    System not cooling, odd line temps

    Hey guys, I'm stumped on this one. The condenser is clean, both fan motors are blowing strong. Air filters are removed. System starts up and sub cooling, super heat and both high side and low side look good, suction line temp drops, 40 degree difference to discharge.

    After about 2 min, VSAT increases, both pressures increase, and SLT starts to rise. Eventually SLT is like 94 degrees. Very little temperature difference inside between supply and return. No ice on evaporator coil, entering and exiting air temp has minimal difference.

    Any ideas? Older R22 system 2 ton carrier. I've attached pictures of the gauge set

  2. #2
    Join Date
    Jun 2017
    Location
    North Texas
    Posts
    13
    Post Likes
    Thread Starter
    Sorry, can't find how to post pics, here's the specs after 2 min run time

    Suction pressure. 86.3
    Suction line temp. 94
    Discharge pressure. 287.3
    Discharge line temp. 104
    Sub cooling. 23
    Super heat 43
    Vsat. 51
    Lsat. 128

  3. #3
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    6,083
    Post Likes
    Somethin goin on with txv , or drier

  4. #4
    Join Date
    Jan 2012
    Location
    USA
    Posts
    1,296
    Post Likes
    Get your post count up and apply for pro membership.

  5. #5
    Join Date
    Aug 2018
    Location
    Piedmont Triad, NC
    Posts
    430
    Post Likes
    W.A.G. Incoming: an overcharged restriction with a heating element stuck on.

  6. Likes heatingman liked this post
  7. #6
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    8,976
    Post Likes
    Where are you taking your SP at. Is there anything between the post and compressor.

    This reminds me of a system I ran onto with a bad suction drier, 100 lb inlet, 45 lb outlet.

  8. #7
    Join Date
    Jan 2010
    Posts
    16,600
    Post Likes
    What was your ambient ?

  9. #8
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    7,862
    Post Likes
    How hot is the space?


    Sent from my iPhone using Tapatalk

  10. #9
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    23,030
    Post Likes
    *
    Quote Originally Posted by Achso017 View Post
    W.A.G. Incoming: an overcharged restriction with a heating element stuck on.
    Quote Originally Posted by BNME8EZ View Post
    Where are you taking your SP at. Is there anything between the post and compressor.

    This reminds me of a system I ran onto with a bad suction drier, 100 lb inlet, 45 lb outlet.
    Quote Originally Posted by VTP99 View Post
    What was your ambient ?
    Attached Images Attached Images  

  11. #10
    Join Date
    Jun 2017
    Location
    North Texas
    Posts
    13
    Post Likes
    Thread Starter
    Hey guys, i really appreciate the help in this one. I dug into the coil box and 3 rows of coil runs on the evap were not cooling hardly at all, like 88 degree temperature with the other "runs" at 38 degrees or so. Found a small leak on the distributor line on one of the runs. Going to replace the Coil and cut out the suction line drier and replace, it had a temp drop on it as well.

    Thank you all again!

  12. #11
    Join Date
    Mar 2012
    Location
    Birmingham Al
    Posts
    403
    Post Likes
    suction line drier and replace

    yeah, replace that with a straight pipe section.