Results 1 to 6 of 6
    Feb 2017
    Australia
    Carrier 30HXC310 with pro dialog plus controls
    Hi gents
    Was wondering if you are able to lock out 1 circuit using the pro dialog key pad instead of creating an alarm on that particular circuit.
    Any advise would be greatly appreciated.
    Sent from my SM-G965F using Tapatalk
    Aug 2018
    Columbus,Ohio
    Should be able to in the configuration
    Sent from my SM-G955U using Tapatalk
    Jul 2018
    Kazakhstan
    On 30HXA Carrier chillers with Comfort Link and Navigator I can make compressors enable or disable easily. But in prodialog cant find such procedure ever in factory and service configurations. Only lead/lag circuits function.
    Not with Pro Dialog, wanted to do it many times myself.
    Keep it simple to keep it cool!
    uk
    There is one possibility you could try the following
    1)Configure the circuit you want to run as lead A =1 or B =2 lead circuit will load up to 100%
    2)Configure for Demand Limit switch control = 1 you need to insert a jumper across the demand limit terminals. Wiring diagram will show terminals.
    3)Configure Demand Limit Capacity % to 50% you may need to adjust this to suit. This should hold off starting the circuit you don't want to run.
    Gibbo
    uk
    There are 2 versions of pro dialog HXC a black display phase 2 or cream display phase 3.Try the Carrier website for manuals and wiring diagrams
    eto.carrier.com/lit.asp
    Gibbo