    I have recently started doing refrigeration after a few years in residential hvac. I am working on a walk in cooler with 30 deg sh and 10 sub cool. I asked a friend and he tells tells me to charge using super heat regardless of txv telling me refrigeration is different than a/c. From what I know, txv regulates sh, so I would like clarification
    Jan 2010
    Sea to Sky
    If it has a receiver and sight glass, charge it to just clear the sight glass of bubbles.
    If the condensing is outdoors and has a headmaster control, then it gets a bit more complicated to calculate the correct winter charge.
    You are correct that the TXV regulates superheat. It should be set to the required superheat when the box is close to set point.
    It is not a throttle and you cannot charge a unit by superheat with one installed.
    Sent from my SM-G965W using Tapatalk
    Jun 2019
    Maryland
    New to the forums but becoming ancient in the field. Significant differences in refrigeration vs. comfort cooling (HVAC). If I may help:
    TXV systems charge by clear sight glass or 5-7 deg subcooling with receiver if no SG. Superheat of 30deg is high for WI cooler you want more out of your evaporator; try ~10 deg general rule. AS per TXV manufacturers: "TXV should have full column of liquid at all times." You cannot charge by superheat as BALloyd said as a TXV is a superheat regulator and will strive to maintain its setpoint at all times.
    Jan 2010
    If he's got 10f of sub cooling with a receiver I'm gonna guess it's over charged to the point that it's backing up into the condenser.
    Sounds like someone tried to get the suction up when there was a restriction in place.
    May 2014
    Bay Area California
    30*F could be normal if it is a remote condensing unit and you are measuring SH at the compressor. Not enough information to give you a proper answer.
    Quote Originally Posted by arctictulsa View Post
    I do a triple evac with nitro to remove non condensables.
    Jan 2010
    What about that 10f sub cooling ?
    May 2014
    Bay Area California
    That could also be normal. If there is no receiver.
    Southeastern Pa
    This is another great place to recommend the book, "Commercial Refrigeration for Air Conditioning Technicians."
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Jan 2010
    Quote Originally Posted by BBeerme View Post
    Yeah but I've never seen a walk-in without one. Now those little pizza prep tables sure. TXV for the rail and a cap tube or TXV for the cabinet. Not much room in those for a receiver. Also critically charged.
    May 2014
    Bay Area California
    What if there is a 30-foot rise? Even with a receiver there would be no subcooling at the expansion valve.
    You see, there is just not enough information to help this guy yet.
    Jan 2010
    Right, I'm assuming 10f sub cooling @ the condenser.
    May 2014
    Bay Area California
    I'm just saying that there is too much we do not know. Sort of like my co-workers who do not even use the proper terminology. I keep telling them that I will give you the answer to your question, but your question may not be worded properly so you will get the wrong information.
    Gawd, I wish my co-workers would come on this forum just so they could learn how to speak properly, I mean, use the right words for what they are trying to ask.
  13. Likes icemeister, trippintl0 liked this post.
  14. #13
    Jan 2010
    I here ya, a lot can get lost in misinterpretation.
  15. #14
    Southeastern Pa
    A few years ago, we had a long thread about subcooling and receivers.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
  16. #15
    May 2014
    Bay Area California
    Likely I was part of that thread. And created more controversy by what I was posting.
    Especially since the 'rule of thumb' is frequently broken for what the ol' timers keep sayin' on here; some equipment has it's own set of rules. And if you pay attention to them, your troubleshooting processes will be greatly shortened.
    Been there, done that.
    Quote Originally Posted by timebuilder View Post
  17. #16
    Virginia
    Just tear it all out and install a coolbot
  18. Likes trippintl0 liked this post.
  19. #17
    Oct 2009
    Atlanta,Ga.
    clear the sightglass..Set the superheat when the box is close to temp.Dont pay attention to the superheat until the box is close to temp, unless it is obviously flooding bad, compressor real cold.then close the valve some.But under normal situations, with a properly sized and working TXV,dont worry about superheat when first charging.check when the box temp is close to temp.This is a TEV,not a piston, likeA/c.Don't use superheat as a charging tool.Use superheat to set valve(8-12 degrees) for proper TEV operation and to protect the compressor from getting liquid back to it.If you have low suction ,check for restrictions, plugged drier, maybe clogged screen on TEV ,but sightless will still be clear.
  20. #18
    May 2014
    Bay Area California
    Okay.
    Let's go back to the beginning.
    Is there a problem with this unit?
    I'm guessing no.
  21. #19
    May 2014
    Bay Area California
    If that is the case, the best thing to do here is log the data in your brain, and move on to the next call.
  22. #20
    Southeastern Pa
    And buy a copy of the book.....
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules: