    Correct tonnage

    Hey guys I have a two part question here, first is this model number R2A360GKR2 a 5ton unit? I'm pretty sure it's a carrier unit since any name placards are missing. Secondly I shouldn't have a problem taking a compressor from a straight cool and installing it in a heat pump would I?

  2. #2
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    10,689
    Post Likes
    Quote Originally Posted by Gabriel24 View Post
    Hey guys I have a two part question here, first is this model number R2A360GKR2 a 5ton unit? I'm pretty sure it's a carrier unit since any name placards are missing. Secondly I shouldn't have a problem taking a compressor from a straight cool and installing it in a heat pump would I?
    This is an ICP unit (now owned by Carrier), and it is 5 ton (60).

    A compressor is a compressor, no matter if it is in a Heat pump or AC condenser. The question is, is the BTUH size and Refrigerant type, compatible for the system you are installing it in?
    Instead of learning the tricks of the trade, learn the trade.

  3. #3
    Join Date
    Nov 2011
    Location
    USA
    Posts
    1,878
    Post Likes
    Quote Originally Posted by rundawg View Post
    This is an ICP unit (now owned by Carrier), and it is 5 ton (60).
    R2A360GKR2

    I was bettin' on 36...

  4. #4
    Join Date
    Dec 2009
    Location
    maroon lazyboy
    Posts
    2,358
    Post Likes
    Quote Originally Posted by rundawg View Post
    This is an ICP unit (now owned by Carrier), and it is 5 ton (60).

    A compressor is a compressor, no matter if it is in a Heat pump or AC condenser. The question is, is the BTUH size and Refrigerant type, compatible for the system you are installing it in?
    The heat pump compressor needs to be designed for very high compression ratios in heating mode, basically it’s a low temp system with as low as -10° SST and 110° SCT. Keeping compressors cool in those conditions can be a problem.

  5. #5
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    10,689
    Post Likes
    Quote Originally Posted by knave View Post
    The heat pump compressor needs to be designed for very high compression ratios in heating mode, basically it’s a low temp system with as low as -10° SST and 110° SCT. Keeping compressors cool in those conditions can be a problem.
    You are correct, but point I am making is, many manufacturers use the same compressor in their straight AC condensers and Heatpumps units of the same model line.
    Instead of learning the tricks of the trade, learn the trade.

  6. #6
    Join Date
    Dec 2009
    Location
    maroon lazyboy
    Posts
    2,358
    Post Likes
    Quote Originally Posted by rundawg View Post
    You are correct, but point I am making is, many manufacturers use the same compressor in their straight AC condensers and Heatpumps units of the same model line.
    That is fascinating, I never would have guessed that.

  7. #7
    Join Date
    Dec 2009
    Location
    maroon lazyboy
    Posts
    2,358
    Post Likes
    That explains a few things, 😀

  8. #8
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    2,955
    Post Likes
    It is a 13 seer, 5 ton....hence 360
    Quote Originally Posted by Saturatedpsi View Post
    R2A360GKR2

    I was bettin' on 36...