    Low temp 20,000btu evap coil

    Anyone know of a current model low profile, low temp 208/230 single phase 20,000btu evap coil with 2 or 3 fans. Customer is replacing an old system that still has 502 in it. The Bally coil that is in there is a BF200**** and only has 2 fans. Coil is thick. I've checked HTPG and Heatcraft. 20,000 btu's is 5 fans.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  2. #2
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    7,370
    Post Likes
    Thread Starter
    tag
    Attached Images Attached Images  
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  3. #3
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    20,893
    Post Likes
    10,000BTU's per fan...………….

    That is one thick coil!

    have you contacted Bally or Heatcraft?

    Any chance of installing 2 evaps?

  4. #4
    Join Date
    Mar 2008
    Location
    kansas
    Posts
    1,198
    Post Likes
    Just to save time I looked at at Trenton and krack
    Honeywell you can buy better but you cant pay more

    I told my wife when i die to sell my fishing stuff for what its worth not what i told her i paid for it

  5. #5
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    20,893
    Post Likes
    This might be a good time to do what Icemeister was saying about LT coils in markets. Inlet air side has less fins per inch so less frost blocking the air flow!

  6. #6
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    30,293
    Post Likes
    Quote Originally Posted by 2sac View Post
    Anyone know of a current model low profile, low temp 208/230 single phase 20,000btu evap coil with 2 or 3 fans. Customer is replacing an old system that still has 502 in it. The Bally coil that is in there is a BF200**** and only has 2 fans. Coil is thick. I've checked HTPG and Heatcraft. 20,000 btu's is 5 fans.
    I have a FF rest with a walk in using a Larkin evap from 1981. It was also a 503.

    We are looking at a Trenton setup, soup to nuts. Probably a new lineset, too.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  7. #7
    Join Date
    Nov 2014
    Location
    Northern Idaho
    Posts
    857
    Post Likes
    https://www.krack.com/en/technical%2...ation/CRCC.pdf

    Pg. 8? Only thing is its medium profile, just noticed that.

    MK26E-206

  8. #8
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    13,721
    Post Likes
    Quote Originally Posted by GoCougs View Post
    https://www.krack.com/en/technical%2...ation/CRCC.pdf

    Pg. 8? Only thing is its medium profile, just noticed that.

    MK26E-206
    The older style Bally evaporators were essentially medium profile. Their current BF-200 is a five-fan low profile but the old ones were a two-fan style with a fan diameter of about 16" or so.

    The Heatcraft equivalent would be a BML220, which is a 2-fan 22,000 Btuh coil.

    Name:  Bohn-BML-Evaporators.png
Views: 80
Size:  114.1 KB

  9. #9
    Join Date
    Mar 2008
    Location
    kansas
    Posts
    1,198
    Post Likes
    How in the do you remember all this
    Honeywell you can buy better but you cant pay more

    I told my wife when i die to sell my fishing stuff for what its worth not what i told her i paid for it

  10. Likes The Turtleman liked this post
  11. #10
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    5,267
    Post Likes
    What is the product?

  12. #11
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    7,370
    Post Likes
    Thread Starter
    Quote Originally Posted by TechmanTerry View Post
    What is the product?
    Middle school cafeteria food. This cafeteria also stores/supplies food to 2 other smaller schools. The boxes are immaculate for as old as they are. They are doing a remodel at the school and replacing the condensing units for the cooler and freezer and relocating from the boiler room to the roof. I'm going to sell the equipment to the general and he's subbing out the install. The evaps may not even get replaced, the general is going to quote 2 entire systems, or 2 condensing units with gas and metering devices. The original boxes/equipment appear to be ordered from Bally as a custom remote set up based on the cooler model#. We're a Witt dealer so Witt would be my best option and I'm going to call them next week as well.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  13. #12
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    7,370
    Post Likes
    Thread Starter
    I found a Witt Med Profile with 2 fans. Hopefully the dimensions work. Thanks for the help