    Intermittent cooling

    My upstairs A/C, a 3.5 ton unit has started to intermittently fail to cool.
    I had a technician come over while the failure occurred and he opined that the suction line at the condenser seemed too warm. He explained that of the line is too warm the compressor will overheat and shutdown, causing the system to stop cooling.
    He suggested adding 1Lb of R22 as low freon the likely cause. The explanation made sense to me. He did that and the system started cooling.

    Unfortunately the problem reoccurred.
    So before I call anyone back here, I'd like to get a better reading of the problem, with your help.

    When the system is working the DeltaT is about 20F and cooling is adequate. I measured the pressures at liquid 255PSI and suction 78PSI. I also took readings and calculated the Subcool (17F) and Superheat (11F) both measured near condenser.
    When failing the pressure at the high side fluctuates between 200-225PSI and the suction side at 120-125PSI. During those times DeltaT is very low, 2-4F. Needless to say, the unit runs forever under these conditions. Reading 13A of current at compressor during failure.
    The explanation offered by the tech didn't confirm, I had the unit running for hours and the compressor never shut down (although it may have overheated?!).

    Your expert advice is very much appreciated.
    thanks

  2. #2
    Join Date
    Jul 2019
    Posts
    7
    Post Likes
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thread Starter
    .

  3. #3
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    28,260
    Post Likes
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    He’s partly correct but there’s a lot more to determining the correct refrigerant charge. Warm line is not one of them.

    I would request a more senior tech or a different contractor!

  4. #4
    Join Date
    Mar 2018
    Location
    Chico, Ca #StateofJefferson
    Posts
    2,012
    Post Likes
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    What kind of metering device does your system have and what was the inside temperature/RH%?

  5. #5
    Join Date
    Jul 2019
    Posts
    7
    Post Likes
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thread Starter
    Quote Originally Posted by Makeitcold View Post
    What kind of metering device does your system have and what was the inside temperature/RH%?
    Piston; The inside temperature at the time of these readings was 78F. I am in Phoenix AZ, the humidity was about 35% at the time.

    Other details, in case you would like to know:The Condenser unit is YORK H2RC042S06A, installed ~2002.

  6. #6
    Join Date
    Jan 2014
    Location
    New England
    Posts
    7,117
    Post Likes
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If recip. compressor have senior Tech. pump it down to see what they get. That experienced tech should get some info by doing that.

    You didn’t mention what the OD temperature was when you had those pressures.

  7. #7
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    20,249
    Post Likes
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by adrian62 View Post
    Piston; The inside temperature at the time of these readings was 78F. I am in Phoenix AZ, the humidity was about 35% at the time.

    Other details, in case you would like to know:The Condenser unit is YORK H2RC042S06A, installed ~2002.
    Did they check anything other than the refrigerant, maybe like the capacitor?
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "When the teachers become unteachable we're all in trouble"

    "It's what you learn after you know it all that counts." ~ John Wooden



  8. #8
    Join Date
    Jul 2019
    Posts
    7
    Post Likes
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thread Starter
    Quote Originally Posted by Bazooka Joey View Post
    If recip. compressor have senior Tech. pump it down to see what they get. That experienced tech should get some info by doing that.

    You didn’t mention what the OD temperature was when you had those pressures.
    90F

  9. #9
    Join Date
    Jul 2019
    Posts
    7
    Post Likes
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thread Starter
    Quote Originally Posted by Mr Bill View Post
    Did they check anything other than the refrigerant, maybe like the capacitor?
    Cap is good.