    N4 calendar alway shows inactive

    I have referenced my schedules to a calendar and everything works fine but the calendar alway shows inactive@10. I would like to show it's status in a graphic so do I have to demux or composite something?

  2. #2
    Join Date
    Jan 2003
    Location
    USA
    Posts
    4,358
    Post Likes
    The out slot on your calendar should go true if there is an active date, otherwise false. Should be able to link to that.
    Propagating the formula. http://www.noagendashow.com/

  3. #3
    Join Date
    Jul 2002
    Posts
    1,207
    Post Likes
    Thread Starter
    I agree it SHOULD but sadly it doesn't. Is this an N4 error? Anybody?
    Attached Images Attached Images  

  4. #4
    Join Date
    Jan 2003
    Location
    USA
    Posts
    4,358
    Post Likes
    Whats linked to the in slot of your calendar? Pretty sure that overrides it.
    Propagating the formula. http://www.noagendashow.com/

  5. #5
    Join Date
    Jul 2002
    Posts
    1,207
    Post Likes
    Thread Starter
    Another good call by Orion. I tried linking an override to the calendar. The schedule and calendar worked fine it just always showed Inactive.

  6. #6
    Join Date
    Jan 2003
    Location
    USA
    Posts
    4,358
    Post Likes
    If that's the case, you want your override to push in a null when it's not in effect.