Results 1 to 11 of 11
    Feb 2019
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Johnson Controls/York E-Link Gateway BACnet Issue
    Hi,
    I am having an issue writing to AV 1 and AV 2. I have read the commissioning and trouble shooting document and even reached out to Johnson Technical support ( though they do not seem in any hurry to return my call), we are writing at priority 13. This is a York air cooled chiller. We can put the unit in remote control and use BV 1 to start/stop the unit with no issues but it will not accept the write commands to the two AV's in question. Any help will be appreciated.
    Jan 2002
    Fort Worth\Dallas, Texas
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    What is AV1 and AV2?
    Go Rangers!
    Feb 2019
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by lwarren View Post
    AV1 is remote chilled water set point and AV 2 is remote current demand limit. The documentation states the objects have to have their SOURCE set to R-Setpoint, R-Setup Flag or Network. We cannot find where to access the "SOURCE" to verify how it is set up.
    Apr 2014
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Sweat View Post
    It will only accept a write every 15 minutes.
    Feb 2019
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by JCIman View Post
    Problem is it never writes to it. I would be happy if I could get a write every 15 minutes
    Apr 2014
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Can you try to write with a bacnet discovery tool like the one from contemporary controls?
    I’ve used that in the past to isolate similar problems.
    Feb 2019
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks for the replies, yes we have tried it with a contemporary controls router and a KMC 5150E BACnet router. Just not finding how to tell the AV it's "SOURCE". This is being brought into a Trane front end using an SC+
    Chicago area
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Sounds like a setting or 2 in the chiller through the user interface requires adjustment.
    Have the model number of the chiller?
    Feb 2019
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by heatingman View Post
    We have set every possible parameter through the York keypad interface, all other documentation wants you to use hyper terminal but seems those settings have nothing to do with the BACnet objects
    This is a York Air Cooled Chiller Model Number YVAA0275EGL46BA
    Chicago area
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Are you using an analog input to the chiller for the remote settings or trying to use written points in bacnet?
    Cause if your doing it via hardwired points, then I believe you need to have the chiller set to local.
    Feb 2019
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Everything I have tried so far is with the e-link, no hard wire points though I am considering going that route.
Contracting Business
HPAC Engineering
EC&M
CONTRACTOR
