    Crazy, needs your support or immediate rejection

    Have a 26yr old 15-tonne electric powered HVAC unit. Recently, A/C portion has failed. No way of repair. Fan still works, heating coils still work.

    Need to provide A/C to a 1.5-2 story work space. No real money, and no means to fix or replace HVAC unit without major cash injection and taking out heritage walls, or current office construction.

    I know, horrible situation.

    Any possibility that I can get a few off-the-shelf ~15k BTU A/C units, blowing their cold air into existing ductwork (fan still works) and vent hot air into HVAC return? Can't vent through any window or wall. Trust me.

    Is this idea stupid/how stupid is this idea?

  2. #2
    Join Date
    Jan 2015
    Location
    Iowa
    Posts
    2,451
    Post Likes
    Send whomever is doing whatever in the workspace someplace else to do their work

  3. #3
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Quote Originally Posted by Answer-Man View Post
    Send whomever is doing whatever in the workspace someplace else to do their work
    Truth be told here....

  4. #4
    Join Date
    Jan 2015
    Location
    Iowa
    Posts
    2,451
    Post Likes
    Quote Originally Posted by VTP99 View Post
    Truth be told here....
    What this is a jail or prison?

  5. #5
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,135
    Post Likes
    Quote Originally Posted by CanStage View Post

    Any possibility that I can get a few off-the-shelf ~15k BTU A/C units, blowing their cold air into existing ductwork (fan still works) and vent hot air into HVAC return? Can't vent through any window or wall. Trust me.

    Is this idea stupid/how stupid is this idea?
    Yes, that idea is stupid. Very stupid. It's not a perpetual motion machine that we're talking about here. The heat from the condenser needs to be rejected to someplace other than the place you are trying to cool.

    What you are describing would be like plopping a window air conditioner on the table in the middle of your room. Yes, you would get cold air blowing out the front of it, but warm air blowing out the back. The problem is that there's more warm air produced than there is cool air, and the room would slowly get warmer and warmer. Soon it would become unbearable, even with the slightly cooled air blowing out of the front.

    All air conditioners need to have the "waste heat" discharged to a place where it will make no difference, which is usually outside.
    If at First You Don't Succeed, Skydiving Is Not for You.

  6. #6
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Quote Originally Posted by Answer-Man View Post
    What this is a jail or prison?
    Only he knows, I'm just in agreement with you.

  7. #7
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,903
    Post Likes
    Quote Originally Posted by CanStage View Post
    Have a 26yr old 15-tonne electric powered HVAC unit. Recently, A/C portion has failed. No way of repair. Fan still works, heating coils still work.

    Need to provide A/C to a 1.5-2 story work space. No real money, and no means to fix or replace HVAC unit without major cash injection and taking out heritage walls, or current office construction.

    I know, horrible situation.

    Any possibility that I can get a few off-the-shelf ~15k BTU A/C units, blowing their cold air into existing ductwork (fan still works) and vent hot air into HVAC return? Can't vent through any window or wall. Trust me.

    Is this idea stupid/how stupid is this idea?
    The idea is completely impractical. Your Rube Goldberg suggestion just won't work.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  8. #8
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    7,033
    Post Likes
    Do you own the building???? If not...are you leasing???

    If you are leasing, who is responsible for building capital equipment costs according to your lease agreement????



    Sent from my SM-G965W using Tapatalk

  9. #9
    Join Date
    Jan 2015
    Location
    Iowa
    Posts
    2,451
    Post Likes
    Quote Originally Posted by VTP99 View Post
    Only he knows, I'm just in agreement with you.
    You'd think if he really wanted help he'd provide some real information that could be used just what could be done, But go figure.

  10. #10
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    Immediate Rejection

    PHM
    --------


    Quote Originally Posted by CanStage View Post
    Have a 26yr old 15-tonne electric powered HVAC unit. Recently, A/C portion has failed. No way of repair. Fan still works, heating coils still work.

    Need to provide A/C to a 1.5-2 story work space. No real money, and no means to fix or replace HVAC unit without major cash injection and taking out heritage walls, or current office construction.

    I know, horrible situation.

    Any possibility that I can get a few off-the-shelf ~15k BTU A/C units, blowing their cold air into existing ductwork (fan still works) and vent hot air into HVAC return? Can't vent through any window or wall. Trust me.

    Is this idea stupid/how stupid is this idea?
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  11. #11
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Sounds like he needs heat rejection

  12. #12
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by CanStage View Post
    Have a 26yr old 15-tonne electric powered HVAC unit. Recently, A/C portion has failed. No way of repair. Fan still works, heating coils still work.

    Need to provide A/C to a 1.5-2 story work space. No real money, and no means to fix or replace HVAC unit without major cash injection and taking out heritage walls, or current office construction.

    I know, horrible situation.

    Any possibility that I can get a few off-the-shelf ~15k BTU A/C units, blowing their cold air into existing ductwork (fan still works) and vent hot air into HVAC return? Can't vent through any window or wall. Trust me.

    Is this idea stupid/how stupid is this idea?
    You've had 26 years to budget replacement life cycle costs...……………………..

    Someone's not doing a very good job!

  13. #13
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    You will need a dozen 15K units. That will run about $6000. For $6000. or less I bet the old unit could be all, or at least somewhat, repaired. What is wrong with it that is impossible to fix?

    Who will be doing this work anyway?

    If it were me; maybe we could pipe in three 5 ton condensing units and add three pistons to the evaporator. <g>

    PHM
    -----------



    Quote Originally Posted by CanStage View Post
    Have a 26yr old 15-tonne electric powered HVAC unit. Recently, A/C portion has failed. No way of repair. Fan still works, heating coils still work.

    Need to provide A/C to a 1.5-2 story work space. No real money, and no means to fix or replace HVAC unit without major cash injection and taking out heritage walls, or current office construction.

    I know, horrible situation.

    Any possibility that I can get a few off-the-shelf ~15k BTU A/C units, blowing their cold air into existing ductwork (fan still works) and vent hot air into HVAC return? Can't vent through any window or wall. Trust me.

    Is this idea stupid/how stupid is this idea?
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  14. #14
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Where there's a will there's a way....

  15. #15
    Join Date
    Dec 2006
    Location
    Vancouver, B.C.
    Posts
    1,731
    Post Likes
    I like it when customers present problems like this because they are always happy and surprised when they see it working again. Who said it can’t be fixed? Have you gotten a second (or third) opinion? What exactly makes it unfixable? Often times things look worse than they actually are. I find it’s not very often things become so broke they can be fixed at all, it’s usually just more reliable to replace than repair. In this case it sounds like replace isn’t really an option at all but retrofit may be a solution. I would scrape together as much as you can find for this repair and have a good conversation with a creative tech about how you can make it work. If you don’t put enough money into it then you may end up with a photo on the wall of shame (and to be honest it sounds like that would be acceptable to you at this point of desperation), but if it works then it’s still a great success. 26 years is getting old but there are some buildings that I maintain that has much older equipment and it’s still going strong. I would suggest you don’t take it out back to shoot it without first talking to a few more technicians from various companies. Not everyone will be able to see the answer to the problem so finding the right tech will be part of your problem. They are out there though.


    Sent from my iPhone using Tapatalk
    Quickly, I must hurry, for there go my people and I am their leader!

  16. #16
    Join Date
    Jul 2019
    Posts
    4
    Post Likes
    Thread Starter
    Thanks.

    Forgive my lack of understanding, I'm not an HVAC tech, just a placeholder property manager at a theatre that works out of a 130-year old building.

    The "waste heat" coming each of the A/C units would be pushed right back into the HVAC units return (a 2'x3' intake) immediately beside the unit. I was thinking that the waste heat would enter the return, cycle through, and would be at least room temperature by the time it is in the ducts going back out to the offices.

  17. #17
    Join Date
    Jul 2019
    Posts
    4
    Post Likes
    Thread Starter
    Thanks

    Have had opinions from 4 technicians over 3 companies, and another from a consultant in an engineering firm. There are 2 confirmed, and maybe more leaks on the refrigerant lines. all the techs stated that any attempt at repair the leaks had a good chance of making them worse. The unit is in an incredibly tight space, that was pretty much walled up around it. The techs and the consultant all recommended replacement.

  18. #18
    Join Date
    Jul 2019
    Posts
    4
    Post Likes
    Thread Starter
    Quote Originally Posted by BALloyd View Post
    Do you own the building???? If not...are you leasing???

    If you are leasing, who is responsible for building capital equipment costs according to your lease agreement????



    Sent from my SM-G965W using Tapatalk
    Thanks

    Leasing.

    We have a below-market lease. We get the property for a very affordable price, but are on the hook for most all repairs and all upkeep. Currently landlord has no interest in remedying this issue, as it is in our contract for the tenant (us) to perform the upkeep of the system.

  19. #19
    Join Date
    Jan 2015
    Location
    Iowa
    Posts
    2,451
    Post Likes
    Thank you for additional information. You stated all vendors recommended replacement but you did not say if they provided a repair opition. They're just bounding their work with known replacement work. Repairs are many time crapshoots as you just don't know all that could be wrong. It's easier to pull out the old and replace with new. I woulld call sevral others and those whom you have already talked to tell them you are interested in repair not replacement. While I do not know what your contact says, you state you are responsible for upkeep, that typically means cleaning, filters, seasonal tune up, some refrigerant, maybe some other misc repairs. But upkeep is different than replacement due to, wear out, obsolence or damage. No one will pay to sit in a hot theater to watch a movie, which means your client is loosing revenue. How long before they fail to make rent payment. Which means the building owner is now loosing revenue. This probably also means you loose income for your part in this operation. There should be discussion with tennet and owner of a potential shared repair/replacement cost. Get some additional (repair) quotes add them to your replacement quotes and call a meeting (you buy the lunch). If a deal is not worked out I doubt you remain in business.

    Good Luck

  20. Likes thatguy liked this post.
  21. #20
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    7,033
    Post Likes
    It is common for the leaseholder to be responsible for maintenance the unit. It is uncommon for the tenant to be responsible for replacing equipment past its service life, but this all depends on your lease agreement.

    At 26 years old and after having paid for several independent opinions, I believe your landlord should be bucking up for a new system.
    Quote Originally Posted by CanStage View Post
    Thanks

    Leasing.

    We have a below-market lease. We get the property for a very affordable price, but are on the hook for most all repairs and all upkeep. Currently landlord has no interest in remedying this issue, as it is in our contract for the tenant (us) to perform the upkeep of the system.
    Sent from my SM-G965W using Tapatalk

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •