Thread: TXV Sensing Bulb

  1. #1
    Join Date
    May 2019
    Posts
    2
    Post Likes

    Lightbulb TXV Sensing Bulb

    Hey guys,
    I have recently installed a new TXV on Nordyne evaporator coil. Model number: B4VM-X30K-B
    Serial Number: 920773D. The issue I am having is when I have it in cool mode, my Suction pressure goes up to 125psi and drops down to 80, then it just keeps doing the same thing over and over. It takes about a minute for the pressure go up then back down. I have a feeling its my sensing bulb just not placed properly. Does anyone have any ideas as to what it could be? If it is the sensing bulb, some advice on placement and insulation to use over it. The system runs on R-410a. Any help would be really appreciated.
    Thanks

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,738
    Post Likes
    Quote Originally Posted by Matador429 View Post
    Hey guys,
    I have recently installed a new TXV on Nordyne evaporator coil. Model number: B4VM-X30K-B
    Serial Number: 920773D. The issue I am having is when I have it in cool mode, my Suction pressure goes up to 125psi and drops down to 80, then it just keeps doing the same thing over and over. It takes about a minute for the pressure go up then back down. I have a feeling its my sensing bulb just not placed properly. Does anyone have any ideas as to what it could be? If it is the sensing bulb, some advice on placement and insulation to use over it. The system runs on R-410a. Any help would be really appreciated.
    Thanks
    What are the SH & SC readings?

  3. #3
    Join Date
    May 2019
    Posts
    2
    Post Likes
    Thread Starter
    I only checked the SH, but it kept fluctuating going from 50 and dropping to 20. Im a new tech, still learning.

  4. #4
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,905
    Post Likes
    Please have your post moved from AOP to the tech to tech forum.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  5. #5
    Join Date
    Oct 2011
    Location
    Culver, Oregon (Central OR)
    Posts
    5,051
    Post Likes
    Sensing bulb. Depends how you installed everything too.

  6. #6
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    Whats it do when you remove it from the suction line?


    Sent from my iPhone using Tapatalk

  7. #7
    Join Date
    Dec 2009
    Location
    maroon lazyboy
    Posts
    2,723
    Post Likes
    Quote Originally Posted by Matador429 View Post
    I only checked the SH, but it kept fluctuating going from 50 and dropping to 20. Im a new tech, still learning.
    Hello Matador and welcome...
    You say you are still learning, and that is good. All good technicians are still learning.

    What you are describing sounds as if the system is low on charge and the txv is not getting enough liquid... rather a slug of liquid every now and then. Txv systems need to be charged by sub-cooling.
    Keep asking questions it is how you learn. Good luck.

  8. #8
    Join Date
    Dec 2015
    Location
    Ohio
    Posts
    28
    Post Likes
    A quick check of subcooling will tell a lot. This number is essential to know when charging a system with a TEV.

  9. #9
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    Quote Originally Posted by frankhvac View Post
    A quick check of subcooling will tell a lot. This number is essential to know when charging a system with a TEV.
    Could be low on gas
    Could be incorrect bulb placement. (If in vertical position, cap tubes should be coming off the top of bulb, not the bottom)
    Possible you overheated it
    Could be a piece of brazing rod slag stuck in the equalizer line.


    Sent from my iPhone using Tapatalk

  10. #10
    Join Date
    Apr 2006
    Location
    Tyler, Tx
    Posts
    1,793
    Post Likes
    Bulb should be place either between 2 and 5 o'clock position or the 7 and 10 o'clock position. NEVER on top or on bottom of pipe. It needs to be insulated. Once you do this verify subcooling. ~8-10° SC, depends on system. Report back what you did...
    Philippians 4:13
    I can do all things in him that strengthen me.
    Apostle Paul inspired by GOD.

  11. #11
    Join Date
    Dec 2007
    Posts
    13,231
    Post Likes
    Quote Originally Posted by Artietech View Post
    Bulb should be place either between 2 and 5 o'clock position or the 7 and 10 o'clock position. NEVER on top or on bottom of pipe. It needs to be insulated. Once you do this verify subcooling. ~8-10° SC, depends on system. Report back what you did...
    Which most mfrs DON'T do, insulate or position.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  12. #12
    Join Date
    Apr 2006
    Location
    Tyler, Tx
    Posts
    1,793
    Post Likes
    Quote Originally Posted by pacnw View Post
    Which most mfrs DON'T do, insulate or position.
    That is correct, but as I pull the bulb off the line to braze, it does not bother me. I think Trane is the only one who ships it installed, which means some installers are overheating the bulb because they do not bother with pulling the panels off, let alone wrapping the bulb with a rag...
    Philippians 4:13
    I can do all things in him that strengthen me.
    Apostle Paul inspired by GOD.

  13. #13
    Join Date
    Jan 2019
    Location
    Vero Beach, Florida
    Posts
    827
    Post Likes
    Quote Originally Posted by Artietech View Post
    That is correct, but as I pull the bulb off the line to braze, it does not bother me. I think Trane is the only one who ships it installed, which means some installers are overheating the bulb because they do not bother with pulling the panels off, let alone wrapping the bulb with a rag...
    Lennox does as well. I can’t tell you how many horizontal installs I’ve seen where the bulb is still in the vertical position.

  14. #14
    Join Date
    Dec 2009
    Location
    maroon lazyboy
    Posts
    2,723
    Post Likes
    It’s a piece of copper pipe, it’s not gonna vary that much from 6 to 9 to 12, especially if insulated. When/if it frosts over (low/medium temp) its not like it just frosts in one place. Yes theoretically there could be a river of oil that insulated the bottom, and warmer vapors at the top. So mount it properly, but incorrect o’clock won’t cause 80 psi suction with 410A.

    Make sure it has good thermal contact along the length of the bulb and copper straps are tight. That bulb is measuring temperature just like we do when we check superheat. Kind of obvious but just saying. Do you really put your temp clamps at a certain o’clock to check superheat?

  15. Likes Core_d liked this post.
  16. #15
    Join Date
    Apr 2006
    Location
    Tyler, Tx
    Posts
    1,793
    Post Likes
    Quote Originally Posted by knave View Post
    It’s a piece of copper pipe, it’s not gonna vary that much from 6 to 9 to 12, especially if insulated. When/if it frosts over (low/medium temp) its not like it just frosts in one place. Yes theoretically there could be a river of oil that insulated the bottom, and warmer vapors at the top. So mount it properly, but incorrect o’clock won’t cause 80 psi suction with 410A.

    Make sure it has good thermal contact along the length of the bulb and copper straps are tight. That bulb is measuring temperature just like we do when we check superheat. Kind of obvious but just saying. Do you really put your temp clamps at a certain o’clock to check superheat?
    Bulb placement does affect the valve operation. I have moved a bulb from the bottom to the manufacturer recommend position and the TXV stopped hunting....thermal contact with pipe and good insulation are key.

    Sent from my S60 using Tapatalk
    Philippians 4:13
    I can do all things in him that strengthen me.
    Apostle Paul inspired by GOD.

  17. #16
    Join Date
    Dec 2009
    Location
    maroon lazyboy
    Posts
    2,723
    Post Likes
    Quote Originally Posted by Artietech View Post
    Bulb placement does affect the valve operation. I have moved a bulb from the bottom to the manufacturer recommend position and the TXV stopped hunting....thermal contact with pipe and good insulation are key.

    Sent from my S60 using Tapatalk
    I can see that it could help with hunting to get farther from the liquid. In refrigeration I see hunting quite abit, even with proper bulb location. I still don’t think it caused the OP situation of 80 psi.

  18. #17
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Typically bulb position does not really affect operation until you get into larger pipe, just don't put it on the bottom where there can be a layer of oil acting as an insulation layer.

  19. Likes Core_d, Turtleman liked this post.
  20. #18
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    Quote Originally Posted by Chuck View Post
    Typically bulb position does not really affect operation until you get into larger pipe, just don't put it on the bottom where there can be a layer of oil acting as an insulation layer.
    And make sure if mounting in the vertical position, the captubes on the end of the bulb are facing upwards


    Sent from my iPhone using Tapatalk

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •