    I checked the gas pressures and the voltage at the gas valve. I didn’t know what else it could be. I never ran into a problem like this before. That’s why came on here to see what else would cause the sputtering

  2. #15
    Join Date
    Mar 2018
    Location
    Kansas Flatlands
    Posts
    287
    Post Likes
    Did you check the orifices? sometimes a white corrosion gets around the holes of the brass.

  3. #16
    Join Date
    Sep 2015
    Posts
    15
    Post Likes
    Thread Starter
    Yeah I pulled the burners and made sure they were clean

  4. #17
    Join Date
    Sep 2015
    Posts
    15
    Post Likes
    Thread Starter
    What about clogged exhaust and/or intake pipes? Would a clogged drain cause the sputtering?

  5. #18
    Join Date
    Sep 2015
    Location
    Ontari-ari-ari-o
    Posts
    1,709
    Post Likes
    Quote Originally Posted by cp3 View Post
    What about clogged exhaust and/or intake pipes? Would a clogged drain cause the sputtering?
    Absolutely.

  6. #19
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    21,396
    Post Likes
    Sounds like a lot of guessing...…………

    Have you called Tech Support?

  7. #20
    Join Date
    May 2019
    Posts
    7
    Post Likes
    Birds nest or an unlucky squirrel in the flue pipe maybe? what are your inducer amps and pressure looking like?, if u bypass the pressure switch manually after inducer spools in sequence, does it still flutter? (obviously dont let it run for long.)

  8. #21
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    21,396
    Post Likes
    Quote Originally Posted by Small Tech View Post
    Birds nest or an unlucky squirrel in the flue pipe maybe? what are your inducer amps and pressure looking like?, if u bypass the pressure switch manually after inducer spools in sequence, does it still flutter? (obviously dont let it run for long.)

    NEVER
    bypass a safety!

    Use your volt meter to test

  9. #22
    Join Date
    Jan 2015
    Location
    Iowa
    Posts
    1,303
    Post Likes
    I had one not too long ago (not a Trane but Carrier) it had sufficient flow to make up the pressure switch and go through the normal start sequence but when the burner came it did pretty much what you said, when it did burn for a couple seconds the flame was pretty lazy. After checking gas valve (pressure & voltages, cleaning flame sensor) found the exhaust partially plugged. It would lock out on weak flame signal. She just did not have enough air flow through it.

    Good Luck