    Hanging 12" Black Pipe

    I need to run 12" black pipe for process cooling about 20-25' up. I have a concrete wall (E/W) and a beam (N/S) for support. Right now I plan on roll-grooved Victaulic joints, but I'm considering welding everything 4"-8", and NPT <4". What do you think is the most efficient way of safely getting the pipe in place? I'm thinking 2 chainfalls and 3 lifts; 1 centered on the run for the pipe/hoists, and 1 on each end to align, support, and tie in the pipe, 2 guys/lift. Does anyone have any suggestions on specific types of lifts that might be useful here?

  2. #2
    Join Date
    Jul 2018
    Location
    Wisconsin
    Posts
    744
    Post Likes
    Rent a Lull

    Sent from my SM-G960U using Tapatalk

  3. Likes Metalman0880 liked this post
  4. #3
    Join Date
    Nov 2011
    Location
    East Side
    Posts
    6,055
    Post Likes
    40.52 lbs per foot for schedule 40, or 810 lbs per 20’ joint.

    3 man job, chain falls, lift or 2, and some engineering approval for your hanger system.

    Capacity is 117 gallons water per 20’ at 980 lbs.

    Sooo...20’ of pipe, with water, will weigh 1,790 lbs. I hope and engineering firm is owning the liability!

  5. Likes Metalman0880 liked this post
  6. #4
    Join Date
    May 2019
    Location
    Detroit, MI
    Posts
    8
    Post Likes
    Thread Starter
    Haha if they aren't, they better start looking for someone else to do it. They have mechanical engineers that specified everything already, but I should make sure I'm not liable for their design, especially because they specced out the sizing and I don't even agree with that.
    Thanks for the heads up.
    I didn't think of a lull, that might be a game changer.
    3 man job? You think so? I was thinking 2 on each lift: 2 at the lift for the connection, and 1 opposite to line it up, then the other 3 double-checking the hangers/support, operating the lull, and prepping the next run, etc.
    Maybe you're right. Me and my brothers could do it. I just don't want anyone to get hurt cuz like you said, 1,790 lbs/stick!

  7. #5
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    2,999
    Post Likes
    If you have an overhead beam install a welded lug on the elbow. Is there a pump at the bottom of the pipe?
    No man can be both ignorant and free.
    Thomas Jefferson

  8. #6
    Join Date
    Nov 2011
    Location
    East Side
    Posts
    6,055
    Post Likes
    Quote Originally Posted by dbmoody View Post
    Haha if they aren't, they better start looking for someone else to do it. They have mechanical engineers that specified everything already, but I should make sure I'm not liable for their design, especially because they specced out the sizing and I don't even agree with that.
    Thanks for the heads up.
    I didn't think of a lull, that might be a game changer.
    3 man job? You think so? I was thinking 2 on each lift: 2 at the lift for the connection, and 1 opposite to line it up, then the other 3 double-checking the hangers/support, operating the lull, and prepping the next run, etc.
    Maybe you're right. Me and my brothers could do it. I just don't want anyone to get hurt cuz like you said, 1,790 lbs/stick!
    Yeah, really it is a 4-5 man job.....I thought you were pushing for 2 guys, figured I’d bump you a little! LOL!!

  9. #7
    Join Date
    Apr 2003
    Location
    St. Louis
    Posts
    1,045
    Post Likes
    Is this outside or inside?