Results 1 to 8 of 8
    Oct 2007
    Confused Heatpump problem...
    ok gents...here my symptoms, seeing if anyone has a bit of useful advice as its taking me a minute.
    I did NOT install it, was just called out to take a look. Was called for a loss of cooling. When i got there, it was locked out on low pressure lockout. Reset control and got the system to kick on. When I first got to the site, there was 0 degrees super heat, recovered about 1 pound to get the superheat of 8-9 degrees, also cleaned the condensor while i was there. System ran for two days, did the same thing again,lost cooling and homeowner said they saw frost on the lines coming out of the house. Froze up. Told them to turn off the unit and turn on fan only and i would come back out. Get out there and reset the control and get the system to run again. Below are the numbers i got. Ran all day, kept house at 71. I just got a call that the system froze up again. Told them to turn the system off and fan on, Id get back out later.......
    Lennox Heatpump 3 ton........Fixed piston (dont know the size of piston)
    Discharge pressure 220...........Saturation 109...........Line Temp 89----subcooling 20
    Suction 100...........Saturation 60...............Linetemp 68.7..........Superheat 8-9 degrees
    RLA--nameplace 16.9.............acutal 9.3
    OAT 77 discharge air from condensor 87...........10 degree temp rise through condensor
    75 degree return to Furnace...........58.5 supply air
    Thanks to anyone and everyone for replies and insight.
    Air flow problem inside. Blower may be shutting off at times.
    Looks like system is still over charged.
    Oct 2007
    Blower was verified.......
    As far as I know, the blower has always stayed running. While I've been there working the blower never shut off, and during all of this, I asked the home owner to pay attention to the blower and notice if it shuts off or if they lose airflow from registers. Only time they lose airflow is when they confirm ice on the lines and at that time I would expect a frozen coil to block airflow. The blower was my third assumption, but has not stopped.
    TXV?
    slow to respond?
    occasionally shutting down?
    Oct 2007
    Quote Originally Posted by dandyme View Post
    TXV?
    slow to respond?
    Fixed piston.........
    Jul 2013
    Richmond, VA
    Static pressure and blower speed? Maybe a collapsed duct or fallen insulation. Fan relay board may be acting up.
    Jan 2012
    Missouri, USA
    Test the blower capacitor.
    Dec 2003
    Citrus County, Florida
    Hang a ribbon from a supply. Then the client can tell if the blower cuts out.
    Doug