    here are my notes. cant figure it out

    3 ton split system complaint was insufficient cooling. Noticed the LL sweating in the attic to piston evaporator.

    Put gauges on R22 system and noticed low suction. (evap not iced and good airflow)

    Added about 1 lb and cooling was giving me 16 degree split.

    Low 60 psi @ 51 (12 SH)
    High 160 psi @89 (0 SC) (this isn't same as measurement i took at LLF (maybe I misread thermometer)
    Ambient= 81, inside 78
    measure 57 degrees at evap LL and 76 LL, in and out of LLF.

    Don't understand LL temp sweating and zero SC. Conflicting, LL restricted or not.

  2. #2
    Join Date
    Aug 2013
    Location
    Visalia California 93291
    Posts
    7,915
    Post Likes
    Drier inside condensing unit plugged, you are reading pressure downstream from that drier

  3. #3
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by timjimbob View Post
    3 ton split system complaint was insufficient cooling. Noticed the LL sweating in the attic to piston evaporator.

    Put gauges on R22 system and noticed low suction. (evap not iced and good airflow)

    Added about 1 lb and cooling was giving me 16 degree split.

    Low 60 psi @ 51 (12 SH)
    High 160 psi @89 (0 SC) (this isn't same as measurement i took at LLF (maybe I misread thermometer)
    Ambient= 81, inside 78
    measure 57 degrees at evap LL and 76 LL, in and out of LLF.

    Don't understand LL temp sweating and zero SC. Conflicting, LL restricted or not.
    Didn't some units have a screen in the piping before the piston?

  4. Likes Metalman0880 liked this post.
  5. #4
    Join Date
    Jul 2010
    Location
    US of A
    Posts
    6,346
    Post Likes
    Quote Originally Posted by timjimbob View Post
    3 ton split system complaint was insufficient cooling. Noticed the LL sweating in the attic to piston evaporator.

    Put gauges on R22 system and noticed low suction. (evap not iced and good airflow)

    Added about 1 lb and cooling was giving me 16 degree split.

    Low 60 psi @ 51 (12 SH)
    High 160 psi @89 (0 SC) (this isn't same as measurement i took at LLF (maybe I misread thermometer)
    Ambient= 81, inside 78
    measure 57 degrees at evap LL and 76 LL, in and out of LLF.

    Don't understand LL temp sweating and zero SC. Conflicting, LL restricted or not.
    Looks like 17SH to me. Did suction raise with added coolant?

  6. #5
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    Thread Starter
    SH did rise when added freon. might have screen

  7. #6
    Join Date
    Jul 2010
    Location
    US of A
    Posts
    6,346
    Post Likes
    Quote Originally Posted by timjimbob View Post
    SH did rise when added freon. might have screen
    Would have been useful to have numbers before and after adding ref. along with wetbulb. I would have expected SH to lower with added ref and suction to hopefully rise. At this point I think it may still be low on ref.

  8. #7
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    Thread Starter
    Suggested by an oltimer who experienced this to him.. No piston installed

  9. #8
    Join Date
    Mar 2018
    Location
    Cottonwood, Ca #StateofJefferson
    Posts
    2,187
    Post Likes
    So your reading 160 psi and 89 degrees at the liquid line service valve, then its 76 degrees going thru the filter/drier and finally 57 degrees right at the coil? Just making sure I read that correctly as i have the flu and my brain only half works. Sounds like a plugged filter driver in the condenser or liquid service valve not fully open.

  10. #9
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    Thread Starter
    LLD has no temp. drop. 89 and 76 degrees. I measured something wrong so I'll go back.

  11. #10
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,111
    Post Likes
    160 PSI Is 87°

    With an 81 ambient you should have around a 225 head assuming less than 12 SEER.

    76° LLT at the filter is lower than ambient so there has be be a restriction before the point you took the reading.

    Put a probe on the LL right at the cond coil outlet, see haw that compares to ambient.

    You may have a restricted service valve or you may have restricted pass(s) in the cond coil.

  12. Likes gravity liked this post.
  13. #11
    Join Date
    Mar 2015
    Location
    Tx
    Posts
    1,951
    Post Likes
    Quote Originally Posted by pecmsg View Post
    Didn't some units have a screen in the piping before the piston?
    90's Carrier/BDP had a screen in liquid line before service valve & some evaporator just ahead of the piston body on the flares outside cabinet.

  14. #12
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    Liquid line can’t be colder than the ambient air entering the condenser.

    Upstream restriction. Cant always use temp to find the restriction. Especially since you added more gas.


    Sent from my iPhone using Tapatalk

  15. Likes BALloyd liked this post.
  16. #13
    Join Date
    Oct 2002
    Location
    Plano, TX
    Posts
    2,568
    Post Likes
    Thread Starter
    [QUOTE=BNME8EZ;25725327]160 PSI Is 87°

    "With an 81 ambient you should have around a 225
    76° LLT at the filter is lower than ambient"

    This is an obvious observation that I failed to see. How could liquid be colder then the air cooling it? Has to be a changing of state property.
    My second mistake is I look at my Iphone to see the ambient. Need to take a actual measurement.

  17. #14
    Join Date
    Nov 2008
    Location
    Piney Flats, Tn.
    Posts
    2,282
    Post Likes
    Quote Originally Posted by timjimbob View Post
    3 ton split system complaint was insufficient cooling. Noticed the LL sweating in the attic to piston evaporator.

    Put gauges on R22 system and noticed low suction. (evap not iced and good airflow)

    Added about 1 lb and cooling was giving me 16 degree split.

    Low 60 psi @ 51 (12 SH)
    High 160 psi @89 (0 SC) (this isn't same as measurement i took at LLF (maybe I misread thermometer)
    Ambient= 81, inside 78
    measure 57 degrees at evap LL and 76 LL, in and out of LLF.

    Don't understand LL temp sweating and zero SC. Conflicting, LL restricted or not.
    So I am VERY confused. You say low is 60# @ 51*. I thought 60# = 34*. So I must be screwed up if no one else thinks this.

    My actual thoughts are dude you don't have a clue what you are doing. You may want to do as you suggested go back and get better/correct information.

  18. #15
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Look for a LLFD inside the condenser cabinet. Probably restricted if there is one there.

  19. #16
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    2,810
    Post Likes
    With a zero subcool you're changing state in the liquid line before it gets to the metering device. At 80 ambient I'd expect to see around 12 sc with a fixed orifice before the sh came in line where it should be. That's why it's important to check sh and sc no matter what type of metering device. If nothing else you'll have a memory of what they should look like at various conditions.

  20. #17
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by oldguy1949 View Post
    90's Carrier/BDP had a screen in liquid line before service valve & some evaporator just ahead of the piston body on the flares outside cabinet.
    You are telling your age, the first one of those I ever encountered about had me checking into the mental hospital. But I finally figured it out. :-)


    Sent from my iPhone using Tapatalk
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  21. #18
    Join Date
    Mar 2015
    Location
    Tx
    Posts
    1,951
    Post Likes
    Quote Originally Posted by Mr Bill View Post
    You are telling your age, the first one of those I ever encountered about had me checking into the mental hospital. But I finally figured it out. :-)


    Sent from my iPhone using Tapatalk
    I worked hard for these grey hairs and retirement is great. I'm Trout fishing today on the White River and it beats the hell out fixin ac's. I am one of the older codgers , 70, but a few here are older, but I'm not laid out on display at the funeral home so it's a good day no matter

  22. Likes ChuckDe liked this post.
  23. #19
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,111
    Post Likes
    Quote Originally Posted by oldguy1949 View Post
    I worked hard for these grey hairs and retirement is great. I'm Trout fishing today on the White River and it beats the hell out fixin ac's. I am one of the older codgers , 70, but a few here are older, but I'm not laid out on display at the funeral home so it's a good day no matter
    Wow, what will I don when I retire in a few years? I was always of the opinion that the worst day of work was better than the best day of fishin'. I guess it's a good thing I have my truck to work on. Nothin like the song comin from a well tuned engine.

  24. #20
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Working everyday is what's going to keep me from laying there with people looking at me saying, "he looks like he's sleeping...."
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •