    P4 Error Code On Mini Split New install

    Went to a call today. Mini split air handler was displaying a P4 Error Code. When I hooked up my gauges the standing pressure was between 230-240psi for a 410A system. Inside Air temp must have been about 80 degrees .

    Compressor kept short cycling. Any idea what it could be? I thought my standing pressure seemed high. Noticed the compressor would cut out at 150psi also.

    BRAND: PREMIUM
    MODEL: PIAW24180B

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    22,998
    Post Likes
    Contact Tech Support!

  3. #3
    Join Date
    Jul 2011
    Location
    Aurora
    Posts
    224
    Post Likes
    I know Fujitsu will do that if min lineset length too short or too long.
    Low refrigerant charge will also short cyling.

    Sent from my SM-N910W8 using Tapatalk

  4. #4
    Join Date
    Sep 2011
    Posts
    35
    Post Likes
    Thread Starter
    Went back today and same symptoms persisted. Standing pressure of 240 cutting off at 150.

    Tech support said it could be the board but I don't think it's that. The pressures don't look right to me.

    Upon releasing the refrigerant after pulling a vacuum I opened the suction line first before opening the liquid line.

    Could this have been an issue?

    I recovered all the refrigerant and charged it again. Also took amps on the compressor and it ramps up above the water 12amps to around 17 amps before it cuts off.


    Sent from my iPhone using Tapatalk

  5. #5
    Join Date
    May 2015
    Location
    KS
    Posts
    302
    Post Likes
    Outdoor fan check out good?