    Lennox minisplit driving me insane

    I have a 2 head minisplit I installed for a customer. The upstairs unit,9000btu blows 40degree air but when I turn the temp up to 85 it just keeps blowing cold air. I stood in front of it for 5 minutes. The downstairs unit, 18k btu, was only blowing 63 degree air. I checked the factory charge, it was fine. I switched the unit that wasn't working to a different port on the condenser. I vacuumed and recharged using a scale. The downstairs unit was then 45 degrees but then went back up to 63 and upstairs unit won't stop cooling. Wtf

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    How did you check the charge?

  3. #3
    Join Date
    Mar 2014
    Posts
    38
    Post Likes
    Thread Starter
    I got 98 ounces out of the unit. That matches the factory charge. Each line set comes pre-charged for 25 ft. Each line set that I had was under 25 ft

  4. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    Line sets pre charged on minis?

  5. #5
    Join Date
    Mar 2014
    Posts
    38
    Post Likes
    Thread Starter
    The line set isn't precharged. You open the master to release the charge into the line set after you vacuum them down below 500 microns.

  6. #6
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    2,810
    Post Likes
    Did you call tech support?

  7. #7
    Join Date
    Mar 2014
    Posts
    38
    Post Likes
    Thread Starter
    I will call them on Monday when they are open. I just finished working on it and it's driving me a little crazy so I figured I would see if anyone here had any input in the meantime.

  8. #8
    Join Date
    Aug 2001
    Location
    Pavilion, NY
    Posts
    4,437
    Post Likes
    What happens when both units are calling for cooling? Do they both blow 40deg air?

    'The more you know, the more you realize you don't know'
    ...

  9. #9
    Join Date
    Aug 2002
    Posts
    2,595
    Post Likes
    Kang,
    That is what I was thinking too, seen that issue many times on multi head minis..

    I think you may be into something.
    J

  10. #10
    Join Date
    Mar 2014
    Posts
    38
    Post Likes
    Thread Starter
    While I was recharging the unit both heads where set to to cooling. As soon as I had the correct charge I went into the home and both units where in the 40s. I let them both run for about 20 mins while I put.my equipment away. I went back inside and checked it one last time before I shut them both down and the larger unit was 63 degrees. The smaller one was still in the 40s.

  11. #11
    Join Date
    Dec 2009
    Location
    maroon lazyboy
    Posts
    2,723
    Post Likes
    It was possibly reducing capacity being near set point? Oh. Yes. Triple check your wiring.

    The zones may be crisscrossed

  12. #12
    Join Date
    Mar 2014
    Posts
    38
    Post Likes
    Thread Starter
    Wow that must be it. I must have wires 1,2,3 in the right places but the units must be criss crossed. Boy do I feel like a ****ing idiot! Easy fix though

  13. #13
    Join Date
    Mar 2014
    Posts
    38
    Post Likes
    Thread Starter
    It still doesn't make sense though because when both units are calling for cooling even if the wires were crossed both units should still be blowing cold air and they are not.

  14. #14
    Join Date
    Dec 2009
    Location
    maroon lazyboy
    Posts
    2,723
    Post Likes
    They start modulating before they reach setpoint. Like 3° above on one manufacturer.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •