I assume the application is remote condenser. If so 12 to 18 degrees sub cooling at full load taking in consideration coil condition.
Sent from my iPhone using Tapatalk
Hi all ,
I’m working on a couple of these units and I am going to be adding in refrigerant charge tomorrow after a leak was repaired. Just wondering about calculating additional charge and if anyone could help me with determining what piping is considered field piping on this unit?? Thank you
I assume the application is remote condenser. If so 12 to 18 degrees sub cooling at full load taking in consideration coil condition.
Sent from my iPhone using Tapatalk
All set now thanks for the reply 👍🏼