    Or use a 3/4 horsepower medium temp condenser for a walkin cooler.

  2. #22
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by Stevejoe11 View Post
    Just throwing this out there, what if you installed a 1 ton ductless outdoor unit with a 1.5 ton piston coil and simply remove the piston? Then you’d have to alter the condenser wiring and install a basic contactor to control fan and comp, kinda silly but would work no?
    It would be easier to just get a 12,000 BTU ducted mini split.

  3. #23
    Join Date
    Oct 2001
    Location
    Wakefield, MA
    Posts
    64
    Post Likes
    Mitsubishi makes a 1 ton ducted air handler: SVZ-KP12NA It modulates down to 4300BTU/hr.

    https://meus.mylinkdrive.com/files/M...BMITTAL-en.pdf

  4. #24
    Join Date
    Jun 2013
    Location
    Toronto, Ontario
    Posts
    131
    Post Likes
    Quote Originally Posted by captaincompressor View Post
    It would work. It would work. You need a power supply to generate the 40-50 volt DC "s signal" wire.
    I was thinking bypass all controls in the unit and install a contactor to send power to directly to the fan and compressor using a 24v circuit. And I’m nt saying this is the best solution, I’m just saying in theory it could work

  5. #25
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,732
    Post Likes
    Quote Originally Posted by Stevejoe11 View Post
    I was thinking bypass all controls in the unit and install a contactor to send power to directly to the fan and compressor using a 24v circuit. And I’m nt saying this is the best solution, I’m just saying in theory it could work
    Minis don't work that way, several things are constantly being tracked and adjustments are being made accordingly.

  6. #26
    Join Date
    Jul 2012
    Posts
    2,366
    Post Likes
    Quote Originally Posted by Stevejoe11 View Post
    I was thinking bypass all controls in the unit and install a contactor to send power to directly to the fan and compressor using a 24v circuit. And I’m nt saying this is the best solution, I’m just saying in theory it could work
    An old non inverter mini maybe but the newer ones use DC compressors or variable frequency drives that monitor a lot of other parameters.
    You could butcher a window ac and remove the evap coil. Use the supco bullet cap tube size chart and put a cap tube on the evap of the split system. Run a 1/4 x 3/8 line set

  7. #27
    Join Date
    Aug 2000
    Location
    Sandusky Ohio
    Posts
    364
    Post Likes
    Thread Starter
    Hi Everyone, sorry I havent replied and updated earlier but I've had problems logging on. For some reason I log on but only see one post I made years ago. Today I thought I'd try to do a search for myself and it worked, and I was able to find this discussion, very strange.

    I have to apologize to some who suggested to use certain units and I said it would not work. The reason was I thought they were strictly mini-splits, not knowing that they were actually condenser systems. We ended using a Comfort Air unit CMA12 with a regular A-Coil on top of the furnace. It works great after putting start components on it due to the TXV. WORD OF CAUTION, put a liquid line access Tee in, the unit was overcharged since we had short refrigerant lines.
    THANK you to ALL for your kindness, I was very confused, not knowing to do, we are 20% over sized which is ok, using a 1.5 ton unit we would have been over 85% oversized. We adjusted everthing and it works great.
    Rich

  8. #28
    Join Date
    Jul 2012
    Posts
    2,366
    Post Likes
    Quote Originally Posted by Rich View Post
    Hi Everyone, sorry I havent replied and updated earlier but I've had problems logging on. For some reason I log on but only see one post I made years ago. Today I thought I'd try to do a search for myself and it worked, and I was able to find this discussion, very strange.

    I have to apologize to some who suggested to use certain units and I said it would not work. The reason was I thought they were strictly mini-splits, not knowing that they were actually condenser systems. We ended using a Comfort Air unit CMA12 with a regular A-Coil on top of the furnace. It works great after putting start components on it due to the TXV. WORD OF CAUTION, put a liquid line access Tee in, the unit was overcharged since we had short refrigerant lines.
    THANK you to ALL for your kindness, I was very confused, not knowing to do, we are 20% over sized which is ok, using a 1.5 ton unit we would have been over 85% oversized. We adjusted everthing and it works great.
    Rich
    Awesome

  9. #29
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Be simpler to use the 1 ton Heat Controller condenser I pointed out!

  10. #30
    Join Date
    Aug 2000
    Location
    Sandusky Ohio
    Posts
    364
    Post Likes
    Thread Starter
    Quote Originally Posted by BaldLoonie View Post
    Be simpler to use the 1 ton Heat Controller condenser I pointed out!
    BaldLoonie, I appreciate you recommendation, AND we DID USE the Heat_Controller you recommended, it was relabeled under the Comfort Air label.
    I tried to order through two suppliers and they refused to order it, thinking it was a mini split and I finally got it through United Refrigeration who actually took the time to call Mars/Heat-Controller in Jackson, Michigan, had the unit in two days and worked well except it requires a hard start kit when applied to a TXV system.

  11. #31
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Good to hear!

  12. #32
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    6,632
    Post Likes
    Quote Originally Posted by Rich View Post
    BaldLoonie, I appreciate you recommendation, AND we DID USE the Heat_Controller you recommended, it was relabeled under the Comfort Air label.
    I tried to order through two suppliers and they refused to order it, thinking it was a mini split and I finally got it through United Refrigeration who actually took the time to call Mars/Heat-Controller in Jackson, Michigan, had the unit in two days and worked well except it requires a hard start kit when applied to a TXV system.
    How did the one ton compare in price? Was it more or less than a 1.5 ton? I do several apartment buildings and a 1 ton would probably be about correct for them too.


    Sent from my iPhone using Tapatalk

  13. #33
    Join Date
    Aug 2000
    Location
    Sandusky Ohio
    Posts
    364
    Post Likes
    Thread Starter
    I paid $ and I think that was with shipping. The thing I don't like is the unit is made in China, metal is somewhat thin, very light about 90 pounds, (Small) but seems well built. It fits my BTU requirement.
    Last edited by beenthere; 08-27-2019 at 12:05 PM.

  14. Likes jbhenergy liked this post.
  15. #34
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    Install a 2 ton R-410 system with a piston and charge it with R-134.

    PHM
    --------


    Quote Originally Posted by Rich View Post
    Need a one ton condenser with coil, heat gain is 10,300 sensible and 2,700 latent. American Standard and Rheem starts at 1.5 tons. We can't use a mini in this particular installation and customer won't consider a Goodman that I found. Any suggestions of another brand?
    Thanks
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •