    bohn refregration

    I have walk in cooler 3 ton with 2 Bohn evaporator. The suction pressure will not go more than 45psi and supper heat at the evaporator with txv all the way open does not come bellow 26.i could not find any leak even though I put stop leak in it still I have to charge it every 4 to 6 weeks. Bubbles stays in sight glass it clear out for few minutes and come back. The system is about 3 years old. I notice the installer did not put in the orifice for 404a because is in the bag and attached to the evaporator. Is that the reason for the problem. Where all the Freon went? Did it accumulate in the receiver or the problem is some where else?

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    23,936
    Post Likes
    1st issue is the stop leak

    Now your screwed.

    Adding refrigerant every 4 - 6 weeks is a substantial leak.

    What leak detector (s) are you using?

  3. #3
    Join Date
    Aug 2019
    Posts
    11
    Post Likes
    Thread Starter
    big blu micro leak detector solution and TIF XL-1A
    Quote Originally Posted by shavaz View Post
    I have walk in cooler 3 ton with 2 Bohn evaporator. The suction pressure will not go more than 45psi and supper heat at the evaporator with txv all the way open does not come bellow 26.i could not find any leak even though I put stop leak in it still I have to charge it every 4 to 6 weeks. Bubbles stays in sight glass it clear out for few minutes and come back. The system is about 3 years old. I notice the installer did not put in the orifice for 404a because is in the bag and attached to the evaporator. Is that the reason for the problem. Where all the Freon went? Did it accumulate in the receiver or the problem is some where else?

  4. #4
    Join Date
    Aug 2019
    Posts
    11
    Post Likes
    Thread Starter
    big blu micro leak detector solution and TIF XL-1A

  5. #5
    Join Date
    Aug 2019
    Posts
    11
    Post Likes
    Thread Starter
    What can I do about stop leak?

  6. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    23,936
    Post Likes
    Quote Originally Posted by shavaz View Post
    What can I do about stop leak?
    Never use that crap again, Nothing Now its in there.

    Have you dropped the evaporator drain pan and look for stains, Shinny U-Bends, Electronic CAREFULLY near the drain, Just walking into the box with a leak in the coil sets my machine off.

    Have you tested the leak detector?

  7. #7
    Join Date
    Apr 2005
    Location
    Australia : Queensland
    Posts
    1,838
    Post Likes
    Adding gas every 4-6weeks is a crime

    Does your electronic leak detector actually work , have you verified it ?
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  8. #8
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    23,936
    Post Likes
    Quote Originally Posted by fridg View Post
    Adding gas every 4-6weeks is a crime

    Does your electronic leak detector actually work , have you verified it ?
    Adding stop leak is more of a crime!

  9. #9
    Join Date
    Apr 2005
    Location
    Australia : Queensland
    Posts
    1,838
    Post Likes
    Quote Originally Posted by pecmsg View Post
    Adding stop leak is more of a crime!
    I agree ,,, there may not even be a leak , it could be that the stop leak is now slowly blocking the circuit.
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  10. #10
    Join Date
    Jun 2012
    Location
    Northern NV
    Posts
    1,803
    Post Likes
    Two solenoids or one for both?

    Lots of copper between the condenser and evaps or close coupled? Exposed lines or buried in a wall

    And what is the subcooling after you "top it off?"

  11. #11
    Join Date
    Jan 2010
    Posts
    17,171
    Post Likes
    What size are the evaporators ?

  12. #12
    Join Date
    Aug 2019
    Posts
    11
    Post Likes
    Thread Starter
    Two solenoid and is 12000 btu each
    Quote Originally Posted by Juan Madera View Post
    Two solenoids or one for both?

    Lots of copper between the condenser and evaps or close coupled? Exposed lines or buried in a wall

    And what is the subcooling after you "top it off?"

  13. #13
    Join Date
    Jan 2010
    Posts
    17,171
    Post Likes
    So a 3 ton compressor on 2 - 1 ton evaporators ?