    Well, codes require that all of the kitchen outlets be on GFCI protection. If this unit has its own circuit, you might try placing a GFCI breaker in their panel and then installing a conventional outlet for the ice maker to plug into, and then you can label it as "GFCI protected."

    You could also try replacing the GFCI outlet itself with a different brand. Some are more accurate and less sensitive to false actuation.
    Did it used to be a certain distance from a sink? I never heard all of them had to be. How about if it was hard piped no outlet?

  2. #15
    Join Date
    Jan 2016
    Location
    The triangle in the Keystone
    Posts
    1,172
    Post Likes
    Disconnect the curtain switch from the board and put a jumper in there and manually open the circuit when the curtain physically opens. If the GFCI doesn’t trip then the cause is the switch or wiring.

    Even if that fixes it your going to have issues in the future if that machine is plugged into a GFCI. Not sure what the local code is but if you hard wire it does that negate The need for GFCI protection?

    Also Pass and Seymour once made a GFCI with a high milliamp rating and it was very forgiving. You could look into that too.


    Sent from my iPhone using Tapatalk

  3. #16
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    30,752
    Post Likes
    The distance from a sink was the first iteration of the GFCI requirements..... now they're required in basements, kitchens, and several other places..... everything outside, etc etc etc.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  4. #17
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    7,540
    Post Likes
    A disconnect will fix the gfci issue
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  5. #18
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    5,407
    Post Likes
    Manitowoc recommends a GFCI breaker and not that nuisance causing GFCI outlet.

  6. #19
    Join Date
    Mar 2019
    Posts
    6
    Post Likes
    Thread Starter
    The story ends happily. I replaced the switch. I wasn't sure what other direction to go with it. We have a used model in the shop I grabbed a switch from. I haven't yet put the problem switch in the one in the shop, but when I do, I'll post the results. Local code does require GFCI, and any sort of rewiring would have been expensive. This was in a drive thru window and everything was tiled. I'm glad it works...but sometimes I want to know WHY. I guess I just like learning and being able to explain things to my customers.

  7. #20
    Join Date
    Apr 2019
    Location
    sharjah, UAE
    Posts
    11
    Post Likes
    well, i recommend you to go and watch video on youtube. I'm sure you will sort out your problem.

  8. #21
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    30,752
    Post Likes
    Quote Originally Posted by 2lt_swenson View Post
    The story ends happily. I replaced the switch. I wasn't sure what other direction to go with it. We have a used model in the shop I grabbed a switch from. I haven't yet put the problem switch in the one in the shop, but when I do, I'll post the results. Local code does require GFCI, and any sort of rewiring would have been expensive. This was in a drive thru window and everything was tiled. I'm glad it works...but sometimes I want to know WHY. I guess I just like learning and being able to explain things to my customers.
    No rewiring is needed. You just put a conventional receptacle in the outlet box and replace the breaker with a GFCI breaker.
    [Avatar photo from a Florida training accident. Everyone walked away.]