Thread: 404A or 134A?

  1. #41
    Join Date
    Jun 2018
    Location
    Bay saint louis ms
    Posts
    137
    Post Likes
    I went on a w/I and it had. R12 exp valves and someone changed it over to r 408 I always heard and read that r 409 was the freon of choice when dealing with r12 it’s been running like that for 4 years now I believe some of these old semis with the suction line. on the end going through the windings will pump any thing you put in it.its only about 30 years old and went under water in Katrina tiff stuff back in the day

  2. #42
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    R408a was a replacement for R502 and yes R409a was for R12 as well as R401a (MP39) , R414b (HotShot) and others.

  3. #43
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by VTP99 View Post
    R408a was a replacement for R502 and yes R409a was for R12 as well as R401a (MP39) , R414b (HotShot) and others.
    and the a c guys have issues with
    410A
    NU-23
    407A, B , C

  4. #44
    Join Date
    Jul 2019
    Location
    Central Massachusetts
    Posts
    27
    Post Likes
    Sometimes you just never know what the heck is in a system!! The last unmarked one was actually marked, R409a, HotShot, R12, R406a, R416a and a couple others all with magic marker on the wooden support, may as well be unmarked. No dates on any of them either. I removed the 2 HP compressor, dumped out the oil which was pancake syrup color and consistency! The sight glass was black on the 'dot' and all brown inside. I put 20 oz of POE in it, swirled it around a lot, dumped it and filled it with the nameplate called for 48 oz. I added DyeChek and Seal, put the compressor back, replaced the filter dryer and sight, and charged it with R134a. I ALWAYS add a label such as the one below. (I made the label, feel free to use it yourself for free!) I attach it with clear packing tape covering the whole label. I also use spray paint to permanently cover all the other ...uh..."Mishaps"!Name:  POE134 Notice.png
Views: 370
Size:  13.7 KB

  5. Likes zymometer liked this post.
  6. #45
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    I just thought of a reason for them to do this.

    Could it be that the control-intent is to do a lot of the sensible load with the plate and only the remainder as both sensible & latent load with the finned coil? With the idea of lower frosting / longer air for for longer periods / less time devoted to defrosting. To do that really well the plate would have to controlled a degree or two above the dew point - is there anything sensing RH% ?

    PHM
    ---------


    Quote Originally Posted by navyguy1 View Post
    This chamber actually has two evaporators. One is a standard coil and the other is cold plate. I can say now with certainty that its all 404A. But honestly, Im still a bit confused on the piping configuration. I see 3 solenoids that are tying both systems together. The manufacturer, Leica, refuses to provide any information like a schematic, wiring diagram, theory of operation etc. Very frustrating to say the least. I did find a compressor on Ebay for only about $100 so I think its worth replacing the bad compressor and see what happens.

    Thanks for your input.
    Semper Gumby
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  7. #46
    Join Date
    Jul 2019
    Location
    Central Massachusetts
    Posts
    27
    Post Likes
    Hey Poodle, you could be right there. Sometimes the humidity is as or more important as the temperature! Good example; one of my customers had a walk-in humidor. The equipment had been mickeyed 20 ways from Christmas, once I 'started over' it wasn't all that hard to get the humidity and temperatures right. There are 2 compressors in that setup. One drives a fincoil, the other a plate. You might be on to something!

  8. #47
    Join Date
    Jul 2019
    Location
    Central Massachusetts
    Posts
    27
    Post Likes
    Hey NAVYGUY, did you ever post the model number of the equipment, I have access to a lot of the lecia tech sheets.

  9. Likes zymometer liked this post.
  10. #48
    Join Date
    Apr 2019
    Location
    Dubai, UAE
    Posts
    21
    Post Likes
    Some compressors are designed to use different refrigerants so they can use different types instead of using one.

  11. #49
    Join Date
    Jul 2012
    Posts
    2,366
    Post Likes
    404A is superior at low temps vs 134A

  12. #50
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    R404a is the refrigerant of choice. Unfortunately it's slated to go on the EPA chopping block.

  13. #51
    Join Date
    Jul 2012
    Posts
    2,366
    Post Likes
    Quote Originally Posted by VTP99 View Post
    R404a is the refrigerant of choice. Unfortunately it's slated to go on the EPA chopping block.
    That's a shame because it works well for everything.

  14. Likes zymometer liked this post.
  15. #52
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by VTP99 View Post
    R404a is the refrigerant of choice. Unfortunately it's slated to go on the EPA chopping block.
    That's on HOLD!

  16. #53
    Join Date
    Jul 2012
    Posts
    2,366
    Post Likes
    Quote Originally Posted by pecmsg View Post
    That's on HOLD!
    Good to know

  17. #54
    Join Date
    Sep 2020
    Location
    central Arizona
    Posts
    12
    Post Likes
    Quote Originally Posted by MilfordsMrFixIt View Post
    Hey NAVYGUY, did you ever post the model number of the equipment, I have access to a lot of the lecia tech sheets.
    Have you worked on Leica CM1950 cryostats, with two separate refrigeration systems? On this model, the second refrigeration system is for the object holder. Leica uses flexible tubing to the object holder (since it moves up and down, in use). I've got a client with four of these machines. The older two are leaking refrigerant (404a) in the object holder system. I'm pretty sure that it is the flexible liquid line, which is leaking, but Leica doesn't list part numbers for it in the service manual. Have you run into this?

  18. #55
    Join Date
    Sep 2020
    Location
    central Arizona
    Posts
    12
    Post Likes
    Quote Originally Posted by navyguy1 View Post
    Working on a small laboratory chamber that has 2 compressors, two condensers and no information whatsoever on it. One of the compressors is locked up tighter than a tractors nuts. The data plate on the equipment says it uses 404A. there is a sticker on the compressor that says 404A. But the actual data plate on the compressor says 134A. WTH? I went online and the exact replacement compressor says it uses 134A. So, can a 134A compressor use 404A?
    This drives me crazy.
    Remember when life was so easy when it was either R12 for refrigeration and freezing, R22 for AC and R502 for low temp?
    I just wanted to say that this is extremely common on cryostats, which is (I presume) what you were working on. The OEM label on the compressor or condensing unit will say one refrigerant (e.g. 134a), but the equipment manufacturer (Leica, or Thermo, etc.) will specify and install a different refrigerant (and slap a label on it). Go with whatever the cryostat manufacturer specifies, not the compressor manufacturer (unless you have reason to believe that someone else has modified it in the field to a different refrigerant).

  19. #56
    Join Date
    Sep 2020
    Location
    central Arizona
    Posts
    12
    Post Likes
    Quote Originally Posted by Poodle Head Mikey View Post
    I just thought of a reason for them to do this.

    Could it be that the control-intent is to do a lot of the sensible load with the plate and only the remainder as both sensible & latent load with the finned coil? With the idea of lower frosting / longer air for for longer periods / less time devoted to defrosting. To do that really well the plate would have to controlled a degree or two above the dew point - is there anything sensing RH% ?

    PHM
    ---------
    Hi Poodle Head Mikey,
    No, they are controlling the temperature of the cryostat chamber with the main (finned) evaporator. The other is a quick freeze plate, intended to quickly drop the temperature of small aluminum chucks (which are placed on top of the quick freeze plate during that time). The quick freeze plate will usually try to cool below the chamber temperature by another 20 degrees C or more. And usually the software will not allow the quick freeze circuit to start cooling, unless the chamber is already down to at least -5 or -10 degrees C.
    Also, there is never an RH sensor in these instruments. Usually the main finned evaporator will be substantially colder than the quick freeze plate (except maybe for short periods of time). There is usually a daily or weekly defrost cycle - usually hot gas, but sometimes using an electrical resistance heater - but only for the finned evaporator and drip plate. After the defrost cycle ends, the main finned evaporator will capture the moisture left in the chamber.

  20. #57
    Join Date
    Sep 2020
    Location
    central Arizona
    Posts
    12
    Post Likes
    Quote Originally Posted by MilfordsMrFixIt View Post
    Hey NAVYGUY, did you ever post the model number of the equipment, I have access to a lot of the lecia tech sheets.
    Hi MilfordsMrFixIt,
    Do you have information on Leica CM1950 cryostats? It also has two separate refrigeration systems, but on this model, the second refrigeration system is for the object holder (not the quick freeze plate). Leica uses flexible tubing/hoses to the object holder. I've got a client with four of these machines. The older two are leaking refrigerant (404a) in the object holder system. I'm pretty sure that it is the flexible liquid line, which is leaking, but Leica doesn't list part numbers for it in the service manual. Do you have anything that shows the part numbers for these hoses or assemblies?
    Those hoses/tubing have to be flexible at cold temperatures - this client runs the chamber at -25C, and the the object holder (the refrigerant through the hoses) can go as low as -52C; and the object holder moves up and down, during use, a couple of inches.

  21. #58
    Join Date
    Nov 2020
    Posts
    3
    Post Likes
    404a without a doubt has superior performance characteristics and capacity compared to 134a. Love low the lower pressures of R134a but the temperature performance difference is no contest.

+ Reply to Thread
Page 3 of 3 FirstFirst 123

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •