Thread: Sub-Panel

  1. #1
    Join Date
    Jul 2019
    Posts
    7
    Post Likes

    Sub-Panel

    Have an old pole barn (20+ years old) that has a sub-panel. The barn is over 250' from the house. The sub is fed by 3 wires and bonded in the panel. No other wires. I was told by my local utility and Electrical contractor that this was legal as long as there are no other wired connections.

    I would like to run a water line out to this barn, probably would use PVC or PEX. Does anyone see any issues?

    Thanks

  2. #2
    Join Date
    Feb 2011
    Location
    Chicagoland
    Posts
    128
    Post Likes
    Three wires to the panel, hot-hot-neutral?
    Is there a grounding conductor too?



    Quote Originally Posted by G_Stan2000 View Post
    Have an old pole barn (20+ years old) that has a sub-panel. The barn is over 250' from the house. The sub is fed by 3 wires and bonded in the panel. No other wires. I was told by my local utility and Electrical contractor that this was legal as long as there are no other wired connections.

    I would like to run a water line out to this barn, probably would use PVC or PEX. Does anyone see any issues?

    Thanks

  3. #3
    Join Date
    Mar 2015
    Location
    Hamersville, Ohio
    Posts
    7,304
    Post Likes
    G_stan,

    What do they mean by "no other wired connections"?

    And as strogen asked, is this a system with 2 hots & a neutral, or is it a Hot/ Neutral & Ground making it a 120V service?

    Is there a Ground Rod tied in to that Sub panel?

    As far as running water out to the barn, there wouldn't be any problem, unless You added an electric DHW, ... Then since it sounds like the AHJ has "Grandfathered" your Barn Service, many things would have to be brought up current Code.
    Hos 4:6 My people are destroyed for lack of knowledge. Because you have rejected knowledge, I will also reject you, that you may be no priest to me. Because you have forgotten your God’s law, I will also forget your children.


    "You've got to Stand for Something or You'll fall for anything" (A. Tippin)


    Mat_15:24 But he answered, “I wasn’t sent to anyone but the lost sheep of the house of Israel.”

  4. Likes YOUNG FROSTY liked this post.
+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •