    Confused Possible Problem-Leak Saver Direct Inject Refrigerant Leak Sealer

    I am at a loss as to what has happened to 3 ton carrier that had small leak in coil. Customer said they had 410 topped off each year due to small leak, they now wanted leak fixed. Installed Leak Saver Direct Inject Refrigerant Leak Sealer and set sub-cooling to proper reading. Unit did not cool after installing leak sealer. After checking several times next day my gauges now read 100psi on low side and 0 psi on high side. Never come across this befor, could it be that I have somehow increased the leak and if so, why is the low side pressure holding at 100 ?

  2. #2
    Join Date
    Dec 2009
    Location
    maroon lazyboy
    Posts
    2,664
    Post Likes
    Gauges on backward, dryer plugged with easy seal.

  3. #3
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    11,849
    Post Likes
    You caused more problems using that leak sealer junk.
    That should only be used on systems that nobody cares if they die or not.
    I havent failed. Ive just found 10,000 ways that wont work. - Thomas Edison

    Its not whether you get knocked down, its whether you get up. - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486 Instructor & Service Technician

  4. #4
    Join Date
    Dec 2010
    Location
    WV
    Posts
    325
    Post Likes
    Agree with others. Leak sealer has plugged up something. Thats a last resort product for old systems that you have nothing to lose on. I dont use it much either, it causes problems.


    Sent from my iPhone using Tapatalk

  5. #5
    Join Date
    Aug 2006
    Posts
    118
    Post Likes
    I don't use it...... period.

  6. #6
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,434
    Post Likes
    Snake oil, would never use.
    UA Local 32 retired as of Jan 2020

  7. #7
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    26,563
    Post Likes
    Why didn't you locate the leak and repair it?


    Quote Originally Posted by HLWest View Post
    I am at a loss as to what has happened to 3 ton carrier that had small leak in coil. Customer said they had 410 topped off each year due to small leak, they now wanted leak fixed. Installed Leak Saver Direct Inject Refrigerant Leak Sealer and set sub-cooling to proper reading. Unit did not cool after installing leak sealer. After checking several times next day my gauges now read 100psi on low side and 0 psi on high side. Never come across this befor, could it be that I have somehow increased the leak and if so, why is the low side pressure holding at 100 ?
    I do a triple evac with nitro to remove non condensables.

  8. #8
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    10,735
    Post Likes
    Your leak sealer plugged the high side port which may have been where the leak was all along since with 100 low side it sounds low.

  9. #9
    Join Date
    Sep 2018
    Location
    Summerville SC
    Posts
    41
    Post Likes
    Quote Originally Posted by HLWest View Post
    I am at a loss as to what has happened to 3 ton carrier that had small leak in coil. Customer said they had 410 topped off each year due to small leak, they now wanted leak fixed. Installed Leak Saver Direct Inject Refrigerant Leak Sealer and set sub-cooling to proper reading. Unit did not cool after installing leak sealer. After checking several times next day my gauges now read 100psi on low side and 0 psi on high side. Never come across this befor, could it be that I have somehow increased the leak and if so, why is the low side pressure holding at 100 ?
    Is this a split system or package unit?
    High side or liquid line at service valve showing zero?
    The leak stop may have clogged the Schrader valve that is showing zero.
    If it was a clogged expansion device , the high would be more than the low side. Suction would pull down to near zero.

  10. #10
    Join Date
    Dec 2003
    Location
    Citrus County, Florida
    Posts
    3,034
    Post Likes
    Or your hose end is not depressing the shrader. I had a marginal shut off doing that. The depresser would not depress the shrader on all access points. I put another shut off on and problem went away. I realize you stated unit does not cool but this is something to check.
    Doug

  11. #11
    Join Date
    Jul 2019
    Posts
    9
    Post Likes
    Thread Starter
    Quote Originally Posted by Dacman View Post
    Is this a split system or package unit?
    High side or liquid line at service valve showing zero?
    The leak stop may have clogged the Schrader valve that is showing zero.
    If it was a clogged expansion device , the high would be more than the low side. Suction would pull down to near zero.

    This is a typical split system, evaporator coil in furnace and condenser outside, Thanks for your help

  12. #12
    Join Date
    Jul 2019
    Posts
    9
    Post Likes
    Thread Starter
    Did you really need the " If you were a real tech " ??

  13. #13
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,434
    Post Likes
    Most real techs would have informed the customer of the correct ways to locate and repair leaks. If it was you that just decided to put that crap in a refer system , without any explanation of what the results might be, then you own it!