    You told us previously that you had some electrical background.

    There is more than electrical that you'll need to think of.

    Your main concern as the system as not been designed for variable speed will be oil return.
    Some compressor wouldn't last long with a vfd.
    Replacement cost of the compressor will offset
    energy saving by a lot.

    Unit are small tonnage I see no gain in doing that.

    Personnaly I wouldn't recommend it.

  3. #23
    Join Date
    Aug 2019
    Posts
    38
    Post Likes
    Thread Starter
    Quote Originally Posted by patpinet View Post
    You told us previously that you had some electrical background.

    There is more than electrical that you'll need to think of.

    Your main concern as the system as not been designed for variable speed will be oil return.
    Some compressor wouldn't last long with a vfd.
    Replacement cost of the compressor will offset
    energy saving by a lot.

    Unit are small tonnage I see no gain in doing that.

    Personnaly I wouldn't recommend it.
    Thank you for reply.

    Running full speed every say 30 minutes will help solve oil problems. Learned this online. I cant prove it.

    This main purpose of this approach is to test and learn. Like it or not, VFD will play big part in AC world. If I can learn something ahead of time, will benefit from it later on.

  4. #24
    Join Date
    Feb 2010
    Location
    montreal
    Posts
    349
    Post Likes
    That is a great idea.
    Maybe you can ask Emerson for guidance or check there bulletin.
    If it's a scrool be advised that the one for vfd have been modified to help the lubrification for both bearing.
    You might find a kit from Emerson if you want to replace compressor.
    You might want to install a EEV instead of a TXV.

  5. #25
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    1,103
    Post Likes
    I git my info from a bulletin from Emerson I will post the number later. Also be aware they do make a retrofit digital scroll kit. Something to look at if you have a dead compressor.

    Sent from my SM-G960U using Tapatalk

  6. #26
    Join Date
    May 2009
    Location
    SC
    Posts
    2,361
    Post Likes
    Is it me or does it sound like doing all these modifications to the system it might be better to do nothing, wait for the next replacement and get a unit that is capable of all this with warranty? Maybe save the money on mods and do the replacement a bit early?

    DigiRTU is fairly non invasive, they put the whole unit on VFD from what I understand, no modifications to the refrigerant system. As an owner that might be the furthest I'd be willing to go.

  7. #27
    Join Date
    Mar 2005
    Posts
    1,489
    Post Likes
    agree
    Keep it simple to keep it cool!

  8. #28
    Join Date
    Sep 2007
    Location
    Kenilworth NJ
    Posts
    2,253
    Post Likes
    Quote Originally Posted by Spitz View Post
    .

    Sent from my SM-G960U using Tapatalk
    Handy! You got a link for that by chance?
    Hmmmm....smells like numbatwo to me.

  9. #29
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    1,103
    Post Likes
    ae21-1369 r4

    Search that number

    Sent from my SM-G960U using Tapatalk

  10. #30
    Join Date
    Mar 2005
    Location
    Mountain/Pacific Time Zone Typicallly
    Posts
    4,592
    Post Likes
    Ok if this a a pet project to learn from that is one thing, but you are taking a lot of risk and there is a lot of unknowns to your system. Economizer, VAV's, area climate, etc.

    For a pet project I would add a controller to log data.
    Suction Pressure and temperature before compressor to get superheat at compressor
    High side pressure and liquid line temperature to get subcool
    If economizer mixed air temperature to verify inlet temperature isn't too low at evap.
    Supply/Discharge air temp
    Return air temp

    Logic to protect compressor (superheat calcs), ramp up/down as needed
    An EEV would be ideal, could add one with a built in controller and just pull data from that.

    It'd be a cool project, but not sure you'll save $ doing this big picture wise, very unlikely on just one unit. As you get this down and can cut install time maybe...now to add to it your not a refrigeration guy, keeping a compressor 'safe' and running long term is not a simple task on such a system.

    Also not sure what's controlling head pressure, but quick story...worked on units in which programmers were trying to save operating costs and keep head pressure as low as possible, well system wouldn't work correctly in cold weather. Head pressure ended up running so low that the minimum pressure drop across the metering device was not being maintained and therefore system wasn't operating correctly and excessive compressor replacements. Pressures setup to ensure 100 psi differential on metering device and system started working properly. Low ambient kits were not needed at this location, but something maybe you need depending on climate.
    "How it can be considered "Open" is beyond me. Calling it "voyeur-ed" would be more accurate." pka LeroyMac, SkyIsBlue, fka Freddy-B, Mongo, IndyBlue
    BIG Government = More Dependents
    "Any 'standard' would be great if it didn't get bastardised by corporate self interest." MatrixTransform
    My 5 yr old son "Dad, Siri is not very smart when there's no internet."


  11. #31
    Join Date
    Mar 2005
    Posts
    1,489
    Post Likes
    Quote Originally Posted by crab master View Post
    Ok if this a a pet project to learn from that is one thing, but you are taking a lot of risk and there is a lot of unknowns to your system. Economizer, VAV's, area climate, etc.

    For a pet project I would add a controller to log data.
    Suction Pressure and temperature before compressor to get superheat at compressor
    High side pressure and liquid line temperature to get subcool
    If economizer mixed air temperature to verify inlet temperature isn't too low at evap.
    Supply/Discharge air temp
    Return air temp

    Logic to protect compressor (superheat calcs), ramp up/down as needed
    An EEV would be ideal, could add one with a built in controller and just pull data from that.

    It'd be a cool project, but not sure you'll save $ doing this big picture wise, very unlikely on just one unit. As you get this down and can cut install time maybe...now to add to it your not a refrigeration guy, keeping a compressor 'safe' and running long term is not a simple task on such a system.

    Also not sure what's controlling head pressure, but quick story...worked on units in which programmers were trying to save operating costs and keep head pressure as low as possible, well system wouldn't work correctly in cold weather. Head pressure ended up running so low that the minimum pressure drop across the metering device was not being maintained and therefore system wasn't operating correctly and excessive compressor replacements. Pressures setup to ensure 100 psi differential on metering device and system started working properly. Low ambient kits were not needed at this location, but something maybe you need depending on climate.
    in a nut shell
    Keep it simple to keep it cool!