Results 1 to 10 of 10
Thread: Trane Trips
    Apr 2018
    Rhode Island
    Trane Trips
    Had a Trane Chiller. 2 circuits. Each with 2 twinned Compressors. Circuit 1 Compressor,intermittently will trip the Factory installed Circuit Breaker that feeds the Contactor.When on site,all is well. If there was a power loss and the Compressor tried starting under a Heavy load,would that be a possible cause? Bad contactor? Amp draw was 20 out of a rated 25 when on site,low load,because it had been running on the other 3 by the time we arrived. Maybe Condenser fans failing? They all ran when on site.Heavy rains came,so we left the roof. Not much diagnosis time.We did have an error for bad condenser temp sensor on circuit 2,so we ordered one,but can't see that having an effect on circuit 1. Will have to get more into it upon return. Any insight appreciated.
    May 2019
    Sounds intermittent look for broken wires between transitions. Start with the motor that the breaker protects (i.e compressors, condensers).
    Model?
    "Right" is not the same as "Wise".
    Apr 2016
    Maryland
    Verify factory wiring is landed correctly for each circuit
    Apr 2018
    Rhode Island
    It's an oldie. CGAFC604AGA1000F000N000TOW00. One of our senior techs thinks it's the circuit breaker itself, so far everything else checks out. And I did mean to post this in the Pro section. But either way, I'll leave it up to the mods.
    Poor power quality, dropped or low voltage legs, etc can cause a circuit breaker trip. Also, as you found, the compressors will run higher amps with higher head pressures. An inoperable head pressure controller/sensor will chase issues too.
    Jul 2018
    Kazakhstan
    If all checks are in order (including motor insulation resistance check), you may reposition two circuit breakers from one compressor to another. Or simple replace the suspicious breaker (may be temporarily) by the new one.
    Apr 2018
    Rhode Island
    Thanks. All good advice. This particular system,we can shut down too long. So it will be one step at a time. Turn off,check,turn on and bring the temp back down. Then turn off and continue with the checks,and so on and so forth.
    Mar 2010
    Sunny SoCal
    Quote Originally Posted by Sserrviceman View Post
    If all checks are in order (including motor insulation resistance check), you may reposition two circuit breakers from one compressor to another. .........
    This^^^
    Eric
    Jun 2019
    What was the solution with this chiller ? I'm working on the same type right now with similar issues. Any feedback will be great