenser.

    I am going to guess that it is not all that much as manufacturers are continually investigating methods to improve subcooling, and I am sure that somebody in the industry has tried this and found it not worthwhile sometime in the last 70 years*. When I worked for a manufacturer we often looked at ways to use condensate, and the only viable use that I've ever heard of is collecting the water for other uses - feeding back to the cooling tower or watering the lawn - and that is only done for very large systems where there is enough water generated to cover the cost of piping somewhere.

    *For what it's worth, I am always coming up with ingenious new HVAC ideas only to discover, (1) it is actually a dumb idea, or (2) the idea was patented 40 years ago.
    Sent from my rotary telephone using Tapatalk