    Old HVAC tech needs Heat Pump advice

    Hello everyone, I’m and old commercial HVAC tech that has been out of the game for awhile. I am working on my buddies Trane XR12 Heat Pump and came across some strange pressure readings. His unit is operating fine in A/C mode but in Heat Mode the pressures are running 280 on the low side and 650 on the high side. It would hit 650 then shut down on the high pressure switch and come back on when it got below 500. The unit is a 410a system and I did the normal checks on air flow through both coils making sure there was no obstructions. I went ahead and took a super heat reading and it was at 10 which is ok if I remember on these units. Could the reversing valve be leaking through? I am real rusty on diagnosing these units so any help would be appreciated.

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,739
    Post Likes
    Air Flow issue indoors or overcharged.
    Pull and weigh the total charge.

    How did you check indoor air flow?

  3. #3
    Join Date
    Jun 2019
    Posts
    10
    Post Likes
    Thread Starter
    I pulled the front Coil housing and did a flashlight check seemed clean but I know there could be something I might not be seeing. Is there a better way I could check it? Seems like if I’m pegging that high side Pressure switch I would see a lower pressure on the suction side during A/C mode if my coil is plugged? Thanks for the quick reply

  4. #4
    Join Date
    Jun 2019
    Location
    Gloucester City, NJ
    Posts
    26
    Post Likes
    I was going to say overcharge as well.
    Being you have been out of the field for some while are you familiar with the temperamental 410a?
    What was your cooling pressures along with outdoor ambient temp and return air temp.

    Sent from my SM-G960U using Tapatalk

  5. #5
    Join Date
    Jun 2019
    Posts
    10
    Post Likes
    Thread Starter
    They were just switching over the R-22 units when I got out of the field so I don’t have a ton of experience with them. The unit in A/C mode was running 125 on the suction and 330 on the high side. Indoor return temp was 72 and it was 80 outside.

  6. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,739
    Post Likes
    Quote Originally Posted by Oak54 View Post
    They were just switching over the R-22 units when I got out of the field so I don’t have a ton of experience with them. The unit in A/C mode was running 125 on the suction and 330 on the high side. Indoor return temp was 72 and it was 80 outside.
    You cant run in heat mode at those temperatures!

  7. #7
    Join Date
    Jun 2019
    Location
    Gloucester City, NJ
    Posts
    26
    Post Likes
    Quote Originally Posted by pecmsg View Post
    You cant run in heat mode at those temperatures!
    He's right

    Sent from my SM-G960U using Tapatalk

  8. #8
    Join Date
    Jan 2010
    Location
    Central Texas
    Posts
    259
    Post Likes
    Quote Originally Posted by pecmsg View Post
    You cant run in heat mode at those temperatures!
    That's what I was going to say.

    Unless you shut off the Outdoor Fan Motor in the heat mode, thus reducing the heat absorbed by the Outdoor Coil, which would be the Evaporator in the Heat Mode.

  9. Likes Dhumphries82 liked this post.
  10. #9
    Join Date
    Apr 2010
    Location
    California
    Posts
    717
    Post Likes
    I agree with all that has been said here so far, and would like to add another thought if i may. When you have a situation like this, with many unknowns, it best to play it safe, and check the refrigerant charge PURITY, before you charge it back in the unit, after recovery. Cross contaminated refrigerants can also produce high head pressure readings, so re-charge with virgin gas "If You Are In Doubt", and Welcome to the Site.

  11. Likes Dhumphries82 liked this post.
  12. #10
    Join Date
    Jun 2019
    Posts
    10
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    You cant run in heat mode at those temperatures!
    He said this was happening in the dead of winter and never had anybody check it out. How could I simulate it to check out Heat mode?

  13. #11
    Join Date
    Jun 2019
    Posts
    10
    Post Likes
    Thread Starter
    Thanks for the info, I have a old bottle so I probably will weigh it in tomorrow when I go back out there.

  14. #12
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,739
    Post Likes
    Quote Originally Posted by Oak54 View Post
    He said this was happening in the dead of winter and never had anybody check it out. How could I simulate it to check out Heat mode?
    Heat pumps are charged in cooling mode. A S S U M I N G the evaporator coil and air handler are sized and installed properly with NO duct issues that's good enough!

  15. #13
    Join Date
    Apr 2006
    Location
    Tyler, Tx
    Posts
    1,793
    Post Likes
    Is the airflow set correctly for the heat mode? Airflow may be too low, remember that in heat mode the inside unit turns into the condenser and the outside unit turns into the evaporator.

    Now, what symptoms can cause high head?
    Philippians 4:13
    I can do all things in him that strengthen me.
    Apostle Paul inspired by GOD.

  16. #14
    Join Date
    Jun 2019
    Posts
    10
    Post Likes
    Thread Starter
    I checked the numbers and everything seems sized right. Even though it was 80 out I can’t see the pressure pegging to 650 after a couple of minutes running in heat mode. I will try unhooking the outdoor fan and get some pressure readings when I go back out there.

  17. #15
    Join Date
    Jun 2019
    Posts
    10
    Post Likes
    Thread Starter
    I will check the indoor fan in both modes but I don’t believe I heard a difference between both modes when I was out there. Thanks for the advice

  18. #16
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,739
    Post Likes
    Quote Originally Posted by Oak54 View Post
    I checked the numbers and everything seems sized right. Even though it was 80 out I can’t see the pressure pegging to 650 after a couple of minutes running in heat mode. I will try unhooking the outdoor fan and get some pressure readings when I go back out there.
    Please Do Not run in heat mode at those temperatures.

    Read and understand the manual...….Heat pump charges are checked in cooling!!!!!!!!!!!!

  19. #17
    Join Date
    Jun 2019
    Posts
    10
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    Please Do Not run in heat mode at those temperatures.

    Read and understand the manual...….Heat pump charges are checked in cooling!!!!!!!!!!!!
    So is it impossible to check the heat mode in the summer?

  20. #18
    Join Date
    Apr 2006
    Location
    Tyler, Tx
    Posts
    1,793
    Post Likes
    You can turn off the outside fan, as mentioned earlier, but you will not be able to recreate the issue. If it is running fine in cooling mode, I would wait for either a really cool evening, or September...
    Philippians 4:13
    I can do all things in him that strengthen me.
    Apostle Paul inspired by GOD.

  21. #19
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,739
    Post Likes
    Quote Originally Posted by Oak54 View Post
    So is it impossible to check the heat mode in the summer?
    At your level YES

    Its clearly stated in the manual Don't do it...…

    I don't know what your going to gain?

  22. Likes Dhumphries82 liked this post.
  23. #20
    Join Date
    Jun 2019
    Posts
    10
    Post Likes
    Thread Starter
    I will weigh in new refrigerant this week and see if it helps the situation. Thanks for all the info. I will update after the recharge

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •