    I have a dead NPM6E here returned from a site. Apparently this site has had multiple failures and this is the one where I was asking about the asd.jar file a while back. Trying to figure out what happened. Jace pings but there is no web page where there should be. Serial shell shows me this;

    Code:
    IPL for NPM 6-E (PPC440EP) v4.00-6.32 ECC
    
    Press <ctrl-c> to stop autoboot...
    
    Commands:
      0: serial
      1: on-board nand flash
      2: on-board nand flash (verbose)
      3: slot 1 nand option card
      4: slot 1 nand option card (verbose)
      5: sdram test, 1 iteration
      6: sdram test, continuous iterations
    IPL>
    
    Try again.
    
    Commands:
      0: serial
      1: on-board nand flash
      2: on-board nand flash (verbose)
      3: slot 1 nand option card
      4: slot 1 nand option card (verbose)
      5: sdram test, 1 iteration
      6: sdram test, continuous iterations
    IPL> 2
    NAND00000001000000F1
    ngi 00000028
    ETFS_FS_2048
    ifs image loaded 00000709 pages
    Image load complete, starting image scan
    
    Scanning flash at     0x02000000
    Found image at        0x02000000
    Jumping to startup at 0x002022D0
    npm6xx startup version 7.00-6.41
    Welcome to QNX Neutrino 6.4 on the NPM 6xx (ppc440)
    fs-etfs-jace2048: readtrans BADBLK on cluster 27904
    fs-etfs-jace2048: readtrans BADBLK on cluster 53632
    
    Press ESC to choose alternate boot options...
    
    continuing boot...
    
    ----------------------TCP/IP Network Status------------------------------
    en0: flags=80008843<UP,BROADCAST,RUNNING,SIMPLEX,MULTICAST,SHIM> mtu 1500
            address: 00:01:f0:8f:0a:08
            media: Ethernet none full-duplex
            status: active
            inet 192.168.1.123 netmask 0xffffff00 broadcast 192.168.1.255
            inet6 fe80::201:f0ff:fe8f:a08%en0 prefixlen 64 tentative scopeid 0x2
    -------------------------------------------------------------------------
    
    NPM6-E with T2023 JACE-2 Base Board detected
    SRAM mounted successfully at /sramopt
    MESSAGE [06:58:49 01-Jul-2019] [tid = 2] niagarad: starting, baja_home=/niagara
    MESSAGE [06:58:49 01-Jul-2019] [tid = 2] webserver: web server threads started [threadCount = 1]
    MESSAGE [06:58:49 01-Jul-2019] [tid = 2] app registry: station registry starting
    login:
    Sounds like the memory is no good with those bad block messages?

    This doesn't sound good;

    Code:
    Commands:
      0: serial
      1: on-board nand flash
      2: on-board nand flash (verbose)
      3: slot 1 nand option card
      4: slot 1 nand option card (verbose)
      5: sdram test, 1 iteration
      6: sdram test, continuous iterations
    IPL> 5
    memTestDevice from 0x00030000to 0x10000000
    
    Try again.
    
    Commands:
      0: serial
      1: on-board nand flash
      2: on-board nand flash (verbose)
      3: slot 1 nand option card
      4: slot 1 nand option card (verbose)
      5: sdram test, 1 iteration
      6: sdram test, continuous iterations
    IPL> 5
    memTestDevice from 0x00030000to 0x10000000
    
    Try again.
    
    Commands:
      0: serial
      1: on-board nand flash
      2: on-board nand flash (verbose)
      3: slot 1 nand option card
      4: slot 1 nand option card (verbose)
      5: sdram test, 1 iteration
      6: sdram test, continuous iterations
    IPL>
    Moving to a computer where I have workbench, seems that might have a chance of connecting to the platform anyway.

  2. #2
    Join Date
    May 2009
    Location
    SC
    Posts
    4,047
    Post Likes
    Thread Starter
    This is everything I can see in application director, I wasn't able to catch the rest for some reason.

    Code:
    ead "Ping:AsdNetwork", waiting until one is available (attempt 1 of 3)
    WARNING [13:19:02 08-May-19 EDT][platDataRecovery.service] No idle block available at time of flush on thread "Ping:AsdNetwork", waiting until one is available (attempt 1 of 3)
    WARNING [13:19:03 08-May-19 EDT][platDataRecovery.service] No idle block available at time of flush on thread "server:worker", waiting until one is available (attempt 2 of 3)
    WARNING [13:19:05 08-May-19 EDT][platDataRecovery.service] No idle block available at time of flush on thread "Ping:AsdNetwork", waiting until one is available (attempt 2 of 3)
    WARNING [13:19:05 08-May-19 EDT][platDataRecovery.service] No idle block available at time of flush on thread "Ping:AsdNetwork", waiting until one is available (attempt 2 of 3)
    WARNING [13:19:06 08-May-19 EDT][platDataRecovery.service] No idle block available at time of flush on thread "server:worker", waiting until one is available (attempt 3 of 3)
    WARNING [13:19:08 08-May-19 EDT][platDataRecovery.service] No idle block available at time of flush on thread "Ping:AsdNetwork", waiting until one is available (attempt 3 of 3)
    WARNING [13:19:08 08-May-19 EDT][platDataRecovery.service] No idle block available at time of flush on thread "Ping:AsdNetwork", waiting until one is available (attempt 3 of 3)
    ERROR [13:19:09 08-May-19 EDT][platDataRecovery.service] Could not obtain an idle block when attempting to flush, a serious error has occured
    java.lang.Exception: Stack trace
     at java.lang.Thread.dumpStack(Unknown Source)
     at com.tridium.platDataRecovery.BDataRecoveryService.doFlushRecoveryData(BDataRecoveryService.java)
     at com.tridium.platDataRecovery.BDataRecoveryService.append(BDataRecoveryService.java)
     at com.tridium.platDataRecovery.BDataRecoveryService.append(BDataRecoveryService.java)
     at com.tridium.history.BDataRecoveryHistoryRecorder.historyEvent(BDataRecoveryHistoryRecorder.java)
     at javax.baja.history.db.BHistoryDatabase.fireHistoryEvent(BHistoryDatabase.java)
     at com.tridium.history.db.BLocalDbHistory.append(BLocalDbHistory.java)
     at com.tridium.history.audit.BAuditHistoryService.audit(BAuditHistoryService.java)
     at com.tridium.sys.schema.ComplexSlotMap.audit(ComplexSlotMap.java)
     at com.tridium.sys.schema.ComplexSlotMap.audit(ComplexSlotMap.java)
     at com.tridium.sys.schema.ComplexSlotMap.set(ComplexSlotMap.java)
     at javax.baja.sys.BComplex.set(BComplex.java)
     at javax.baja.bacnet.export.BBacnetAnalogWritableDescriptor.writePriorityArray(BBacnetAnalogWritableDescriptor.java)
     at javax.baja.bacnet.export.BBacnetAnalogWritableDescriptor.writeProperty(BBacnetAnalogWritableDescriptor.java)
     at javax.baja.bacnet.export.BBacnetPointDescriptor.writeProperty(BBacnetPointDescriptor.java)
     at com.tridium.bacnet.stack.server.PropertyHandler.processWritePropertyMultipleRequest(PropertyHandler.java)
     at com.tridium.bacnet.stack.server.PropertyHandler.receiveRequest(PropertyHandler.java)
     at com.tridium.bacnet.stack.server.BBacnetServerLayer.processConfirmedRequest(BBacnetServerLayer.java)
     at com.tridium.bacnet.stack.server.BBacnetServerLayer.process(BBacnetServerLayer.java)
     at com.tridium.bacnet.stack.server.BBacnetServerLayer$ServerRequest.run(BBacnetServerLayer.java)
     at javax.baja.util.Worker.process(Worker.java)
     at javax.baja.util.Worker$Processor.run(Worker.java)
     at java.lang.Thread.run(Unknown Source)
    ERROR [13:19:09 08-May-19 EDT][platDataRecovery.service] Flush operation failed.
    ERROR [13:19:12 08-May-19 EDT][platDataRecovery.service] Could not obtain an idle block when attempting to flush, a serious error has occured
    java.lang.Exception: Stack trace
     at java.lang.Thread.dumpStack(Unknown Source)
     at com.tridium.platDataRecovery.BDataRecoveryService.doFlushRecoveryData(BDataRecoveryService.java)
     at com.tridium.platDataRecovery.BDataRecoveryService.update(BDataRecoveryService.java)
     at com.tridium.dataRecovery.BDataRecoveryComponentRecorder.record(BDataRecoveryComponentRecorder.java)
     at com.tridium.sys.schema.ComplexSlotMap.set(ComplexSlotMap.java)
     at javax.baja.sys.BComplex.set(BComplex.java)
     at javax.baja.serial.BSerialHelper.setBaudRate(BSerialHelper.java)
     at com.ibms.asd.request.InitializeBaudRateReq.run(InitializeBaudRateReq.java)
     at com.ibms.asd.BAsdNetwork.setNetworkBaudRate(BAsdNetwork.java)
     at com.ibms.asd.BAsdMonitor.run(BAsdMonitor.java)
     at java.lang.Thread.run(Unknown Source)
    ERROR [13:19:12 08-May-19 EDT][platDataRecovery.service] Flush operation failed.
    ERROR [13:19:15 08-May-19 EDT][platDataRecovery.service] Could not obtain an idle block when attempting to flush, a serious error has occured
    java.lang.Exception: Stack trace
     at java.lang.Thread.dumpStack(Unknown Source)
     at com.tridium.platDataRecovery.BDataRecoveryService.doFlushRecoveryData(BDataRecoveryService.java)
     at com.tridium.platDataRecovery.BDataRecoveryService.update(BDataRecoveryService.java)
     at com.tridium.dataRecovery.BDataRecoveryComponentRecorder.record(BDataRecoveryComponentRecorder.java)
     at com.tridium.sys.schema.ComplexSlotMap.modified(ComplexSlotMap.java)
     at com.tridium.sys.schema.ComplexSlotMap.set(ComplexSlotMap.java)
     at javax.baja.sys.BComplex.set(BComplex.java)
     at javax.baja.driver.ping.BPingHealth.setLastOkTime(BPingHealth.java)
     at javax.baja.driver.ping.BPingHealth.pingOk(BPingHealth.java)
     at javax.baja.driver.BDevice.pingOk(BDevice.java)
     at com.ibms.asd.BAsdDevice.doPing(BAsdDevice.java)
     at com.ibms.asd.BAsdMonitor.run(BAsdMonitor.java)
     at java.lang.Thread.run(Unknown Source)
    ERROR [13:19:15 08-May-19 EDT][platDataRecovery.service] Flush operation failed.
    ENGINE WATCHDOG TIMEOUT STACK DUMP @ Wed May 08 13:21:05 EDT 2019Full thread dump Java HotSpot(TM) Client VM (1.5.0_34-b28 mixed mode):
    
    "/Services/JobService/StationSaveJob3" prio=5 tid=0x488ead10 nid=0x3b runnable [0x46399000..0x4639aac0]
     at java.net.PlainSocketImpl.socketConnect(Native Method)
     at java.net.PlainSocketImpl.doConnect(Unknown Source)
     - locked <0x4abf8d78> (a java.net.SocksSocketImpl)
     at java.net.PlainSocketImpl.connectToAddress(Unknown Source)
     at java.net.PlainSocketImpl.connect(Unknown Source)
     at java.net.SocksSocketImpl.connect(Unknown Source)
     at java.net.Socket.connect(Unknown Source)
     at java.net.Socket.connect(Unknown Source)
     at sun.net.NetworkClient.doConnect(Unknown Source)
     at sun.net.www.http.HttpClient.openServer(Unknown Source)
     at sun.net.www.http.HttpClient.openServer(Unknown Source)
     - locked <0x4abf8eb8> (a sun.net.www.http.HttpClient)
     at sun.net.www.http.HttpClient.<init>(Unknown Source)
     at sun.net.www.http.HttpClient.New(Unknown Source)
     at sun.net.www.http.HttpClient.New(Unknown Source)
     at sun.net.www.protocol.http.HttpURLConnection.getNewHttpClient(Unknown Source)
     at sun.net.www.protocol.http.HttpURLConnection.plainConnect(Unknown Source)
     at sun.net.www.protocol.http.HttpURLConnection.connect(Unknown Source)
     at sun.net.www.protocol.http.HttpURLConnection.getInputStream(Unknown Source)
     - locked <0x4abf8f40> (a sun.net.www.protocol.http.HttpURLConnection)
     at java.net.HttpURLConnection.getResponseCode(Unknown Source)
     at com.tridium.platform.daemon.LocalSessionUtil.localDaemonIsAvailable(LocalSessionUtil.java)
     at com.tridium.platform.BSystemPlatformService$SaveListener.stationSaveOk(BSystemPlatformService.java)
     at com.tridium.sys.station.Station.saveOk(Station.java)
     at com.tridium.sys.station.Station.saveSync(Station.java)
     - locked <0x4975f5d8> (a java.lang.Object)
     at com.tridium.sys.station.Station.saveSync(Station.java)
     at com.tridium.sys.station.BStationSaveJob.run(BStationSaveJob.java)
     at javax.baja.job.BSimpleJob$JobThread.run(BSimpleJob.java)
    
    "BSystemPlatformServiceQnx::failureRebootUpdateThread" prio=5 tid=0x48ba10f8 nid=0x3c runnable [0x46319000..0x4631a9c0]
     at java.net.PlainSocketImpl.socketConnect(Native Method)
     at java.net.PlainSocketImpl.doConnect(Unknown Source)
     - locked <0x4abe5638> (a java.net.SocksSocketImpl)
     at java.net.PlainSocketImpl.connectToAddress(Unknown Source)
     at java.net.PlainSocketImpl.connect(Unknown Source)
     at java.net.SocksSocketImpl.connect(Unknown Source)
     at java.net.Socket.connect(Unknown Source)
     at java.net.Socket.connect(Unknown Source)
     at java.net.Socket.<init>(Unknown Source)
     at ja

  3. #3
    Join Date
    May 2009
    Location
    SC
    Posts
    4,047
    Post Likes
    Thread Starter
    Ah crap, file system full maybe? What fills up in a jace?

    /var/log didn't have anything in it.
    /ffs0/niagara/stations really didn't have anything of a significant size in it under history or alarms.
    /ffs0/niagara/stations/dataRecovery directory was full of things like 1202407.drdb 133kb files. 518 of them and that only works out to like just under 70MB?
    /dev/mem shows file size 4,194,303KB. Seems big but normal for a copy of memory.

    Code:
    Platform summary for 192.168.1.123
    ----------------------------------
    
    Daemon HTTP Port:     3011
    Host ID:              Qnx-NPM6E-xxxx
    Niagara Runtime:      nre-core-qnx-ppc (3.7.106.1)
    Architecture:         ppc
    Number of CPUs:       1
    Model:                NPM6E
    Module Contents:      runtime
    Strip line nos.:      true
    Operating System:     qnx-jace-npm6xx-etfs2048 (2.6.27)
    Java Virtual Machine: sun-jre-qnx-ppc (Sun Microsystems Inc. 1.5.0.34.28)
    Niagara Stations Enabled: enabled
    Sedona Support:       unsupported
    Niagara R2 Support:   unsupported
    Platform SSL Support: disabled
    Port:                 5011
    Certificate:          tridium
    Protocol:             SSLv3+TLSv1
    System Home:          /niagara
    
    Physical RAM  Free            Total         
                      218,240 KB      262,144 KB
    
    Filesystem    Free            Total           Block Size    Files         Max Files   
      /ffs0                 2 KB      126,976 KB   2,048 bytes          1314          4096
    
    Modules
      alarm (Tridium 3.7.106)
      app (Tridium 3.7.106)
      asd (IBMS 3.5.34)
      backup (Tridium 3.7.106)
      bacnet (Tridium 3.7.106)
      baja (Tridium 3.7.106.1)
      bajaScript (Tridium 3.7.106)
      bajaui (Tridium 3.7.106)
      basicDriver (Tridium 3.7.106)
      box (Tridium 3.7.106)
      bql (Tridium 3.7.106)
      chart (Tridium 3.7.106)
      control (Tridium 3.7.106)
      converters (Tridium 3.7.106)
      driver (Tridium 3.7.106)
      file (Tridium 3.7.106)
      fonts (Tridium 3.7.106)
      fox (Tridium 3.7.106.1)
      gx (Tridium 3.7.106)
      history (Tridium 3.7.106)
      html (Tridium 3.7.106)
      hx (Tridium 3.7.106)
      icons (Tridium 3.7.106)
      js (Tridium 3.7.106)
      kitPx (Tridium 3.7.106)
      lonworks (Tridium 3.7.106)
      net (Tridium 3.7.106)
      niagaraDriver (Tridium 3.7.106)
      niagaraVirtual (Tridium 3.7.106)
      nsh (Tridium 3.7.106)
      oro (Tridium 3.7.106)
      pdf (Tridium 3.7.106)
      platBacnet (Tridium 3.7.106)
      platDataRecovery (Tridium 3.7.106)
      platLon (Tridium 3.7.106)
      platMstp (Tridium 3.7.106)
      platPower (Tridium 3.7.106)
      platSerial (Tridium 3.7.106)
      platSerialQnx (Tridium 3.7.106)
      platform (Tridium 3.7.106)
      program (Tridium 3.7.106)
      query (Tridium 3.7.106)
      schedule (Tridium 3.7.106)
      serial (Tridium 3.7.106)
      tunnel (Tridium 3.7.44)
      wbutil (Tridium 3.7.106)
      web (Tridium 3.7.106.4)
      wiresheet (Tridium 3.7.106)
      workbench (Tridium 3.7.106)
      zwave (Tridium 3.7.106)
    
    Other Parts
      npm6xx-etfs2048 (1.2)
    
    Applications
      station xxxx autostart=false, autorestart=true, status=Idle
    
    Lexicons
    
    Licenses
      JENEsys.license (Tridium 3.7 - never expires)
      Lynxspring.license (Lynxspring 3.7 - never expires)
    
    Certificates
      Lynxspring.certificate (Lynxspring - never expires)
      Tridium.certificate (Tridium - never expires)

  4. #4
    Join Date
    Jan 2003
    Location
    USA
    Posts
    9,437
    Post Likes
    Sounds like the data recovery bug.

    Delete some / all of those files, reboot and then upgrade to the latest 3.7 version.
    Propagating the formula. http://www.noagendashow.com/

  5. #5
    Join Date
    May 2009
    Location
    SC
    Posts
    4,047
    Post Likes
    Thread Starter
    Which file should I be deleting? I pulled back the entire station directory and it was only 68MB.

    I see some other things that can go like lonworks.jar and zwave.jar.

  6. #6
    Join Date
    Jan 2003
    Location
    USA
    Posts
    9,437
    Post Likes
    Stuff in the data recovery folder. Normally dump it all, but if you want to be safe just get all the old files and keep the 3-4 most recent.

  7. #7
    Join Date
    May 2009
    Location
    SC
    Posts
    4,047
    Post Likes
    Thread Starter
    Cleaned out the files and restarted, same issue. Application director said auto start was disabled. Told it to start and it started, looked normal until I saw tons of these errors scream by.

    I don't think I saw the Asd Block Proxy Ext errors in the backup station I had.

    I'm reasonably sure the Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow errors in that station backup I had and I resolved that by deleting exposed BACnet points for ASD equipment that didn't exist any more.

    So it seems we might not have had to replace the actual jace here, hardware is OK? What about those memory tests that didn't come back and those BADBLK errors on serial shell?

    Code:
    ERROR [09:49:20 01-Jul-19 EDT][sys.engine] Cannot start component: Asd Block Proxy Ext
    java.lang.NullPointerException
       at com.ibms.asd.point.BAsdBlockProxyExt.initProxyExt(BAsdBlockProxyExt.java)
       at com.ibms.asd.point.BAsdBlockProxyExt.started(BAsdBlockProxyExt.java)
       at com.tridium.sys.engine.EngineUtil.started(EngineUtil.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
    ERROR [09:49:20 01-Jul-19 EDT][sys.engine] Cannot start component: Asd Block Proxy Ext
    java.lang.NullPointerException
       at com.ibms.asd.point.BAsdBlockProxyExt.initProxyExt(BAsdBlockProxyExt.java)
       at com.ibms.asd.point.BAsdBlockProxyExt.started(BAsdBlockProxyExt.java)
       at com.tridium.sys.engine.EngineUtil.started(EngineUtil.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
    ERROR [09:49:20 01-Jul-19 EDT][sys.engine] Cannot start component: Asd Block Proxy Ext
    java.lang.NullPointerException
       at com.ibms.asd.point.BAsdBlockProxyExt.initProxyExt(BAsdBlockProxyExt.java)
       at com.ibms.asd.point.BAsdBlockProxyExt.started(BAsdBlockProxyExt.java)
       at com.tridium.sys.engine.EngineUtil.started(EngineUtil.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
    ERROR [09:49:20 01-Jul-19 EDT][sys.engine] Cannot start component: Asd Block Proxy Ext
    java.lang.NullPointerException
       at com.ibms.asd.point.BAsdBlockProxyExt.initProxyExt(BAsdBlockProxyExt.java)
       at com.ibms.asd.point.BAsdBlockProxyExt.started(BAsdBlockProxyExt.java)
       at com.tridium.sys.engine.EngineUtil.started(EngineUtil.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
    ERROR [09:49:20 01-Jul-19 EDT][sys.engine] Cannot start component: Asd Block Proxy Ext
    java.lang.NullPointerException
       at com.ibms.asd.point.BAsdBlockProxyExt.initProxyExt(BAsdBlockProxyExt.java)
       at com.ibms.asd.point.BAsdBlockProxyExt.started(BAsdBlockProxyExt.java)
       at com.tridium.sys.engine.EngineUtil.started(EngineUtil.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
       at com.tridium.sys.schema.ComponentSlotMap.start(ComponentSlotMap.java)
       at javax.baja.sys.BComponent.start(BComponent.java)
       at com.tridium.sys.engine.EngineManager.start(EngineManager.java)
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.heatDisable [binaryValue:156]: h:35d1
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.emsMorningWarmup [binaryValue:157]: h:35d3
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.emsOccupied [binaryValue:158]: h:35d5
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.emsCoolSetpoint [analogValue:390]: h:35d7
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.emsHeatSetpoint [analogValue:391]: h:35d9
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.emsUnoccHeatSetpoint [analogValue:392]: h:35db
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.occupancyStatus [binaryValue:159]: h:35e5
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.do1Status [binaryValue:160]: h:35e7
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.do3Status [binaryValue:161]: h:35eb
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.zoneTemp [analogValue:393]: h:35fd
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.boxFlow [analogValue:394]: h:35ff
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.coolOutput [analogValue:395]: h:3601
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.heatOutput [analogValue:396]: h:3603
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.auxTemp [analogValue:397]: h:3605
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.controlCoolSetpt [analogValue:398]: h:3607
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.controlHeatSetpt [analogValue:399]: h:3609
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.unoccHeatSetpt [analogValue:400]: h:360b
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.controlMaxFlow [analogValue:401]: h:360d
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.controlMinFlow [analogValue:402]: h:360f
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.flowSetpt [analogValue:403]: h:3615
    WARNING [09:49:41 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_36_402.points.overrideTime [analogValue:404]: h:3619
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.heatDisable [binaryValue:288]: h:13918
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.emsMorningWarmup [binaryValue:289]: h:1391a
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.emsOccupied [binaryValue:290]: h:1391c
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.emsCoolSetpoint [analogValue:720]: h:1391e
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.emsHeatSetpoint [analogValue:721]: h:13920
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.emsUnoccHeatSetpoint [analogValue:722]: h:13922
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.occupancyStatus [binaryValue:291]: h:1392c
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.do1Status [binaryValue:292]: h:1392e
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.do3Status [binaryValue:293]: h:13932
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.zoneTemp [analogValue:723]: h:13944
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.boxFlow [analogValue:724]: h:13946
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.coolOutput [analogValue:725]: h:13948
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.heatOutput [analogValue:726]: h:1394a
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.auxTemp [analogValue:727]: h:1394c
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.controlCoolSetpt [analogValue:728]: h:1394e
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.controlHeatSetpt [analogValue:729]: h:13950
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.unoccHeatSetpt [analogValue:730]: h:13952
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.controlMaxFlow [analogValue:731]: h:13954
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.controlMinFlow [analogValue:732]: h:13956
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.flowSetpt [analogValue:733]: h:1395c
    WARNING [09:49:43 01-Jul-19 EDT][bacnet.server] Unable to resolve point ord for Drivers.AsdNetwork.AsdMnFlow_58_414.points.overrideTime [analogValue:734]: h:13960
    MESSAGE [09:49:48 01-Jul-19 EDT][web.server] HTTP Server started on port [80]
    MESSAGE [09:49:49 01-Jul-19 EDT][fox] FOX server started on port [1911]
    MESSAGE [09:49:49 01-Jul-19 EDT][sys] Niagara Runtime Environment: 3.7.106.1
    MESSAGE [09:49:49 01-Jul-19 EDT][sys] *** Station Started (41638ms) [118418ms total] ***
    niagara>MESSAGE [09:49:51 01-Jul-19 EDT][sys] Saving station...
    WARNING [09:50:20 01-Jul-19 EDT][fox] Closing session [0: Server 192.168.1.200:55419 doesn't match opened session [null]
    MESSAGE [09:50:27 01-Jul-19 EDT][fox] Opened: 1 <- 1 :: Workbench @ computer
    MESSAGE [09:51:03 01-Jul-19 EDT][history.db] Saved history archive (280ms)
    MESSAGE [09:51:05 01-Jul-19 EDT][sys] Saved /ffs0/niagara/stations/name/config.bog (73651ms)

  8. #8
    Join Date
    Apr 2007
    Location
    San Diego, CA
    Posts
    2,254
    Post Likes
    Quote Originally Posted by MaxBurn View Post
    So it seems we might not have had to replace the actual jace here, hardware is OK? What about those memory tests that didn't come back and those BADBLK errors on serial shell?
    fs-etfs-jace2048 BADBLK messages are normal, I'm told it's just the file system doing some routine maintenance.

    As for the data recovery service, there's a thread on the niagara-community site with an explanation from one of Tridium's engineers.

    https://www.niagara-community.com/_u...D5D000005DPJLK

  9. #9
    Join Date
    May 2009
    Location
    SC
    Posts
    4,047
    Post Likes
    Thread Starter
    Good find there and I feel more assured the unit we sent out is going to be a long term fix as it was updated to the latest 3.7 mentioned there.

    Funny thing, this jace had a battery in it all along.

  10. #10
    Join Date
    Jan 2003
    Location
    USA
    Posts
    9,437
    Post Likes
    Ditto on the bad blocks, seen this on more than one working unit.

    If a Jace only boots to the IPL command line, its usually a door stop. If you can get to the full serial shell menu, its normally nothing that can't be dealt with.

    On units with battery, I normally disable data recovery since it seemed to cause more harm than good. It seems they have gotten past the initial issues with it these days.
    Propagating the formula. http://www.noagendashow.com/

  11. #11
    Join Date
    May 2009
    Location
    SC
    Posts
    4,047
    Post Likes
    Thread Starter
    Full serial shell menu like the ctrl-c one with the memory tests etc in it? Not sure which part you are referring to.

  12. #12
    Join Date
    Jan 2003
    Location
    USA
    Posts
    9,437
    Post Likes
    Full serial has the options to change the IP, reset platform creds, etc.

    IPL is the IPL> command prompt. That's where the memory tests are. If the Jace only boots to that point, its warranty return or door stop. Platform is not running, cannot enable FTP, pretty screwed.
    Propagating the formula. http://www.noagendashow.com/

  13. #13
    Join Date
    May 2009
    Location
    SC
    Posts
    4,047
    Post Likes
    Thread Starter
    Got it, thanks again.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •