    Quote Originally Posted by Dave122290 View Post
    Thanks for the reply. Good info I read a lot of that manual last night. Can’t find much on the RTHC.
    FYI
    RTHC-SVB010-EN Corrosion on Steel Piping.p9t80.pdf

  2. #15
    Join Date
    Feb 2017
    Location
    Australia
    Posts
    19
    Post Likes
    Think it would be best if you install isolation valves on both sides of the liquid level sensor to prevent refrigerant being removed again if future works is required on the liquid level sensor.

    I would also inspect the oil return system lines as no doubt they are bundy steel also therefore these should be replaced.

    Oh and another recommendation would be to carry out the oil return enhancement as well

    Sent from my SM-G965F using Tapatalk

  3. #16
    Join Date
    Jun 2017
    Location
    Ct
    Posts
    10
    Post Likes
    Thread Starter
    Thanks for the reply. Didn’t put ball valves on. Would of been a good idea. Job is complete and the chiller is running good with no issues. York YK repair next 🛠