    Hi
    I am working on a carrier roof top unit. When I got here I found the filters plugged and the belt broke on the blower assembly. I switched out the belt and filters. I still had low suction pressure. What I noticed is the blower fan was not turning. It had a delay on it. During this delay the unit freeze up.
    MN# 48TFEOO7
    Southold, NY
    How long of a delay?
    Nov 2018
    I think it was about 3 minutes
    Southold, NY
    That’s a long delay!
    Nov 2018
    Ya I took some picks of the wiring diagram. Once I get to a pc I will post them here.
    Oct 2006
    The Beach
    You should be able to bypass the delay or get one with a lot less delay time.
    Blue Fox
    Nov 2011
    East Side
    sounds like you have something else going on. a 3 minute delay would more likely be on a low pressure switch bypass before it would be on a blower delay.
    someone may have changed the timer and put in the wrong one.
    Operating Sequence COOLING, UNITS WITHOUT ECONOMIZER — When thermostat calls for cooling,terminals G andY1areenergized. The indoor-fan contactor (IFC) and compressor contactor are energized and indoor-fan motor, compressor, and outdoor fan starts. The outdoor fan motor runs continuously while unit is cooling.
    Jan 2010
    Quote Originally Posted by 71CHOPS View Post
    There's a delay but probably the wrong one. Should be a delay on break vs make.
    Nov 2018
    Hi Guys.
    I was able to post the wiring diagram to the unit here. It definitely seems like something is not operation properly after reading your posts. I am trying to figure out the wiring diagram here.
    So as described above the unit should not have a time delay on make but a 30 second time delay on break. In the wiring diagram it shows power going to the ICG board from G on the connection board. My question is does the fan Logic determine when the fan runs? I notice on the J2 line on the ICG board there is a IFO black wire going to the IFC coil. If this is the case what are the BM contacts used for on the IGC board?
    thanks
    May 2018
    VA/DC
    carrier doesn't have a fan delay on in cooling, just heating
    Nov 2018
    Quote Originally Posted by Cool breeze 38 View Post
    According to the manual there is a 30 second delay on break for cooling.
    Virginia
    Quote Originally Posted by Noname81 View Post
    The single phase Indoor Fan Motors (IFM) in this model line, use the “BM” terminal to energize L1 on the motor, and do not use an Indoor Fan Contactor (IFC).