    Bosch BOVA with TAM9

    Im probably missing something simple but when setting up the TAM9 to work with a new Bosch condenser Im getting a HP signal on the AH interface in cooling. Thermostat is set to energize RV in Heat and it is cooling well but not showing correct mode at TAM9.

  2. #2
    Join Date
    Jan 2012
    Location
    Arrowhead Stadium
    Posts
    1,166
    Post Likes
    The TAM9 needs to have the o and y terminals energized in cool mode to have the correct airflow and operation.

  3. #3
    Join Date
    Nov 2015
    Posts
    4
    Post Likes
    Thread Starter
    Understood. How do I make that happen when the Bosch requires o be energized in Heat? Cant find anything in either service manual about proper fix that will work in both modes?
    Last edited by letthesmokeout; 05-17-2019 at 07:02 PM. Reason: Spelling grammer

  4. #4
    Join Date
    Nov 2015
    Posts
    4
    Post Likes
    Thread Starter
    Quote Originally Posted by letthesmokeout View Post
    Understood. How do I make that happen when the Bosch requires o be energized in Heat? Cant find anything in either service manual about proper fix that will work in both modes?
    Do I move condenser O to W1 and condenser W to W2 then set thermostat back to O? Sorry. Brain is a little attic fried from his week.

  5. #5
    Join Date
    Dec 2009
    Location
    maroon lazyboy
    Posts
    2,359
    Post Likes
    Quote Originally Posted by letthesmokeout View Post
    Do I move condenser O to W1 and condenser W to W2 then set thermostat back to O? Sorry. Brain is a little attic fried from his week.
    No, I wouldnt do that...
    The older thermostats used to have both O and B, in which case you could wire O to the TAM and B to the Bosch.

    In this case you will likely need a small relay to reverse the logic: Use heat mode O to power the coil of relay. TAM O gets power from R, through the NC contact.

  6. #6
    Join Date
    Jan 2012
    Location
    Arrowhead Stadium
    Posts
    1,166
    Post Likes
    I can’t remember exactly how we wired a tam9 to a Rheem with b for hp. A couple 90-340 relay, set stat to B for heat, powers coil, b to nc and through to rv coil, jumper to no then back to ah.

  7. #7
    Join Date
    Nov 2015
    Posts
    4
    Post Likes
    Thread Starter
    Quote Originally Posted by ksefan View Post
    I cant remember exactly how we wired a tam9 to a Rheem with b for hp. A couple 90-340 relay, set stat to B for heat, powers coil, b to nc and through to rv coil, jumper to no then back to ah.
    I can do something with that info. Thanks.