Thread: Goodman 4 ton 14seer not cold....on hot day

  1. #1
    Join Date
    Jul 2019
    Posts
    5
    Post Likes

    Goodman 4 ton 14seer not cold....on hot day

    I have had my new HVAC system up and running for only a few weeks without any issues until today.

    The unit is struggling to maintain temperature. We normally set at 71*, but will not get any lower than 74* and the compressor is running 100% duty cycle.

    Here is what I have measured:

    Thermostat set: 71
    Indoor temp: 74
    Return temp: 73
    Supply temp: 58
    Indoor RH: 39%
    Outdoor RH: 52%
    Outside temp (side condenser): 92
    Condenser discharge temp: 103

    The air handler is running a 2 stage blower. 25% constant fan, 50% within 1* temp swing and 100% over 3 degrees. I have seen hot humid days and the unit would cycle on and off at 50% blower for 20 minutes.

    Now today, it is running nonstop, and cannot keep up. Im ok if this is just undersized, but my feeling is thst something is not operating correctly....like it needs more freon. Before I call my installer back, I'd like to know if there is more information to diagnose.

    The unit is installed in a very tight attic space, and I was limited to 22" high, making this 4 ton the largest install.

    Im sure im missing some very pertinent information, please let me know.

    Thank you

    Paul

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    How hot is it outside?

  3. #3
    Join Date
    Jul 2019
    Posts
    5
    Post Likes
    Thread Starter
    Measured at the side of the condenser is 92 degrees

  4. #4
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    2,810
    Post Likes
    A 15 degree temperature drop inside and a 11 degree rise outside shows it's not working right. Guessing your installers did a crappy job leak checking their joints.

  5. #5
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by Paulk7269 View Post
    Measured at the side of the condenser is 92 degrees
    So 72 is fine!

  6. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by Paulk7269 View Post
    Measured at the side of the condenser is 92 degrees
    So 72 is fine!
    Stop compla

  7. #7
    Join Date
    Jul 2019
    Posts
    5
    Post Likes
    Thread Starter
    Quote Originally Posted by martyinlincoln View Post
    A 15 degree temperature drop inside and a 11 degree rise outside shows it's not working right. Guessing your installers did a crappy job leak checking their joints.
    I just rechecked. The temp is dropping outside slightly

    Inside 71/56 - 15*
    Outside 101/88 - 13*

    He hooked up some inert gas, and preasure tested it for 30/40 minutes with a digital gauge. Does this seem like a leak may be present?

  8. #8
    Join Date
    Jul 2019
    Posts
    5
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    So 72 is fine!
    The compressor is nonstop running and cannot cool past 74. I can't help but to think something is not quite here.

  9. #9
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by Paulk7269 View Post
    The compressor is nonstop running and cannot cool past 74. I can't help but to think something is not quite here.
    Your at design conditions.
    It’s perfect!

  10. #10
    Join Date
    Jul 2019
    Posts
    5
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    Your at design conditions.
    It’s perfect!
    Ok, got it. I'm just asking more then the unit can provide. I went into the project thinking this *may* be so, but was hoping it was not.

    Thanks for the sanity check.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •