    Trane rtaa 70 low pressure fault.

    I have a chiller that trips once a day or so. The charge looks fine. I am going to replace switch. Any other ideas besides exv hanging up. Thanks

  2. #2
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    The low pressure switch is opening .
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  3. #3
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Sensors beginning to fail, flow switch is hung up
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  4. #4
    Join Date
    Mar 2005
    Location
    Indiana
    Posts
    459
    Post Likes
    I have had those Texas instrument low pressure peanut switches trip way to soon, you need to see if that's happening. They normally have valve cores under them.

  5. #5
    Join Date
    Jan 2001
    Location
    Carlisle, Pa
    Posts
    945
    Post Likes
    Thread Starter
    It is to open at 7# (r22). I checked charge on both circuits. It's fine. I had to replace lvg water sensor in July. I checked flow back then it was fine. This thing may trip once a day. It went all weekend without tripping. I am replacing low pressure switch tommorrow. If it continues the only thing I could figure is exv isnt opening all the time. I guess it could be suction sensor too.

  6. #6
    Join Date
    Sep 2008
    Location
    Sunrise,fl
    Posts
    188
    Post Likes
    Checked ampage on startup.Make sure compressor is not starting loaded.That could also cause issue.

  7. #7
    Join Date
    Jun 2010
    Location
    U.A. (upper Alabama)
    Posts
    1,253
    Post Likes
    Check the male unload solenoid coil. May be loading but not unloading when it needs to. Seen a few bad unload coils that will cause problems with low evap temp and low pressure cutout.


    Sent from my iPhone using Tapatalk

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •