Results 1 to 13 of 19
    Oct 2018
    Water Chiller Problem
    Unit not cooling
    Carrier R22
    m#38ak-008---501
    s#0897g00166
    Aqua products co., inc
    m#dcp-71b
    s#078049700701
    suction pressure-96
    discharge pressure-160
    liquid line pressure-145
    suction line temp-81F
    discharge line temp-186F
    liquid line temp-80F
    Comp RLA-28.8
    Comp actual amps-13.8
    unable as of posting to get TD off water, pressure, or flow.
    The chilled water temperature seems to be at set point so I am not sure why you think there is a problem.
    "Right" is not the same as "Wise".
    Oct 2018
    How can you say the chilled water is at set point. I know it is not cooling because the machine it is cooling is over heating. Unfortunately there is no history of performance from the custom besides the chilled water lines were sweating and cold and now they are not. They dont have any real data only that it has been working for the last 20 years and now it is not. There has been no increase in heat load on the unit.
    Let's kinda look at your numbers here:
    Quote Originally Posted by Snow23 View Post
    Unit not cooling
    Carrier R22
    m#38ak-008---501
    s#0897g00166
    m#dcp-71b
    s#078049700701
    suction line temp - 81F
    SSH - 24º
    suction pressure-96 - 57º
    discharge pressure-160 - 87º
    liquid line pressure-145 - 81º
    liquid line temp - 80F
    Liquid SC - 1.0º
    discharge line temp - 186F
    Imagine my best Karl Childers voice: It ain't got no gais innit!
    Comp RLA-28.8
    PHM
    Oct 2018
    Name plate has a system charge of 1.5lbs. Believe low charge to be the problem i added 1 lb with no change.
    How can you say the chilled water is at set point...
    Exactly.
    Oct 2018
    Manaual says unit comes factory charged with 7 lbs. Recovered freon and made sure it had 7 lbs.
    From what I understand the subcool is very low so no liquid to the txv so no cooling. With the high suction pressure and low discharge pressure Im thinking bad compressor valves, but I was under the impression that scroll compressors couldnt fail this way.
    Every pump can wear out. With scrolls it's obviously not the rings or the valves but the scrolls themselves can eventually wear out.
    But . . . . is there any thing which bypasses the TXV? Hot gas bypass or anything like that?
    What other components are there beside them Condenser, Receiver, TXV, Evaporator, ad the Compressor?
    Does the compressor ever cycle off on it's internal overload?
    PHM
    PHM
    Jul 2018
    Kazakhstan
    Is it condensing unit with Copeland ZR94KC scroll? Does this system has Hot Gas Bypass?
    Without hot gas you may close liquid line valve and check the suction pressure. If it will go down to about 0 bar (dont let vacuum), compressor is in order. Previously adjust low pressure switch.
    Oct 2018
    Compressor m#zb58kce-tf5-931
    no hot gas bypass
    no reciever
    nothing bypasses txv
    compressor does not cycle off on overload
    Southold, NY
    Total charge 1.5#'s and you added 1# ???
    Southold, NY
    Factory charge is 7#'s you adjust it in the field according to the chart in the manual!
    montreal
    Google is telling me that 38ak is a split condensor. Not a chiller
    Is Google right? Just trying to figure out on what your working.
    How long of pipe do you have to the condensor.
    What is water in- water out temp
    What is the temp at the condensor?