    Controls Transformer Circuit Breaker Tripping....

    Ive got a 90VA panel transformer that is tripping very inconsistently, Ive installed another 100VA transformer and separated the controller power and the field device power. I've rung the wiring and also made sure there were no direct shots to ground or between the legs on the transformers. There is no rime or reason as to when this thing trips, my next step was going to be to install small in line circuit breakers on the outputs of any load carrying devices. I've used the tattle tales in the past for safeties but not sure if they'd work in this situation. Anyone have any input?
    "The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin

  2. #2
    Join Date
    Nov 2006
    Location
    NW Florida
    Posts
    711
    Post Likes
    Intermittent faults are the worst!

    Give the tattletales a shot. At the very least it could help you define which output/circuit is the problem child.

    If you have successfully separated the power between the control board and devices can you run a trend on when your outputs cycle and when the circuit breaker trips? If you have a spare input maybe you could wire in a relay directly to the transformer and use a spare input to monitor for when the state changes. Run your trends and check for when your outputs change and when that relay changes state.

    It's kind of a long way around but it might help.

    If that doesn't pan out and you are able to use the tattletales to identify which circuit is the issue check for what may be getting wet from condensation or a leaky valve body.

    Good luck!

  3. #3
    Join Date
    May 2018
    Location
    VA/DC
    Posts
    672
    Post Likes
    inline fuses. low amp ones. Or turn one field device at a time and amp it out.
    The way I read your post the field device transformer is tripping?

  4. #4
    Join Date
    Mar 2005
    Location
    Mountain/Pacific Time Zone Typicallly
    Posts
    4,592
    Post Likes
    Have you measured the amperage?

    Have you measured incoming voltage to the transformer? Outgoing voltage from? Voltage at all devices on the transformer?

    Have you done a load calc on the devices that are on the secondary side of the power supply?
    "How it can be considered "Open" is beyond me. Calling it "voyeur-ed" would be more accurate." pka LeroyMac, SkyIsBlue, fka Freddy-B, Mongo, IndyBlue
    BIG Government = More Dependents
    "Any 'standard' would be great if it didn't get bastardised by corporate self interest." MatrixTransform
    My 5 yr old son "Dad, Siri is not very smart when there's no internet."


  5. #5
    Join Date
    May 2002
    Location
    Baton Rouge, Louisiana
    Posts
    4,120
    Post Likes
    Now that you have separated the power is it still tripping? Have you fired off each output one by one to see if it trips on a certain output? I had one job that ate my lunch one time, installed by someone else, worked on by about 10 different companies and I had to repair in place, even chiller start/stops were wired wrong. Anyway there was a York centrifugal that everytime it started it would knock the controller offline for a second and cut off random outputs and lock them. Long story short, I was only given a few hours to troubleshoot everytime I went out there by the customer(not a contract), come to find out the controls contractor had put a ct on the York chiller that was rated for nameplate running amps, not the spike at start, everytime it started the first time it send 15+volts to the inputs and would wreck my controller.
    Quote Originally Posted by MatrixTransform View Post
    very soon it is you that will be pwned

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •